A second floor shower pan drain seal leaked. It did quite a bit of damage to the first floor ceiling. The “no caulking required” seal was only a few years old. Either the manufacturer changed the size or the first one shrunk.

IMG_2241.jpeg
«1

Comments

  • hot_rod
    hot_rod Posts: 28,699

    Or is it the shower pan to clamping ring seal that is leaking?

    Plug the drain and flood the shower to the curb threshold. If it leaks it may be the pan installation.

    After you replace the seal :)

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    it didn't shrink so much as it was forced in to that smaller diameter between the drain pipe and drain and hardened that way as it aged. it could have shrunk after the pipe was no longer in the middle of it but i suspect it was compressed that way in use and just fossilized like that.

    Lyle {pheloa} Carter
  • skyline137
    skyline137 Posts: 85

    The seal came with the shower base. The pan and seal were the same brand. I don’t know why it shrank. It did last longer than the 1 year warranty. I’m not using that brand seal again I’ll try something different and put a bead of silicone around the pipe first.

  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    I always installed them with Marine-Grade Silicone on all sides and neatly wiped off excess. Added leak prevention. Mad Dog

    skyline137kcopp
  • skyline137
    skyline137 Posts: 85
  • skyline137
    skyline137 Posts: 85
    edited May 19

    The leak happened a few months ago. I thought it was interesting that a seal that came with the pan actually didn’t. I replaced it with a toilet tank to toilet gasket. It’s not leaking as observed from the hole in the ceiling underneath. I wanted to make sure before ceiling was repaired.

  • Larry Weingarten
    Larry Weingarten Posts: 4,210

    Hi, If it isn't too, too ugly, I'd put an access hatch in that ceiling. That way, the shower will never leak again. 😉

    Yours, Larry

    mattmia2Alan (California Radiant) Forbes
  • mattmia2
    mattmia2 Posts: 18,399

    there are access panels that are designed to install in a hole you cut in the celling after the ceiling is installed, they have a flange that covers the edge of the hole instead of being mudded in. unless this is in like your living room or dining room or a bedroom where you'd rather not think about there being a hole there.

    PC7060
  • JUGHNE
    JUGHNE Posts: 11,653

    I have used a cold air grill to cover the uglies. The wall face type not the baseboard.

    PC7060
  • skyline137
    skyline137 Posts: 85

    I need to replace a 3’x4’ piece of if sheetrock in the first floor kitchen and repaint. The house is 70 years old and has be remodeled a few times. Card board and a staple gun works for now.

    IMG_5994.jpeg IMG_6095.jpeg
  • hot_rod
    hot_rod Posts: 28,699

    Is it a moulded one piece shower base? Or a tile floor with a pan liner below.

    Looks like a creative homemade P trap?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    looks like it does not meet code. makes one wonder what is happening at the shower pan.

  • skyline137
    skyline137 Posts: 85

    It’s a moulded plastic shower base which replaced a 60 year old tile shower floor during a bathroom remodel. The seal obviously shrank and no longer sealed as can be seen by the first side by side photo. That seal came with the base same brand as the base.

  • mattmia2
    mattmia2 Posts: 18,399

    normally it would be compressed between the drain and pipe and clamped in place in some way to keep the synthetic rubber compressed between the 2 usually either with a plate and some screws or a compression ring that screws in to the drain

  • skyline137
    skyline137 Posts: 85

    The rubber seal is friction fit between drainpipe and pan as in the image

    IMG_6100.jpeg
  • mattmia2
    mattmia2 Posts: 18,399

    that is terrible design. not only is there nothing to compress the gasket, the drain is on the outside of the pipe instead of the inside so even the slightest amount of leakage is dripping down to the floor below rather than in to the pipe.

    skyline137
  • skyline137
    skyline137 Posts: 85

    It is a terrible design especially when the seal shrinks. The

    IMG_6102.jpeg

    type of seal in the image with RTV silicone is a tight fit and has not leaked in a few months. I’m having some rooms painted in a few weeks and it will be repaired.

  • I've had pretty good luck with the gaskets that come with the shower drains. They typically come with a threaded compression ring that you tighten down with a key.

    image.png
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    mattmia2Larry Weingarten
  • jumper
    jumper Posts: 2,625

    I have also. If leak is minor enough it may evaporate.

  • jumper
    jumper Posts: 2,625

    »that is terrible design. not only is there nothing to compress the
    gasket, the drain is on the outside of the pipe instead of the inside so
    even the slightest amount of leakage is dripping down to the floor
    below rather than in to the pipe.«

    Yes indeed. There are deck drain systems that feed into a funnel so that any water getting past the primary strainer still end up in drain pipe.

  • skyline137
    skyline137 Posts: 85

    Bad design aside. I sent a photo of the leaking seal to the manufacturer of the shower base and seal. The seal on the left is smaller than the replacement I bought. The part number is the same. It can be see by zooming in. I don’t know if the original on the left shrunk or they made it larger in size. I

    IMG_2241.jpeg

    got no response. I have $700 damage from the leak. My insurance is $1,000 deductible.

  • hot_rod
    hot_rod Posts: 28,699

    With that homemade trap, maybe the pipe going through the pan is not perfectly plumb? So the gasket is not sealing as designed.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2Alan (California Radiant) Forbeskcopp
  • mattmia2
    mattmia2 Posts: 18,399

    without a lockring to compress the gasket in place as the pipe and the shower pan expand and contract and move it is likely to slowly push the gasket out as they move around.

    i wonder if you could cut out the molded in drain and clamp on a drain of a better design, of course you also have clearance issues in the ceiling.

  • skyline137
    skyline137 Posts: 85

    The home made trap is because the drain was exactly over the 3” wide joist and the tile guy was coming in the morning. The 2” pvc is level and the toilet tank gasket is working great. It’s a tighter more secure fit than the one supplied with the base.

  • pecmsg
    pecmsg Posts: 7,634
  • mattmia2
    mattmia2 Posts: 18,399

    it doesn't seem that there is anything of substance to retain the seal in place and both the pan and the pipe are going to change size a lot with temp, that part does seem to be a design issue.

  • skyline137
    skyline137 Posts: 85

    I didn’t get an answer from E.L Mustee as to why or if they changed the size of the gasket. If the gasket was made larger then it may have worked better but I didn’t want to chance it

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,328

    Seems to me it is like a doughnut you use in a CI hub when replacing CI with PVC or ABS. The drain pipe expands the gasket.

    @skyline137 did you measure the gaskets to see if there is any difference?

    The old one does look smaller.

    wvmountains
  • mattmia2
    mattmia2 Posts: 18,399

    but using a doughnut instead of caulking hub and spigot cast iron the pipe slips inside the hub and doesn't have someone walking on it and in a lot of cases has gravity in its favor.

    for this it would be like if you extended a piece of 4" ci by slipping a piece of 6" ci over the top of it from above and jammed a doughnut in from the bottom.

  • pecmsg
    pecmsg Posts: 7,634

    That gasket needs something on the outside to hold it in place as well as the pipe inside!

    Installation Error!

  • mattmia2
    mattmia2 Posts: 18,399

    i think it is a design error because el mustee/owens corning makes fixtures, not fittings.

  • hot_rod
    hot_rod Posts: 28,699

    Those Muster and Swan brand shower bases have been around for years with those gaskets they generally work just fine

    Aggressive water could break down certain rubber blends causing them to get brittle

    There may be a tolerance difference between the ABS/ PVC and the CI versions

    Have you seen how freestanding tub drains assemble? You set the brass tub tailpiece down into an o ring, which you may not even see from below. A dab of silicone grease to help it slide in place

    If the shower bases flexes at all, that could be a problem. I like to spray foam under them for support and noise suppression

    Weight them down first😲

    IMG_2526.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    2 tight fitting sleeves that fit inside each other with an o-ring in a groove on one of them would be 1000x more secure than that doughnut jammed in between the pipe and the shower pan. everything on a car has worked like that for about the past 40 years.

  • hot_rod
    hot_rod Posts: 28,699

    WOW! 1000X, got some data to back that up?

    At days end the correct, product and correct installation the factory supplied "donut" should be adequate. It's not a pressure seal as a tub full of water presents, even at flood rim.

    I would trust it more that a foam or rubber toilet tank gasket.

    Top of the pipe cut straight? Donut tapped down as shown? Bedding under the pan as shown?

    Screenshot 2026-05-20 at 8.20.33 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    even if the pan is bedded especially pvc pipe is going to expand and contract a lot. i wouldn't trust any of those things without the ring to compress it that @Alan (California Radiant) Forbes showed

  • mattmia2
    mattmia2 Posts: 18,399

    it is also possible that for any number of reasons those weren't made out of the compound that was specified

  • skyline137
    skyline137 Posts: 85

    A lot of people have had problems with this type of installation. That seal is the most likely place to leak. Bad installation is definitely a problem with that gasket. In my case I think the size of the original gasket was the cause of the leak. I would have noticed the leak sooner if there wasn’t a second sheet rock ceiling covering the original ceiling in the converted garage. Water pooled and came down all at once. I used a different seal (toilet bowl to tank gasket) it definitely works better it

    IMG_6104.jpeg

    hasn’t leaked in a few months use. I feel confident enough to get the ceiling repaired now.

  • hot_rod
    hot_rod Posts: 28,699

    there are 3 different gaskets, maybe it shopped with the wrong size for PVC?

    Any part number on it?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • skyline137
    skyline137 Posts: 85

    The reason for the original post was about the part number on two supposed identical gaskets. The gasket on the left leaked. I don’t know if it shrank or came that way but it’s definitely not the same size as the one on the right.

    IMG_6106.jpeg IMG_6107.jpeg

    If you ZOOM in the part number is the same.

  • mattmia2
    mattmia2 Posts: 18,399

    does the new gasket just slip in or does it get smaller when you slide it in there? as most synthetic rubbers age they harden and will take the shape they were confined to