Can someone explain to me why that reducer will cause the pipes to bang or if it shouldn't cause them to bang. The supply piping with the reducer just doesn't seem right to me. This is the only picture I have.

Comments

  • Captain Who
    Captain Who Member Posts: 883
    edited February 16

    Reducer Tee you mean? That equalizer should be at the end of the header, not a tee before the supplies to the mains. Also the Hartford Loop is way higher than the manufacturers recommendations. Actually, with the angle of the photo I can't really tell what the height of the Hartford Loop is. It might be OK if it is below the cyclegard probe.

    Basically he piped it in a way that encourages water entrainment up into the system, instead of dry steam.

  • pecmsg
    pecmsg Member Posts: 7,267

    because the installer didn’t read the manual concerning near boiler piping!

    GrallertIntplm.mattmia2
  • Grallert
    Grallert Member Posts: 1,146

    "The supply piping with the reducer just doesn't seem right to me"

    Yes. It's not right.

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

  • ethicalpaul
    ethicalpaul Member Posts: 8,927

    passed all inspections though, how could anything be wrong?

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    Intplm.4GenPlumber
  • ethicalpaul
    ethicalpaul Member Posts: 8,927
    edited February 16

    If the water is not oily and not carrying over it will be fine.

    See if the water level drops during steaming

    Where is the banging if you can tell?

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Intplm.
    Intplm. Member Posts: 3,079

    Look for low points in the system. Sagging pipes where condensate will build up and cause steam and condensate to collide. Any spot that is sagging and not pitching back to the boiler can cause banging.

    Check the owners manual for proper installation and correct any issues. Your near boiler piping needs some work.

  • neilc
    neilc Member Posts: 3,196
    edited February 16

    the Tee to the equalizer is reduced, the header has to flood to at least the tee level to "equalize" or drain, meanwhile you're pushing that flood water (tidal wave) up your main,

    and or you could be getting collapsing occurring at the rise reduction out of the boiler also,

    and it's not close to the correct order as mentioned above, (system main after the reduced equalizer tee on the header)

    do over,

    known to beat dead horses
  • mattmia2
    mattmia2 Member Posts: 17,409

    Was the steve that wrote their name in the mortar the person that installed this abomination?

    You have 2 reducers that are problems among several other things that are just as much if not more of your problem.

  • mattmia2
    mattmia2 Member Posts: 17,409

    Is that plug under the pressuretrol that looks unused the skim port?