How do I hook it up?
Comments
-
you are sure the new motor is 240v not120?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
OK swapped both white wires to one side of the CAP and the brown is on the other. And it works and does seem slightly noisier which I think means spinning faster.
So assuming we didn't hurt anything with the mistakes looks like it's good to go.
Now, about that replacement sequencer…
0 -
It says 210-230v on the box. Picture on the last page. Aw heck here is the box picture.
0 -
The sequencer, I'll try to find some specifications, I suspect there is a delay for the second stage. How long have you run the furnace for ?
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Before I swapped maybe a couple of hours. It was on but didn't run that whole time. Before the swap it easily quickly raised the house temp 2 degrees and then another 2 degrees. It's now been on ever since the swap but again not a lot for it to do right now.
0 -
It looks like the 'sequencer' is just a time delay relay with with two sections (that are the same) and 2 switches per section. The second switch may close some random time after the first contact in each section closes. The switch pins 1 & 2 also power the blower in heat mode. Since both sections seem to have the same specifications. Looks like the unit you found is a reasonable replacement. Just make sure you really need it.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
I ordered the sequencer. Even though my in family expert blew the wiring I trust him that 2 of the heating elements aren't getting power from the sequencer. I watched him take those measurements. And even with this new part the total cost of parts including motor, mount bracket, capacitor and sequencer is less than just the hello we're here service charge from the company that didn't do anything.
Is it reasonable to infer the problem all along was the old motor failing? The virtually inaudible performance of the new motor versus the old plus the lack of end play in the shaft makes me think the old motor was definitely failing for a while. A long while…
0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements