Taco SR506 to Hydrostat 3250 Plus Constant Heat Call

Options
2»

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,159

    That configuration does not necessarily shut off the space heat circulators. so you could have all 6 zone circulators operating at the same time. If you want to have priority for the DHW then you need to wire the DHW circ to zone 6 and the water heater thermostat to zone 6

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?