New Caleffi 132 Balancing Valve / Flow Meter Not Showing Flow. Missing a Part?

Options
crj
crj Member Posts: 1

I recently replaced the 60 year old gas boiler on a large 4 loop Monoflo system. The loops are 1" steel pipe in the basement and 1/2" copper risers to the convectors. I had them use 3/4" Taco ZoneSetter valves, since they have higher Cv than the 1" version.

I had the tech install a Caleffi 132 1-1/4" 5-19 GPM flow meter in the supply as a sanity check on the flow through the system with various combinations of zones open.

I have a Taco 0011 pump, so I figured that I would have at least 5 GPM to register flow on the meter. With the shortest zone only, I get no measured flow, and with all 4 zones open I get no measured flow. The system heats fine and the circulator sounds fine, so there is definitely flow.

The installers had never installed one of the valves, since I asked for it to be installed. When they took it out of the box, a cylindrical brass piece about 2" long and 1" in diameter fell out from inside the valve. It had an O-Ring and on the flat end and a conical flare on the other. I saw the part sitting on top of the boiler, so I'm almost positive that they installed the valve without the cylindrical insert in place.

My guess is that this piece not optional and that it is it required to provide the pressure differential that drives the flow meter. Does anyone know if this is the case?

Is there any possibility that a Taco 0011 would not provide a flow above 5 GPM with all 4 zones open?