Glycol Additives for new Ground Loop commissioning

Options
knobby44
knobby44 Member Posts: 8
edited 4:59PM in Geothermal

Hello. I have a Geothermal system that I am just filling with glycol. I have the radiant side filled and working with my backup Combi Boiler with 30% Dowfrost HD, so that side works great.

I'm getting ready to fill my ground loop (~115 gal capacity) and going to add 35 gal of Dowfrost (30%) and 70% DI water ( I got this for about 10% of the going cost) and wondering if there are additives that I can/should put in the system to make it closer to Dowfrost HD (both use Dipotassium hydrogen phosphate @ 4%-6%). I did see HVAC-1 as a recommendation at 4% solution to glycol, but can't find that in small containers which seems to be 40-50% Tetrapotassium Pyrophosphate and 5% proprietary inhibitors (if it's even available any longer). (need about 1.5 gal)

My system is a 4T heat pump with about 20ft of 1" copper between the non-pressurized pump station and the Heat Pump with a couple brass fittings and the rest is HDPE gound loop (5x 750ft 3/4" HPDE) and manifolds.

Thanks for any suggestions.

Carson City, NV
Mechanical Engineer
Building ICF House

Comments

  • hot_rod
    hot_rod Member Posts: 27,471

    sentential, Rhomar, Nobel and other small “blenders” use Dow as their base and add their own additives. They may know if their boosters are compatible in jwith Dowfrost

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    knobby44
  • Jamie Hall
    Jamie Hall Member Posts: 27,376

    Make sure that ground lop is pressure tested and certified leak gith — I'd want it to hold at least twice the relief valve pressure for at least 24 hurs.

    Why? Because if you get that glycol into the ground in your area, you are going to have a big cleanup for really big dollars.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • knobby44
    knobby44 Member Posts: 8

    Jamie, that is why I held off on that side until now, I had a leak in 1 of my 5 lines, I hit it with the backhoe early on and missed it. I found the leak with air from one side and water from the other to pinpoint the leak with a very sensitive ground probe microphone and fixed the leak.

    It has held 50psi for 2days and ready to fill.

    So, in this case, being a ground loop, if there was a leak for some reason in the future, then the Dowfrost (food grade) might be the better choice?

    Carson City, NV
    Mechanical Engineer
    Building ICF House
  • Jamie Hall
    Jamie Hall Member Posts: 27,376

    Yep

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England