Y-Pipe strainers
This is a hydronic boiler system in a school in Denver. The system is from the 1960's, the boiler and near boiler piping was replaced in 2015.
There is a Y-pipe strainer before the circulator and another after the circulator both 2" pipe. The one before (china) closes down to about 1 1/2" size strainer, the one above (Italy) does not. Just cleaned them out and the strainer above the circulator is without a strainer. The one below was fairly clogged with sludge after a year.
Question; should I do something different about this setup? Change the strainer to the larger one above the circulator, add a strainer to the one above, or leave it alone?
Comments
-
the ones above the pumps look like Y pattern swing check valves
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Are these pins / shoulder bolts what gives it away?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
The ones above the pumps aren't strainers — they are check valves. Or werent'. I hope the innards of the check valves are still there???
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Ok. I see.
Thanks for the help.
Nothing inside them that I could see easily, But I will check again.
edit: I read up a little and the cap is for 'easy maintenance'. What maintenance do these need?
0 -
-
You may need to do a system flush, add clean water and a hydronic chemical if you have chronic sludge issues. A Y strainer that plugs will starve the pump of flow and can cause a pump failure.
More and more systems are getting dirt separators instead of strainers. More capacity, better performance and easy to blow down.
Typically one at the boiler return.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
On Y strainers it's quite handy to put a blow down valve on them so you or building staff can blast out the shmutz more frequently, but like @109A_5 mentioned, they shouldn't really be installed upwards like that since they wont work properly that way
1 -
The ones above the pumps are check valves for sure.
0 -
some things to avoid with circulator piping.
No flow restricting devices on the inlet side
A section of straight pipe upstream and downstreamPump away from an expansion tank
A blow down valve is a good idea for occasionally serviced.
If the system has sludge or magnetite you usually need to remove the strainer and scrub it clean. To fine of mesh can cause more problems than it solves.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements