2 stage vs 1 stage furnace
I am looking at Lennox ML180EK 66,000 BTU and EL280EK 88,000 BTU models.
Is there any reason someone would take a 1 stage model over a 2 stage?
The way I understand it, the Elite would operate at 66,000 in Stage 1 unless it needed more power and only then would kick into stage 2.
I have a basic Google Nest, do I need anything different if I get the 2 stage?
For context, my current furnace is 88,000 but short cycles due to being oversized. I’m looking to downgrade in terms of power, but think it could be worth it to keep extra kick for the really cold days.
    HVACNUT Posts: 7,784
    Unless the Nest has a W2, second stage kicks in either 7 or 12 minutes into the cycle depending on a Dip switch setting.
    To answer your question, if my heat loss was 66K, I wouldn’t install one capable of 88K.
    Do a heat loos calculation and install the correct size furnace. Not sure I would bother with 2 stage with a 60-80K heat loss. More parts to go bad.
    Robert_HHot_water_fan
  • pedmec
    pedmec Posts: 1,488
    Is there a reason to buy a single stage over a two stage? There sure is, $. Why would you install a two stage unit in an investment property? You don't get the savings. The tenant would. You pay more for a 2 stage unit.
    If your unit is oversized your wasting money and ruining the controls by allowing short cycling. The ignition sequence, like everything else, has a life span cycle. The more it cycles the less time it will last. How long do you think your car starter would last if you shut the car off at every red light, and then start it up again.
    Also long run cycles allow for the maximum efficiencies. i think you need to define short cycling.
    EdTheHeaterMan Posts: 12,940
    @2lefthands said:
    "For context, my current furnace is 88,000 BTU but short cycles due to being oversized. I’m looking to downgrade in terms of power, but think it could be worth it to keep extra kick for the really cold days."
    If that is happening on really cold days, then you should consider using the proper size furnace. When you are at design temperature outside (AKA: the coldest day of the year used for heat-loss calculations) and your furnace is still short cycling, then you probably do not need an 88,000 BTU furnace on the coldest days of winter.
    You might be better served by the EL280E070, which has a high fire of about 66,000 BTU input and a low fire of about 50,000 BTU input. It can run on the 50,000 BTU stage for most of the winter and only go to 66,000 BTU when you need the extra kick. That should make the cycles longer.
    The goal is to reduce short cycles and turn them into longer cycles, and that is done by using a smaller firing rate. Think of it like this: if the 88,000 BTU furnace short cycles on the coldest days, for example 5 minutes on and 5 minutes off, then the burner is only operating 50% of the time. That means it is effectively delivering about 44,000 BTU per hour (88,000 × 0.5). If your short cycles are 6 minutes on and 3 minutes off, the burner is on two-thirds of the time, so the effective output is about 59,000 BTU per hour (88,000 × 0.67).
    Both of those numbers are still in the range where a smaller furnace could likely handle the load, especially one with a lower first-stage firing rate.
    Not until you get cycles of something like 10 minutes on and 3.5 minutes off (roughly 74% burner runtime) would the effective output approach about 65,000 BTU per hour, which is close to the high stage of the 66,000 BTU furnace. This means that the low stage will operate constantly at 50,000 BTU and only step up the 66,000 BTU for short "kicks" keeping the combustion process on constantly which is a more efficient way to operate a furnace. Not 88,000 on then off then on then off then on then off... A 50,000 always on to keep you comfortable without any off cycles is much better.
    Question: So when you experienced the operation of the current 88,000 BTU furnace on the coldest winter days, how long were the on/off cycles?
    i have an about 75,000 btu/hr 2 stage in an 800 ft^2 house which is probably quire oversized. It has a honewell 2 stage t-stat. It only runs 2nd stage when it is recovering from setback.
    the 2 stage makes it run longer cycles on non design day conditions which keeps the temps more even especially if the ductwork is less than ideal.
    I would like @EBEBRATT-Ed said do the heat loss and get a furnace about that size but i would do the 2 stage or a modulating and control it with a good 2 stage stat so the second stage doesn't kick on unless it needs it. i don't like the built in second stage runs on a timer.
  • 2lefthands
    2lefthands Posts: 18
    not an investment property, my home for at least next 10 years.
    Current heat will run for max 5-7 minutes, flames shut off, blower runs for another 2, shuts off, process restarts.
    Price diff between these 2 models is negligible - I just want the best unit to handle avg cold days and super cold days.
    I’ve also been told by everyone: undersized ducts
  • 2lefthands
    The current 88,000 has short cycled from the time I moved in - 2 years. I recently discovered it has a cracked heat exchanger - that’s why I’m getting a new one.
    Cycle: run for 5-7min, flame goes out blower only for another 3min, then everything off, then restarts. Typical heat settings 68 at night and 72 during the day.
    pecmsg Posts: 7,634
    edited April 4
    when at “design“ conditions that furnace should run nonstop. Seeing as you’re actually at “design“ conditions less than of the time that furnace is oversized 99% of the time
    “Design“ conditions is not the coldest day of record!
    Your short cycling timing indicaters taht you have an effective yield of no more than 66,000 BTUh if that is how your system is operating. With that information, does your home stay at the desired set point temperatures when the outdoor temperature is at its coldest? If you home stays comfortable even when the temperature drops below the normal coldest days, then you do not need an 88,000 BTU heater.
    Your existing heated is already working like it is a 66,000 BTU Heater when the 88,000 gas burner can only operate for 7 minutes our of every 10 minutes. You would be better off putting less heat in your duct work if it is undersized. 50,000 BTU would be better for you and the undersized duct work. The only kick you need is the additional 16,000 BTU when it gets really cold.
  • 2lefthands
    Low fire on this one looks to be input of 43,000 and output of only 35,000 - that seems insufficient. Unless I’m reading the chart wrong.
    EXACTLY RIGHT: That 43,000 BTU stage is insufficient for a very cold day. If you were in New Jersey, where I used to work, those coldest days could be below 0°F, and keeping the indoor temperature at 72°F was the job of the high fire stage. But we only saw temperatures below 0°F about once every four years or so, not every day of the winter. So to get the home to 72°F when the outdoor temperature is 0°F, you might need 66,000 BTU/h for about three or four hours every three or four years. Other than that, you don’t need 66,000 BTU/h.
    The 43,000 BTU burner is not for those extreme days. That burner is for most of the rest of the winter.
    For example, when it is 40°F outside, the house might only need about 22,000 BTU/h, and the 43,000 BTU stage is almost double what you need. When it is 30°F outside, you might need about 35,000 BTU/h, which is still less than 43,000 BTU/h.
    Now when the temperature gets down to 20°F, that 43,000 BTU stage is too small. But guess what happens? The additional 23,000 BTU burners come on, and suddenly you have a furnace producing about 66,000 BTU/h, even though the house might only need about 48,000 BTU/h. So what happens? the 43,000 burner never shuts off, the most efficient use of fuel, no OFF and ON cycling. The additional 23,000 BTU burner cycles ON to make up the difference then cycles OFF when the temperature at the thermostat gets higher that the set point. The over sized 66,000 BTU burner does not shut off completely, only the 23,000 burner shuts off so the 43,000 burner can keep you comfortable. Much more efficient operation.
    Does that make sense?
  • pedmec
    pedmec Posts: 1,488
    If the Flame goes out and the blower motor stops its because the thermostat is satisfied. That would not be indicative of undersized ducts. That is normal operation. Heat demand, safety check, combustion fan, ignition sequence, flame, heat exchanger warm-up, then blower motor on is the start-up. Shutdown is Thermostat satisfied, gas valve closed flame off, combustion fan off, then after a timed period by dip switch the blower motor will shut off.
    If the ductwork was undersized you can test it by measuring the temperature rise over the heat exchanger. There is a low and high temperature that the manufacturer's recommend that you use to help sizing your ductwork. you can see it on the manufacturer's tag. That is how you get a long life out of the heat exchangers.
    What i like to do is work backwards. Determine what my ductwork can handle using recommended static for residential installs and then using the sensible heat equation to see the maximum temperature rise over the heat exchanger. Then do a heat load calculation and see if it lines up with the existing ductwork. This will determine whether modifications to the existing ductwork are needed.
    Its really kind of critical to size the new furnace to the ductwork correctly if you want your new heat exchanger to last. They really don't make them to last and if you stress it with high temperature rise it's not gonna last. This is an area where they really " don't make them like they used too". It's funny because the competitive models don't handle the the stress like the brand name units but if you stay within the temperature rise area they will last just as long.
  • bjohnhy
    bjohnhy Posts: 220
    Your cycle description does not state the duration of how long is "everything off"? And is this cycle time typical of the coldest nights or design temps?
    Try doing this calculation if you can, make sure it matches with numbers you are considering https://www.greenbuildingadvisor.com/article/replacing-a-furnace-or-boiler
    Hot_water_fan
  • Sal Santamaura
    Sal Santamaura Posts: 547
    "…How long do you think your car starter would last if you shut the car off at every red light, and then start it up again…"
    In the last two years, between 65% and 72% of new cars sold in the U.S. have been equipped with start-stop systems that do exactly that. 😊
    OK, back to heating. 😀
    bjohnhyEdTheHeaterMan
    edited April 4
    did it not have a nest at some point, did run longer cycles before the nest was installed or was it already there when yo got it. the short cycling you describe seems to be a control problem although it could also be oversized in addition to the control problem. one common failure point of nests is that their battery doesn't get adequate power and it will die during a heat call causing the heat call to end then the battery charges and starts another heat call.
    it could be incorrect anticipator settings/behavior in the thermostat or the thermostat being right at a heat vent too. maybe it could be a safety in the furnace shutting the burner down too.
    bjohnhy
    it seems that gm is intent on testing that. intentionally over with the models of the past 20 years or so, unintentionally with the models of the late 70's through the 90's
    hot_rod Posts: 28,699
    Most homes are at design condition a small % of the year, less than 10%, you can look up temperature info for your location. As such a single stage is mostly oversized. The closer the furnace to the actual load the more efficient and comfortable the home. Below are some examples of temperature data for various cities.
    Any air sealing upgrades will lower the load also. A load calc and blower door test can shed a lot of info on your needs. Most furnaces get over-sized.
  • 2lefthands
    edited April 4
    thank you for this detailed explanation. What is the largest consequence of utilizing a stage 1 furnace that only works at 66k BTU? I assume I’ll waste more gas unnecessarily, but what are the other consequences?
    I ask because I imagine there are more components that can break in the 2 stage model. So maybe effeciency savings are cancelled out by repair costs. Also, I might not mind the “light switch effect” ie on full blast then off vs always on at lower power.
    But if the more frequent on/off with a stage 1 66k is gonna cause other issues, those are the risks I want to understand.
    p.s I’m in NJ and we had a very cold winter.Northern NJ (e.g., Sussex, Warren, Passaic): Likely 30–50+ days with at least some stations reporting lows below 20°F
  • 2lefthands
    These short cycling issues persisted even when the thermostat was disconnected at the furnace and it was basically set to “just work”. Even with the filter box open and empty - it would short cycle.
  • bjohnhy
    bjohnhy Posts: 220
    did it do it before the hx cracked? the cracked hx could be causing the flame to rollout or spill and it could be shutting off on that. it could be tripping a pressure switch.
    it could be that it is too big for the ductrowk but there are numerous other safeties that could be tripping or defective.
    I assume by "just run" you mean you have r-w jumpered at the furnace
    edited April 5
    The “just run” comment likely means the furnace is being operated by jumping the R and W terminals at the thermostat connection on the furnace. Placing a wire between R and W forces a constant call for heat — essentially the same as setting the thermostat to 100°F in a room that will never reach 100°F. In the trade, we simply call this “jumping” the thermostat.
    If that is the case, there is probably an underlying issue. One possibility is that the furnace is oversized for the duct system it is connected to. When a furnace produces more heat than the ductwork can safely carry away, the heat exchanger temperature rises excessively, which can lead to overheating and premature heat-exchanger failure.
    Under normal operation, the thermostat calls for heat and the burner fires, warming the heat exchanger. The blower then moves room air across the heat exchanger, carrying that heat into the duct system. When the duct system is properly sized, airflow is sufficient to keep the heat exchanger within its safe operating temperature.
    During a typical heating cycle, the furnace may run 10, 15, or even 20 minutes or longer, depending on the outdoor temperature. Once the thermostat is satisfied, the burner shuts off and the blower continues running for several minutes to remove the remaining heat from the exchanger. That completes the run cycle.
    The off cycle then begins, during which the home gradually cools until the thermostat calls for heat again. In many homes this entire process may occur once or twice per hour.
    In your case, however, the furnace is running 5 minutes ON and 3 minutes OFF, which forces the unit to cycle as many as eight times per hour. That is far more frequent than the system was designed for.
    Every time the burner fires, the heat exchanger expands from the heat. When it shuts off, the exchanger contracts as it cools. Repeating that expansion and contraction eight times per hour is similar to bending the lid of a tin can back and forth over and over again. Eventually, the metal fatigues and fails.
    The root cause may be that the system is trying to push 88,000 BTU/h into a duct system that cannot carry that much heat.
    Before purchasing a replacement furnace, two questions should be answered:
    1. How much heat does the home actually require?
    2. How much heat can the existing duct system distribute?
    Without determining those two values, selecting a furnace becomes little more than an educated guess.
    You may already have a clue from the cold weather we experienced in New Jersey this past winter. In February 2026, temperatures dropped to approximately −1°F, which is 9 degrees lower than the ASHRAE load calculation guide for that area of 7°F. If your home maintained the thermostat setting of 68°F during that overnight low — even with the furnace short cycling — then the proposed 66,000 BTU/h furnace is probably not undersized. But it might be even better to operate a 43,000 BTU furnace for the lion’s share of the winter, don’t you think?
    For perspective, historical records show that the temperature in parts of New Jersey reached −14°F in both 1935 and 1984. Heating systems are generally not designed for those once-in-50-year extremes. Instead, we accept that indoor temperatures may drop slightly during those rare events and move on.
    And of course, when Governors Harry Hoffman and Tom Kean declared a state of emergency, that apparently fixes everything. (sarcasm) 😄
    I doubt there are more components on a 2 stage, just different components, basically a two stage gas valve controlled by a similar mother-board on the control module.
    Most motors are multi speed, if it has an ECM it will either have multiple or variable speed function, probably controlled by the same circuit board.
    Really the first step should be the heat load. You want the high firing rate as close as possible to the design heat condition.
    there is a little more but I wouldn't use it as a reason to choose between 1 or 2 stage. the control board either has more components or an add on 2 stage board, many times the pressure switches have 2 stages or there are high and low switches, on my lennox the 2 stage inducer is a proprietary lennox part with about a 4x markup.
  • Hot_water_fan
    Hot_water_fan Posts: 2,249
    have we nailed down a fuel usage based heat loss yet? Seems like we are jumping the gun here: you might only need 40kbtu. It is COMMON for furnaces to be 3x oversized.
    I don't think we know if the duct system can handle 40,000 BTUh yet. What we do know it that @2lefthands can't purchase one pair of gloves that fit. He must purchase two pair and therefore has a drawer full of right handed gloves he can't use.
    somehow i have like 4 left handed glove and no right handed gloves in the trunk of my car
    EdTheHeaterManPC7060