I recently replaced the 60 year old gas boiler on a large 4 loop Monoflo system. The loops are 1" steel pipe in the basement and 1/2" copper risers to the convectors. I had them use 3/4" Taco ZoneSetter valves, since they have higher Cv than the 1" version.

I had the tech install a Caleffi 132 1-1/4" 5-19 GPM flow meter in the supply as a sanity check on the flow through the system with various combinations of zones open.

I have a Taco 0011 pump, so I figured that I would have at least 5 GPM to register flow on the meter. With the shortest zone only, I get no measured flow, and with all 4 zones open I get no measured flow. The system heats fine and the circulator sounds fine, so there is definitely flow.

The installers had never installed one of the valves, since I asked for it to be installed. When they took it out of the box, a cylindrical brass piece about 2" long and 1" in diameter fell out from inside the valve. It had an O-Ring and on the flat end and a conical flare on the other. I saw the part sitting on top of the boiler, so I'm almost positive that they installed the valve without the cylindrical insert in place.

My guess is that this piece not optional and that it is it required to provide the pressure differential that drives the flow meter. Does anyone know if this is the case?

Is there any possibility that a Taco 0011 would not provide a flow above 5 GPM with all 4 zones open?

Chris

Comments

  • mattmia2
    mattmia2 Posts: 18,399
    edited August 3

    Looks like there should be a venturi in the body of it and you have to pull the ring for it to read anything:

    https://www.supplyhouse.com/Caleffi-132772A-QuickSetter-Balancing-Valve-with-Flow-Meter-1-1-4

    How is the balancing valve set? if it is closed or partially closed you could have less than 5 gpm.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,328

    @crj

    @hot_rod

    is the Caleffi expert on this site and I am sure he will see this post and respond shortly.

    I agree it sounds like that part needs to be installed.

    Maybe the attached will help.

  • hot_rod
    hot_rod Posts: 28,699

    It takers a bit of force to get this spool out of the body? Matt took on off the shelf to see how it would disassemble.

    Was it separated in an unopened box?

    It definately needs to be in the body to read.

    Screenshot 2026-08-04 at 11.31.24 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    crj
  • mattmia2
    mattmia2 Posts: 18,399

    i'd imagine unless there is something supporting it that bouncing in a truck for a few hundred miles at just the right angle could pop it out of there.

  • GGross
    GGross Posts: 2,104

    You'd have to see how they are in the box, not entirely supported necessarily, but they are wrapped in a form fitted foam insulation and pretty well secure. I would have never even known that part could come out if I didnt just see it for myself and i sell a couple dozen of these each year. I'd think its a bit more than bouncing on the roads. either a factory mistake or someone took it apart, put it back in the box and returned it to the vendor.

    mattmia2
  • hot_rod
    hot_rod Posts: 28,699

    Did he question what the part was for if it was separated when he opened the box?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    GGross
  • crj
    crj Posts: 4

    Bob,

    Thanks for the answer and the picture! The cylindrical part on the right is exactly the part that fell out of the box when it was opened. The box and the valve looked new. It was ordered from a highly rated online supplier, so it did get a bit of "truck time" during delivery.

    I verified with the contractor that it was not installed. During installation, looking at the installation videos they saw nothing about installing the "extra" part. Looking at the installation instructions myself, it seems that it is not ever expected to fall out, since it was not obviously called out as a separate part.

    Could the part getting dinged up by rattling around inside the box during shipping affect the ability to re-seat it or the measurement accuracy?

    Looking at the cutaway view below from https://www.caleffi.com/en-us/blog/how-clean-balancing-valve , presumably the part goes in flat end first? Does the rotational orientation matter at all, i.e. does the slot in the cylinder need to point toward up as shown in the cutaway view?

    image.png

    Chris

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,328

    How could an "installer" install something with parts "left over" and not question whether they were needed or not?

    Yeah sometimes you buy something that has multiple adapters or something that you don't use all of them but geeze.

    GGross
  • mattmia2
    mattmia2 Posts: 18,399

    the instructions show it in the diagrams but don't mention it as a part that could be removed, it is kind of confusing even if you are looking at the instructions trying to figure out if that should be put back in there. they should understand that you need a restriction to measure flow by pressure differential but i can also see someone doing ok on moderately complex residential stuff without quite grasping that.

  • crj
    crj Posts: 4
    edited August 5

    The plumbing contractor has in general been great to work with. Except for the flow measurement valve, everything works great. Most contractors I talked with would not install a part that they had not used before. I give these guys credit for trying something new. Unfortunately, they were thrown a curve by the part falling out. The documentation could have certainly been better regarding the insert. They have owned up to the problem and are working to make it right.

    JohnNY
  • hot_rod
    hot_rod Posts: 28,699

    I looked at a few I have here.

    It looks like a tool puts 4 indent marks into that inner piece that lock it into a groove in the body. It may be hard to see in these pics? Like maybe a 4 sided star punch pushes some brass into the groove?

    You can see that groove in this cut away, with the spool just above it.

    It takes some force to push it out.

    I'll see if I can get the factory tomorrow to understand how it goes and stays in.

    Certainly it is under warranty if you can remove and return it.

    Sorry about the hassle.

    Screenshot 2026-08-04 at 7.29.30 PM.png Screenshot 2026-08-04 at 7.29.17 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2crj
  • mattmia2
    mattmia2 Posts: 18,399

    circling where it is staked might help. i can't tell what is a spot of corrosion and that is the indentation where it is staked. a macro lens would help too.

  • 109A_5
    109A_5 Posts: 4,759

    I suppose the venturi could be crimped once fitted into place, the purpose for the groove near the O Ring. If it is crimped in there is no taking it apart to clean the slots.

    I'm surprised the O Ring would not hold it in place (Orange Arrow). How well would the O Ring seal if the venturi could just fall out ? I'm thinking it was just not properly seated past that slight shoulder on the inlet side (Yellow Arrow).

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    crj
  • Jamie Hall
    Jamie Hall Posts: 27,975

    No idea how that piece could fall out — but I can assure you that the flow meter will register zero flow with it out of there, and it has to be installed the way around shown.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • crj
    crj Posts: 4
    edited August 6

    It's definitely installed with the flow in the direction of the arrow. There certainly will be SOME pressure drop without the insert, but nowhere near enough to move the indicator. It will be interesting to see what the measured GPM is when the replacement valve is installed. I can't imagine it will be less than the 5 GPM minimum value on the meter scale with all four 1" zones open and a Taco 0011 circulator.

  • hot_rod
    hot_rod Posts: 28,699

    $ zones? What kind of gpm are you looking for?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    the pressure drop won't be between the sampling ports of the flow meter though, it will be at the inlet of the fitting, at least other than the tiniest loss due to friction on the walls of the fitting.