Heat flow visualizer

Options
jesmed1
jesmed1 Member Posts: 1,472
edited 2:07PM in THE MAIN WALL

It seems that many of the problems homeowners come here with involve mismatches between boiler output, radiation, and/or building heat loss. This morning there's yet another post here from someone whose boiler is short cycling. Various pros here asked the usual questions and made the usual suggestions, all good.

That got me thinking about how to visualize heat flows from the boiler into the building, and the image of three buckets flowing into each other in series popped into my head. I'm sure I'm not the first person to draw this analogy, but since it helped me make sense of how heating systems work, I drew some sketches to illustrate various problems that people come here with.

The boiler is illustrated by the first "bucket," which is a BTU "reservoir" whose output rate R1 is represented by the diameter of the output pipe at the bottom of the bucket.

The thermal mass of the water and radiators is illustrated by the second bucket, and the radiation output rate R2 is represented by the diameter of its output pipe.

The building is represented by the third bucket, with its heat loss rate R3 represented by the diameter of its output pipe.

The water flowing between buckets represents the flow of heat (BTU's). If BTU's flow into a bucket faster than they flow out, the temperature (water level) in the bucket rises.

The size of the thermal mass bucket in the middle of the series matters, because a small thermal mass "bucket" will fill very quickly, with high water temps causing short cycling. Conversely, a large thermal mass bucket (like a gravity conversion system) will fill very slowly, keeping water temps low.

IMG_20260323_091111144.jpg

Common problems seen here at HH happen when R1> >R2, when an oversized boiler heats a small thermal mass too fast, resulting in short cycling, and when R3 > R2, meaning the building loses heat faster than insufficient radiation can emit.

IMG_20260323_091958930.jpg

In the case of gravity conversion systems, the thermal mass "bucket" is relatively large, meaning the "water" (temperature) level rises slowly. If the boiler is correctly sized to the building heat loss, R1 and R3 are roughly equal, and the large thermal mass and large EDR (R2) means the water temperature stays low.

IMG_20260323_093745192.jpg

But commonly we see gravity conversion systems with massively oversized boilers. This is the case in my 4-unit condo building. Here we have R1> >R3, where the boiler output rate is 2-3 times the building heat loss rate.

IMG_20260323_093753920.jpg

All analogies are imperfect, and I'm sure I'm not the first one to think of the bucket analogy, but it helped me make sense of the various flow rate imbalances that often show up as problems here at HH.

tcovert83GGross

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 27,346

    Anything that helps visualise or understand is wonderful! Thank you, @jesmed1 !

    Of course step 1 is to realise that the heating system is a system in the first place, and nut just a bunch of isolated components!

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    jesmed1GGross
  • hot_rod
    hot_rod Member Posts: 27,436

    Good graphic of the concept.

    The issue with typical CI boilers is even when properly sized, 80% or more of the heating season they are oversized. On mild days they are grossly over-sized.

    The heat load of a building is dynamic, the boiler output is static. So it is a mismatch not easily resolved.

    Multi, staged boilers can help, modulating boilers and modulating pumps are a better answer to dynamic load matching.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    jesmed1
  • ethicalpaul
    ethicalpaul Member Posts: 8,763
    edited 7:21PM

    Please forgive me.

    The issue with typical CI boilers is even when properly sized, 80% or more of the heating season they are oversized. On mild days they are grossly over-sized.

    How oversized are they on a 95 degree day when they are used to heat water 20 degrees in an indirect?

    Edit: I didn't want to make a new post for this:

    Please check my math, honestly I could be way off here:

    50 gallon tank * 20 degree increase in temp = 1000 BTU, is that right? I'm considering the typical case of an aquastat set to heat at 120F and shut off at 140F

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    jesmed1
  • jesmed1
    jesmed1 Member Posts: 1,472
    edited 4:04PM

    For those of us stuck with the fixed-firing-rate cast iron boilers we inherited, the graphic shows how important the size of the second "bucket" (thermal mass) is. Mismatches between an oversized CI boiler and small thermal mass can be helped by adding a buffer tank (making the second bucket bigger).

    My sister just bought a house with a (surprisingly) proper size CI gas boiler. But the house is ridiculously micro-zoned, with limited baseboard radiation. So the boiler runs 24/7, short cycling and bouncing off the high limit every few minutes. But her gas bills this winter weren't bad, which surprised me. The half of the unfinished basement that contains the boiler is the warmest room in the house.

    Still, her short cycling could be fixed with a buffer tank and fewer zones.

  • hot_rod
    hot_rod Member Posts: 27,436

    well if the indirect is piped and pumped to handle all the boilers output, it is not oversized for that load.

    Is it the most efficient way to heat dhw? Debatable

    Its the boilers with tankless coils that seem to be most inefficient

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • GGross
    GGross Member Posts: 1,879

    I'm a bit ambivalent to this specific subject, but wouldn't it stand to reason if the the single stage CI boiler were piped and pumped to deliver full load to the DHW at max demand that it would be oversized for the DHW when just maintaining temperature in the tank? Our "bucket" in the graphic would be different sizes depending on the DHW demand, from a solo cup size when just maintaining temp, to an appropriate sized bucket at steady DHW use, or max draw.

  • hot_rod
    hot_rod Member Posts: 27,436

    You size, mor should size, a boiler to the largest load. Sometimes that is the indirect, depending on it's expectations.

    Suppose you have a new energy efficient 1000 sq ft home, 12 btu/ft load. A family with two teenagers wants lots of dhw for tubs and showers from an 80 indirect.

    What size boiler? You will want more that a 12,000 btu/hr boiler if a basic DHW tank is 35K or more.

    I imagine most indirects are not piped to their maximum performance. It seems all, or most can handle at least 100,000 btu/hr. Often the recovery tables are based on 180- 200° SWT.

    Bob "hot rod" Rohr
    trainer for Caleffi NA