In Floor Loop Design
Hi,
Just looking to see if my loop design is correct for a small home we are building.
Attached is a floor plan and the design I created. If anyone has experience with loop design and can provide some feedback it would be greatly appreciated.
Thanks
Bruce.
Comments
-
Where is the rest of design?
Heat loss?
Loop lengths, and flow rates?
Are these loops in a slab, a build up with warmboard or similar material, or staple up with plates?
What are the floor finishes in each room?
Etc.On first look the utility room and the bathroom are wrong and will most likely result in uneven heating. And it’s definitely not a good idea to run tubing under the toilet flange.
0 -
Heating the closet?
0 -
The utility room and hall probably do not need much tube
The runs down and back to the bed room may be sufficient in the hall
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
the heat loss is 9,102 btu/hr
runs
LoopArea
Plotted length
Z1-L1
Office and bathroom
179.0 ft
Z1-L2
Bedroom
182.6 ft
Z2-L1
Kitchen and utility
138.0 ft
Z2-L2
Hallway and mud room
136.2 ft
Z2-L3
Living A
121.1 ft
Z2-L4
Living B
117.7 ft
0 -
Ideally, you will want to come in and out of the rooms through doorways and not under walls. Nails through bottom plates can snag and penetrate the tubing.
And when you go through the doorways, crowd the tubing together in the middle of the opening to allow for threshold nailing at the ends.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
The less 180 turns , the easier to install. Especially on mesh for a slab pour
I typically do the outside walls first, an L shape loop. You could go through doorways also.
Basically I look at the loop lengths every room needs and adjust the loops as you go, getting all the tube required into the space
You will maybe get 6 different opinions, at days end they will all work
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
-
Tube spacing is important. Even when 12" spacing would satisfy the design, I would install at 9" to be able to lower the supply temperature to allow for greater boiler efficiency with a condensing boiler.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
For a small job, short loops I would even go 6" on center. 3/8" tube is needed for the best 6" design.
If it is a slab, elevating the tube helps performace and efficiency, also.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 122 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements