I probably should start by saying that I realize this thing is both
ancient and dirty, I do plan to clean it up as I'm working on it, but at
the moment not interested in replacing it if it can be fixed.

Turned it on a couple days ago, realized it wasn't putting out cool air,
started trying to figure out the problem. What I know so far:

Heat Controller Inc. model# UCS60-1B

- Looking at serial number guides I think it's from 1981 but I'm not
sure, although I found a video on Facebook of a very similar unit that
seems to confirm the year.

- Air comes out of the vents inside when it's turned on, initially very mildly cool but it quickly gets warmer.

- Fan on the outdoor unit is stopped.

- The lines going inside are both ambient temperature.

From what I've read the first thing to do in this situation is try a new
capacitor. The problem is I don't know how to open it. The copper lines
are running into what appears to be the panel, I didn't come across a
video or guide or anything that looked similar so I'm hesitant to just
start taking things apart. There also isn't an outside box to cut the
power. Is it enough to turn it off inside and shut off the breakers?

Any help would be appreciated!

IMG_4336.jpg IMG_4314.jpg

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,402

    Take the screws out and the panel should wiggle out and the wires should be long enough so you can get inside. Make sure all the circuit breaker for the unit is off. Or call a pro.

  • GW
    GW Posts: 5,289

    or put a box fan on top and let it rip.

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    EdTheHeaterManIronman
  • mattmia2
    mattmia2 Posts: 18,484
    edited July 4

    is the compressor running in the outdoor unit?

    i'm not sure but it looks like the panel to the left of the electrical connection and linesets is removable, not the one with that stuff mounted to it.

    even in the 70's a disconnect was required within sight of the appliance.

    i think the oem of that was also the oem of the stuff sears was selling in the 70's

    or maybe the top lifts up

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,402

    Heat Controller was Comfort Air and I think some other names. Last I knew it was still around.

  • HydronicMike
    HydronicMike Posts: 486

    If you don’t know how to get access, you really shouldn’t be messing with it. There’s some high voltage in there and either you could do more damage or seriously hurt yourself.

    Ironman
  • HVACNUT
    HVACNUT Posts: 7,838

    Does the system ever get serviced? This isn't DIY. You say the fan on the outdoor unit is stopped. What about the compressor? The refrigerant lines being ambient temperature means either the compressor is not running, or there's no refrigerant in the system.

    Have you checked the circuit breaker? Is it tripped? Is the disconnect (outside box to cut the power) fused? Did a fuse blow? If the breaker is tripped or a fuse is blown, you'll need an HVAC pro. And personally, I wouldn’t put more than $25 into a repair on something so old. Time to replace. Maybe think about a heat pump for the shoulder seasons if electricity is cheaper than fossil fuels near you.

    Ironman
  • pecmsg
    pecmsg Posts: 7,664

    Is the disconnect (outside box to cut the power) fused

    I don't see any disconnect outside. That's been code for as long as i remember.

    Unless the homeowner is experienced, I wouldn't recommend touching it!

    Ironman
  • Ironman
    Ironman Posts: 7,980

    I agree: if you don’t even know how to gain access into the unit, this isn’t something you should be attempting to repair.

    Guessing that it’s a bad capacitor because that’s what you read on the internet is not how we diagnose equipment.

    Please, call a competent HVAC pro: this is not something that you should attempt.

    Bob Boan