Stinky oil boiler
Not sure where to turn here. Oil company, hvac company and plumber all have come up short. We’ve been getting oil exhaust smell in our basement when the boiler is cranking good, most specifically when hot water is going for back to back showers. Has been happening for a couple years but only once or twice a winter. Now it also all the time. Oil company will not sell me a new boiler, says I don’t need it.
system.
- Peerless boiler with riello burner. 22 years old
- Vents from basement thru garage into an outside wall chimney. Induction fan installed by previous owners.
Work done in order.
- Cleaning x2
- Replaced exhaust flue, tape seems, insulate to increase draft. Flue pipe was rotted out. Hope was in increase draft with hotter pipe.
- air adjust
- oil company owner son came out, discovered they broke the chamber during the clean. Replaced. This helped a ton. He discovered a back draft issue when the kitchen fan is turned up upstairs. Almost zero smell after this repair, expect when fan or dyer was running upstairs or it was super windy outside
- fresh air intake added to the basement with a ‘fan in a can’ to eliminate the backdraft issue. Unfortunately the Smell back, pretty bad this morning. After we started up the heat downstairs and kids took 3 showers. Heat gets dropped at night to 60, we run a heat pump yesterday with these ‘mild temp’ so it was cooler start up.
Comments
-
reducing the firing rate slightly might help. Post combustion report if you have one.
0 -
Is that a "Fan in a Can" in the corner for combustion air?
Where does it get its air outside?
Picture of the inlet if possible?
0 -
Dumb question maybe. I notice a draught regulator damper on the exhaust. How open is it when the boiler is running (it's closed in the picture)?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Your flue pipe, thru the drywall, next to the studs violates code.
I don't see any combustion numbers.
Is it possible there is some gasketing material missing. Specifically under the top of the unit, where the cleanout plate is located.
Are you sure you solved your depressurization issue?
How far is the horizontal run in the flue pipe & how high is the chimney? You may simply have a bad design, combined with that deep set back and very cold flue on start up.
Although the Riello is a nice burner, a Beckett with a longer pre-purge and a long post purge might help.1 -
-
0
-
Yes they thought it needed more air/wanted to pressurize the basement. 25-30 duct run thru the garage to an outside wall.
here’s the route and intake vent0 -
semi open. We’ve tried very open, not open seems to smell less
0 -
it’s there’s a large insulation air space at the drywall.
The bad routing was brought up by all three folks. Reason for the insulation was trying to over come this. Been in our for 8 years and hasn’t been a issue like this till this year
0 -
Realistically, there are only two ways you can get a smell from an oil burner: either there is inadequate draught on the chimney or stack, or inadequate combustion air getting in. I asked about the draught damper, as if there is adequate stack draught it should be slightly open even with the burner off — and reasonably open with the burner on. If it isn't, that tells you that there is inadequate draught in the stack or chimney or that the house is depressurized relative to outside. May take some tracking down.
The fan in a can may help — provided it is turned on at the start of the burner pre-purge (if any) and in fad preferably earlier — provided it's big enough to compensate for any other exhaust fans or the like.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
thanks. Can in the can kicks on 3-5 seconds prior to fire up. Then the induction fan for a seconds, then fires up. Damper doesn’t move until the induction fan kicks on. They put a screw in it to try and keep it shut closed, not sure if that helps or hurts.
The can-fan is on the low setting, maybe it needs to be bumped up.
Bathrooms fan was going today in the bathroom but that was on the second floor. Though it’s a nice 110cfm fan it’s a long way to affect the basement ?
Heat pump upstairs was also going (ducted in the attic) but that’s tight as a nats ****, had a sub from work do it that does all hospital work.
0 -
Has the flue been inspected? There's a cap to inspect the base.
That looks about a 12 ft horizontal run on the flue. I'd like to see what the draft is without the inducer. I find it hard to believe its only -.01,-.03 with a booster. If there was a need for the booster, where's the interlock?
I say get the chimney and flue inspected. Get draft and smoke readings without the booster. I guess the service company is still using the wet kit? No printout of the combustion test?
0 -
This is not an approved use of this tape:
Obviously the smell is coming from inside the fire box where the flame is converting the liquid fuel into a very hot gas that is supposed to vent up the chimney. When everything is oerating properly, any smell would not be able to leak out of the joints that are marked with a green arrow. Therefore those joints do not need to be sealed because basement air would leak in to those joints combustion fumes can not leak out.
Even if you believe that the fumes are leaking out of those joints, sealing them with that tape will not solve the odor problem because the blue arrow points to a much larger seam that will let much more exhaust odor into your basement. So that tape is useless in resolving your problem.
To correct your problem you need to fix the source of the problem and not put bandaids on the problem in the home that you find the source of the odor leak. the blue arrow it the location of the odor leak and you can't seal that opening or the barometric damper will not be able to perform it job of regulating the ever changing draft opf that chimeny.
Why is the chimney down drafting? Find that reason and you are on the way to correcting the odor problem.
here is one video about down draft:
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
-
I don't believe you have an easy fix. You have an architect who drew a bad design on a piece of paper, and it's too late to get any relief from that architect. He messed up, got paid for his poor design, and the previous owner lived with that mistake for years. Tough situation for you.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Here is my idea for the fix:
Add an all fuel rated manufacturered chimney closer to the oil burner that extends above the second floor /attic roof line.
This will place the top of the chimney above the downdraft area of the vortex currents that occur below the roofline, where the existing chimney terminates.
You can keep the Fan in a Can. No use throwing that away, it can't hurt anything.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
@EdTheHeaterMan why not extend the brick chimney?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
2 -
this makes a ton of sense why it’s worse with storms coming in! Luckily windy typically blow the opposite direction which would help explain the randomness of the issue. In lieu of the doing the tall stack I’m wondering if a power vent dumping out near grade would work. A lot of houses have these in my neighborhood (cookie cutter houses all the same buy the same builder)
I asked about removing the interior barometric vent but Massachusetts requires them by code.
also agree on the tape, my neighbors company did it, he said they fixed three houses in the neighborhood with the same issue so I went with it.0 -
I have done that in the past at my father's home in SeaIsleCity, NJ. I just don't like that 15 ft horizontal run with the insulation around it. It does not look like there is a 1/4" per foot rise from the basement wall to the chimney.
If you have a chimney man build a 8x8 stainless steel extension about 12 foot tall and support it with guy wires it will work. It will look like it does not belong in that neighborhood, but it will work. A good chimney with the proper support next to the 2 story portion of the home can have a nice covering built around it so it blends nicely with the home's construction.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
The sidewall vent is also a good fix for you. However, that would put the odor underneath your deck, which means you would always have that odor outside your home, not just on days with a particular wind direction.
I like getting the exhaust outside, above my head, where I can't smell it.
Field Controls makes a chimney topper with an exhaust fan that might work for you. However, that's just another component that requires maintenance. Every year, someone has to climb onto the roof to inspect the motor and perhaps add a little lubricant. Then, every 5 to 10 years, you may need to replace the fan motor assembly.
These are not low cost and you will need a CK-63 control kit in addition to the chimney top draft inducer. this makes sure that you have established draft before the burner can light. this can be set to continue to operate as a post purge for enough time to get rid of the odors after the call for the burner stops. That odor can last for 10 minutes after the burner shuts down, and if there is a down draft when the motor stops, you will get the odor.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
As a burner tech I would never recommend that chimney top inducer. That's going to break when there's two feet of snow and ice on the roof and nobody in their right mind will want to repair that. I'd recommend extending the existing chimney to the correct height or installing a sidewall power venter. At least those you can get to and work on in bad weather.
0 -
Completely wrong. Riello’s require 0 to + overfire draft which must be controlled, which is done with a draft regulator.
0 -
I suggested that first. @gofaster2828 then asked about a sidewall vent. That would be a good choice; however, I have had customers complain about the odor outside their homes every time the burner operates. Not once in a while when the wind blows from a certain direction, but every time the burner operates. This makes their patio or deck unusable all year round.
That is why I like extending the chimney above the roofline as the best choice. The all-fuel chimney would need to be boxed in on the first floor, between the garage ceiling and the attic above. That would take away a 2-foot-square section of the room where the vent passes through the first floor.
Then there would be only about 8 feet of manufactured chimney above the last support on the side of the building, eliminating the 10+ foot horizontal vent connector.
If you keep the 10+ foot horizontal vent connector and extend the existing chimney, you would have over 15 feet of unsupported vertical chimney that would need guy wires for support in that location. That's not what I would call a good design.
There is no perfect solution here
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 135 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 52 Job Opportunities
- 18 Recall Announcements