Ultra Fin Concerns
I have been involved in at least 8 Ultra fin projects in the San Francisco bay area. I have not received complaints from customers. I have the product in my 2 year old 2100 sq foot house, and it is not very resposive. The total heat load is 39,000 Btu/hr at 30F which relates to 18.5 Btu/hr per square foot. I used kitec aluma pex 30" or less on center. Foil faced R19 on the lower floor with a 4' air gap. R13 glas with a 4" gap for the second floor. The ends of the joist bays are well done with R10 rigid insulation. I have an out going water temperature of 180F.
I was setting the temperature back to 64F at night, and found I had to kick it up at 4.30 am to achieve a 68F temperature by 7.00 to 7.30 am. On cold days (36) the system has not reached design temp in 3 hours. Am I missing something? or is this product not what it is made out to be?
Three wholesalers I have expressed my concerns to have assured me they have not had complaints. I was also not born last night, and don't take that for gosspel.
I'm two houses into a seven house sub division in san francisco, and have concerns from my own house experience.
john owens
  • lee_7
    lee_7 Member Posts: 457
    If this is a radiant floor setup, why such large spacing between pipes? Also, with radiant I don 't believe set back is a great idea as you have a very large mass to reheat. We always set it and forget it on radiant jobs. They are not for quick response in heat changes. They take a long time to reheat.
    Just a thought
    Lee
  • EJ hoffman
    EJ hoffman Member Posts: 126
    what is your return temp?
  • set back and radiant...
    Don't work well together. Get rid of the set back.
    We also run our tubing at a maximum of 16" OC with the fins every 24". Allows for a lower operating temperature, which equates to fuel savings.
    ME
  • John Owens
    John Owens Member Posts: 5
    Return temps vary. When it's cold out. I'm getting about a 14F drop. When the underfloor cavity is really warm the delta T can be a s close as 2F. There are only 11 circuits of tubing, Most are not much more than 110 feet. the circulator is an 007.
  • John Owens
    I am experementing not using set back. It may be more cost effective to maintain the temperature rather than set it back and use a lot of energy to bring it up to temp. Thanks for the suggestion
  • Mark Custis
    Mark Custis Member Posts: 537
    I agree
    with 3lees on setback and Mark with more tubing.
    Here in Cleveland we rarely use less the 9" OC. That is why the tubing makers like us.
    Have yet to use the ultra-fin product.
  • Nailed
    Nailed Member Posts: 2
    ulrta fins
    I have a ultra fin system at my own home and have had simular issues with the system. West coast but north of you in Washington. I feel 30" centers is to much, we did the master with 24" centers and it works well. My water is set at 160 the air space is about 6" with 6" of fiberglass under. R-21 or so. The system does heat but I don't get carried away with the temp. I don't feel that it would ever reach 80 in the winter. If the spacing was closer you would have more fins, but then again if it was closer you wouldn't need to have fins. When the system was first installed it din't work, the contractor bled out the air pockets and turned up the temps before it would maintain 70. I am content with the system now but I wouldn't say happy.
  • kpc_45
    kpc_45 Member Posts: 29
    turned up...
    the water temps to what? I was pretty sure it was supposed to work w/ 180F only.
  • Jed_2
    Jed_2 Member Posts: 781
    Spacing
    Check this out, Lee.
    www.ultra-fin.com/
  • lee_7
    That system looks like a lot of drilling. I will take staple up plates anytime. They look much easier and faster to install. Pipes on 6-9" centers
  • Tombig_2
    Tombig_2 Member Posts: 231
    ultra fin
    I've had it perform down to 140* water temp on OD reset but had to set design/180* at 28-32*. John, when you say 4" air gap is that total or 4" below the fins. If it's 4" overall you might not have enough air space above and below the fins for proper convection around the fins. U-F needs that to work properly. The poorest performance will be exactly where the insulators pushed the insulation up too far and touched the fins. I would opt for less R-value and more air space in shallow joist bays. Also depending on subfloor and floor covering material your setback times/temps need to be adjusted.
    Tom G.
  • Rudnae
    Rudnae Member Posts: 47
    Spacing...
    Gentlemen, I have noticed that some of you who have installed this product are using 4" and 6" air gaps between the pipe and the insulation/floor. In my design manual it only asks for 3" above and 3" below. Wouldn't increasing this space increase the lag time of the system? We have sold many systems up here in the frozen North, using the design manual and not had any issues. Also given the nature of the beast this system does not lend it self to overnight / daytime setback. Too much energy required to make it go. Just my $0.02.
  • McKern_2
    McKern_2 Member Posts: 43
    ultra fin
    have ultra fin installed for 4 years -35 f -37c in northern Canada no problem keeping rooms at 23c 73f wife likes it a little warm.I installed it with 3" above and below air space and 24 oc I do not use set back as radiant systems are too slow for heat recovery each room is controlled with a thermostat
  • mikegee
    mikegee Member Posts: 8
    ULTRA FIN New construction in NY
    i m building a new 6000 sq ft home in NY city. Planning to use Ultra Fin for the entire house. Had ultra fin do a heat loss calculation. They recommend approximately 3700 ft of tubing with 2200 pairs of plates.
    Can anyone comment on the hating system, and suggest a Modulating or Condensing Boiler< Natural gas) should i consider adding some radiators in larger room to make sure I can have a trouble free heating system
    Thank you
  • Zman
    Zman Member Posts: 7,614
    New post
    Mike you would be better off posting this as it's own question in the radiant heat section.
    Ultra fin is a bad idea with modulating boilers.
    Carl
    Albert Einstein
  • Gordy
    Gordy Member Posts: 9,546
    Heat loss details
    What SWT are designed for your system?
    Why ultra fin?
    There are other RF systems to choose from that offer more output at lower supply water temps.
    Mod/con boilers are more efficient at lower supply / return temps to get their full benefit of capable efficiencies .
  • mikegee
    Ultra fin Radiant heating
    Ultra Fin was recomended by a  contractor. I can not find too many completed installations, or a contractor experienced with this system.
    Can you suggest either? or can you suggest another method for in joist installation
    Because of the layout , many rooms have minimal wall space available for radiators?
    Thanks
