Great point , think you figured this out! the original paddle definitely had some play in that valve. It wasn’t noticeable with the new paddle and 0 rings. The 0 rings were worn out in the original paddle so there probably was some metal to metal contact. The close up photo shows wear in the bore. It didn’t come from the factory that way! Thanks for your input.
0 -
You were right about the bore being worn. I had to really get a close up to see it. Thanks for your input.
0 -
wear on the shaft has more to do with a leak around the stem. The spring will pull the paddle tight enough for the few psi that your system pump develops. Even with a few thousands of wear or play in the shaft
If the old paddle had a good imprint, then it was sealing.
If the paddle gets brittle after time and a chip come out like your early post showed, then you can get leak by.
If something else is going on like some reverse flow condition, you may need to wait until all zones are running and the system gets hot.
Ghost flow and reverse circulation (gravity flow) like discussed below is usually a thermally driven condition, hot water rising up, cold flowing down in the same pipe even with a flo control or zone valve on the system..
In some rare cases you need a zone valve and a check on the other side of the circuit to stop ghosting
This is usually a very slow condition, more apt to see if the system is running long hours, design condition days, maybe. Or always hot boilers like tankless coil installations.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I’m going back some now to when I fist discovered this. The furnace was cold and I put one hand on zone 1 and one hand on zone 5. I had my wife put the thermostat for zone 1 on 80. Inducer, boiler and zone 1 light turned on then circulator, light on zone 5 didn’t light. Both zones got equally hot. Within a minute it was too hot to keep my hand on either. The same result with every zone or hot water. I don’t know if the timing matters but that’s what happened. I tried everything nothing worked. 5 new valves and actuators did work. Hey, they were 17 years old anyway!
0
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 127 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements