What could cause cast iron baseboard to crack
This is an old system, approximately 50 year old Baseray baseboard system. Three years ago, 3rd week in March, I came home to wet floor and small crack in one section of 3' strip of baseboard. Replaced this baseboard and heat ran fine for 2 years. This past March, almost the exact date, i heard what sounded like a gun shot in my living room and the end section of a 11' run had a 2" crack on top and flood the room. Fortunately I was there at the time, so water damage was minimal. I found that the expansion tank was water logged and now replaced. Could this have caused the issue?
  • Ironman
    Ironman Posts: 7,982
    Yes, a water logged expansion tank and a faulty pressure relief valve could cause this.
    Bob Boan
    mattmia2 Posts: 18,507
    edited 2:13AM
    but freezing is the most common cause
    could have corroded from the makeup water if the expansion tank has been waterlogged for a while
    109A_5 Posts: 4,834
    Excessive pressure due to the water logged expansion tank may have been the contributing factor. I'd keep better track of the system pressure and the status of the expansion tank. Does the pressure relief valve work properly ?
    Kind of makes me wonder what else has been fatigued.
    Jamie Hall Posts: 28,048
    As @109A_5 and others have said, the failed expansion tank may have been a contributing factor — but unless the system pressure relief valve was also failed, not the real cause.
    Odss are very very good that the system, or at least some of the baseboards, froze at some point, which would have started a small crack or cracks. Combined with the pressure cycling from the expnsion tank problem, these cracks grew — as cracks do — to the point where one failed. Now you've had another fail.
    And the bad news is there are probably others…