Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!

What's the professional way to raise this vent?

Options

Want to raise this vent above the main into the ceiling. Easy peasy. Maybe one day I'll put a #2 up there. Aside from just putting a 3/4" nipple into the main, what's the way a future person wanting to replace the vent would be like "now this was done right"

1000044096.jpg

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,145

    I like the vents as high as possible, but that's just one of my quirks is to keep it up out of the water.

    You could use a close nipple and a union coming out of the tee to make a replacement easier.

    mattmia2ratherbfishing
  • Captain Who
    Captain Who Member Posts: 877

    If you want to cushion the blow of water hammer, you don't have to raise it, although that is preferred. You could tree it off to the side with a 45 and an Ell and a couple nipples and the extra volume in those will give the vent an air cushion. Ideally it should be located further away from the elbow to the return but try that.

    ratherbfishing
  • mattmia2
    mattmia2 Member Posts: 16,670

    like @EBEBRATT-Ed said, i'd put a union in there right off the main so you can pull the whole thing down by just breaking the union but other than that nipples and couplers are the way to go. I think there is even a male-female union that could thread directly in to the main and eliminate the nipple there.

    ratherbfishing
  • ratherbfishing
    ratherbfishing Member Posts: 45

    So like this

    Gorton #1

    |

    3/4" Coupling ← service joint

    |

    3/4" Riser Nipple (6")

    |

    3/4" Union ← removable assembly

    |

    3/4" Close Nipple (1–2")

    |

    Steam Main Tapping

    I'm guessing the close nipple will become permanent basically.

    Yes agree , the vent should be further from return but not gonna fix that

  • mattmia2
    mattmia2 Member Posts: 16,670

    you can remove the close nipple with an inside pipe wrench or sometimes you can grab it between the sets of threads with channelocks without damaging it. you certainly can remove it with a pipe wrench but that is likely to damage the threads.

  • ratherbfishing
    ratherbfishing Member Posts: 45

    Is it bad practice to use something like this instead of a close nipple? It was really really tough to get the old vent loose.

    1000044097.jpg
    Waher
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,587

    Just make sure that you don't have water hammer, and you'll be okay. If you have enough water hammer to damage that valve, then you have bigger issues than valve replacements.

  • AdmiralYoda
    AdmiralYoda Member Posts: 793
    edited February 12

    Well, the way to do this right is to build in a finished recessed box on the ceiling between the floor joists. Then you can use a union and a regular nipple to get the right height. This way the vent is always accessible.

    Instead of a recessed lighting cavity, its a "recessed venting" cavity.

  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    I know you all must get sick of me asking questions, but why would there be water hammer in the main?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    STEAM DOCTOR
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,145

    @ratherbfishing

    You can use any length nipples you want. I mentioned a close nipple because I don't know how much room you have. Use any length that works for you.

  • ratherbfishing
    ratherbfishing Member Posts: 45

    @ethicalpaul I enjoyed your previous post on comparing the #1 and #2. Enjoy seeing empirically derived data.

    @EBEBRATT-Ed thanks for comments.

  • mattmia2
    mattmia2 Member Posts: 16,670

    teflon tape and teflon dope will make things easier to get apart later.

    Larry Weingarten4GenPlumberratherbfishing
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,587

    Agreed. Deal with the underlying problem and not with the symptoms.

    ethicalpaul
  • ratherbfishing
    ratherbfishing Member Posts: 45

    Ya. The other, long main, (not topic of this discussion per se) has iron routed into copper mains that aren't insulated but put inside a closed decorative box running along the ceiling. This main hammers like crazy at the 90 degree turns. Sigh. This was installed probably 20 years before i purchased the house. At least I'm fixing what I can

  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    If it is doing it at the start of a call for heat, it could be as simple as needing to hoist up that part of the main due to a sag that is holding water.

    That's the only thing I can think of, in fact, that would cause water hammer in a main, and that was the reason for my question, which was not yet an argument (haha)—I was honestly curious if anyone had any other causes for water hammer in a main because I haven't experienced or seen it yet.

    Even crazy carryover in my old boiler never caused hammer—it just caused gallons of boiler water to flow through my main and to the wet return—that is something that could potentially foul a vent, but as @STEAM DOCTOR said, that's a problem that should be addressed regardless of how high your main vents are.

    My question was really about how I keep hearing about "water hammer hurting vents" but I don't know what that means. Do people have water hammer at the end of their mains?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 16,670

    i think a sag and steam from the boiler hitting a puddle could cause it, especially in an oversized boiler or poorly balances system.

    in large especially 1 pipe systems where the building is tall there are a few risers with a lot of load on them and if the condensate coming out of them isn't managed properly i think that can cause hammer in the mains.

    ethicalpaul
  • Captain Who
    Captain Who Member Posts: 877
    edited February 12

    It's a shock wave, due to the fact that there is approx. a 1,700x volume change in going from liquid water to steam and vice versa. If it is severe enough it is audible. If it is severe enough it can do damage to vents, especially the float.

    I heard it in this system 21 years ago when I first moved in. My varivalves weren't damaged by it afaik probably since they are only at the radiators, but it was quite disconcerting. My longest main had a large puddle at the last 6 ft or so of it, due to incorrect pitch. I also didn't have enough downward pitch in my dry returns. My main vents aren't at the 180 deg turns into my dry returns but are at the end of the dry returns by the boiler.

  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    Thanks @Captain Who I can see it if there is a pool of cool water due to sagging. I'm familiar with what causes steam/water hammer generally and have experienced it with a sag in a radiator runout, but lots and lots of people say "raise the main vent to avoid water hammer" but there is not water hammer in a properly pitched main that I can picture.

    If you have water hammer in your main, that is the problem… not the height of the main vent, and I, like you, would work hard to fix it. Thanks again.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Captain Who
    Captain Who Member Posts: 877

    People word things wrong sometimes. The reality is that raising the vent helps prevent damage to the vent in the case of water hammer.

    chrome_2026-02-12_11-46-44.jpg
  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    …Allegedly!

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • ratherbfishing
    ratherbfishing Member Posts: 45

    Thanks, everyone. Went from a gorton D installed on the main with a 90 elbow to a gorton #1 on a 10" riser with a serviceable union. Takes about 3:10 for me to feel heat at the end of the main. Just a dumb home owner over here but definitely improved what the installer did 30 years ago.

    1000044170.jpg
    STEAM DOCTORPC7060
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,145

    Your not a dumb homeowner. Most would have asked "what pipe dope do I use" Good job. Glad it sped up the heat.