Where can I find a more complete formula for calculating radiant floor output which accurately accounts for tube spacing, heat spreader, water temperature, flow rate and floor covering R-value?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 27,577

    A single formula is not going to do it. That is not to say that the temperature of the radiating surface (the floor surface exposed to space, which is the governing variable in heat transfer to the space) can't be modelled — it can, and all the items you mention factor into the models. Several firms have the capability of doing this more or less accurately for you — at least two pop up on The Wall from time to time and may see this thread.

    That said, a calculation which comes within 10 percent is going to be the best your can hope for in a real world situation.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hot_rod
    hot_rod Member Posts: 27,824

    Any radiant panel output is based on the floor surface temperature and the ambient air temperature of the space.

    In a residence you want to keep the floor surface below 82° or it becomes uncomfortably warm to bare feet.

    So here is some math for various radiant panels, floor, wall and ceiling. From Caleffi Idronics 25

    So for a room at 70° ambient with average floor surface of 82, 82-70 X 2 = 24 btu/ sq ft output.

    Often when you see higher floor output it is because the room temperature is lower. At 65 ambient

    82-65= 17X 2= 34 btu/sq ft. That may be fine for a shop, but a little cold for me at 65°

    Screenshot 2026-06-18 at 5.15.04 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Jamie Hall
    Jamie Hall Member Posts: 27,577

    Thank you, as always, @hot_rod . For @dcwittlo , that is exactly the kind of approximating approach to which I was referring. As the reference notes — and I noted — going from the variables which you mention to the heat output can also be estimated using various sources — but to get to anything much better than 105 you are going to have to go to finite element heat transfer modelling. And you don't want to do that…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hot_rod
    hot_rod Member Posts: 27,824

    Under a wood floor the subfloor and any final coverings subtract out.

    From Uponor

    Screenshot 2026-06-18 at 8.01.37 PM.png Screenshot 2026-06-18 at 8.03.31 PM.png

    Thjerse infrared show the challenge getting the entire surface a consistent temperature. From left copper tube in 4" extruded aluminum plates

    Suspended tube

    Staple up EPDM

    Pex in 4" extruded plates

    Warmboard.

    The back 1/2 of each sheet has berber carpet, no pad

    The RadPad calculator is another way to run some output options.

    Screenshot 2026-06-18 at 8.04.50 PM.png Screenshot 2026-06-18 at 8.11.08 PM.png

    I do have some FEA models also, but the story is the same.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2DCContrarian
  • mattmia2
    mattmia2 Member Posts: 17,462

    what are the 2 cooler circles in the warmboard?

  • dcwittlo
    dcwittlo Member Posts: 14

    OK, now we are getting somewhere. Next part of the calculation is: How many BTU/hr/ft^2 if one is given the spacing of PEX tubing, flow rate thru tubing, supplied water temp of tubing and maybe the width or area of the aluminum heat spreader. Does it much matter how thick the aluminum is?

  • dcwittlo
    dcwittlo Member Posts: 14

    Sorry, my last post was a little late. I think you already answered these questions.

  • hot_rod
    hot_rod Member Posts: 27,824

    I routered across the sheet to make a return bend for another project.

    It clearly shows the conductivity of the aluminum

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • hot_rod
    hot_rod Member Posts: 27,824

    The grip on the Pex is more important than the thickness of aluminum plates. The extruded plates grip so well that you need to tap the tube in.
    The thin flashing thickness plates can make some noise as they warp and the tube slides. A creaking noise from tube movement, an “oil can” noise as the plates expand and contract. Thin plates work if you lock them between layers of wood.

    Another key is to use a boiler or mixing device with outdoor reset so the plates don’t see wide temperature swings. Constant circulation is ideal.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • DCContrarian
    DCContrarian Member Posts: 1,511

    @hot_rod: Thanks for posting those photos, very interesting. Is the temperature scale the same for all of them? Because I'd expect the Warmboard to be noticeably warmer and evener than the plates, and it doesn't look that way. I'd also expect the copper pipe with plates to out-perform PEX, but that doesn't seem to be the case either.

    Interesting, it looks like the carpet does more to reduce output on the Warmboard than on the plates.

  • hot_rod
    hot_rod Member Posts: 27,824

    What you see with the Warmboard may be the 12” spacing. All the others are 8” on center in a 14” joist bay, so the heat stripping is more pronounced.

    Same SWT, same flow, same room ambient temperature.

    Notice that the carpeted back half reduces the surface temperature, but it does also spread the heat across the surface a bit also.

    The most consistent temperature spread I witnessed was the early SolaRoll mat systems. Both the width of the mat and the counterflow flow path with a hot supply next to a cooler return across the mat did the job well.
    Dealing with 5/16” non barrier tube was another story,