  • ethicalpaul
    ethicalpaul Posts: 8,993
    edited August 11

    it will let this section of pipe move with the boiler possibly along with rotation at the hartford loop fitting. it doesn't take much.

    Well I mean you can't avoid having an elbow from the header down to the equalizer so it's not really a question.

    But the elbows at the tops of the risers could be skipped with the risers running directly into the header (and we sometimes see that), and so that's why I think of those as the swing joints that people are always saying are so necessary.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 20,938
  • ChrisJ
    ChrisJ Posts: 17,645

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • JUGHNE
    JUGHNE Posts: 11,633

    So just to confuse myself and possibly others, what about the consideration of the internal surface area of the ID of the pipe itself?

    The pipe does in effect act as a condenser (think radiator EDR) and the more surface would cause more condensation of the steam.

    Without crunching numbers, it seems that two 2" risers of 24" height would have more ID area than one 3" X 24" riser.

    So what does anyone think?

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 20,938
    edited August 11

    2 2”is 6.2 square inches

    1 3” is 7”

    @JUGHNE it would seem that way but the math says otherwise

  • mattmia2
    mattmia2 Posts: 17,994
    edited August 11

    I think he is talking about the surface area of the cylinder, not the open area of the circle, although they are pretty close, 2x2" has just slighly more interior surface area than 3", assuming i'm using actual 2" and 3" id sizes instead of the nominal sizes.

    edit:
    i used google's calculator for the area of a cylinder and it included the ends which is why it was wrong.

  • ChrisJ
    ChrisJ Posts: 17,645
    edited August 11


    For what @JUGHNE is talking about we need to use circumference.

    Two 2's is 12.57"

    A single 3" is 9.42"

    So a single 3 has less surface area and less heatloss. It probably would never matter especially insulated.

    But, technically…..

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 20,938

    IDK. The size of the hole(s) is what the steam goes through.

  • ChrisJ
    ChrisJ Posts: 17,645

    It is.

    But he's talking about heat loss of the piping and how much it initially absorbs to bring it up to temperature.

    Two 2" pipes has more surface area and probably mass than a single 3"

    A single 3" flows better and has less loss.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ethicalpaul
    ethicalpaul Posts: 8,993

    I think this issue is mostly unimportant and not noticeable—we can't say that pipes don't make good radiators and then claim that uninsulated pipes cause tons of condensate. They can't both be true, pick a side 😅

    But the thing to look at is the surface area vs the interior flow area.

    Yes a small pipe has less surface area for heat loss, but it can carry much less steam. A large pipe although it has a greater surface area, it has a MUCH greater capacity to carry steam, so the ratio is more favorable.

    NJ Steam Homeowner.