old cast iron radiator fills w water tho vents new and tilt is good and rads on floor below r fine
on 2nd floor of 7 floor building, a radiator fills with water and spits alot (many cups)
vents are new, floor valve all the way open, tilt is good
the radiator off the same riser on floor below does no have this problem
a few minutes into cycle you hear gurgling as water builds up, and at end of cycle water drains out completely
no hammering and boiler pressure is not high
is it possible that some sediment in the fins makes this happen? ideas? thanks
Comments
-
It's not the vent's fault. It's not the tilt. It's nothing to do with pressure or vacuum in case that comes up. It's highly unlikely to be something in the fins (wait, fins? What kind of radiator is this? Is it a convector? Photos would help)
I would suspect that even though you think the valve is fully open, it has some kind of problem that is making it be partially closed (like the valve seat having rusted away from the stem and lying in the bottom of the valve.
The other possibility is ridiculous carryover driving water all the way up to that radiator. Even though you said no hammering, strange things can happen—check the gauge glass during boiler firing.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
I don't believe in such an event as a pocket of water in a runout, but my beliefs can change over time and strange stuff does happen.
But a radiator runout pipe is too large to hold water the way a straw does in that famous glass of water experiment.
Unless what you are saying is another way to say what I said: "The other possibility is ridiculous carryover driving water all the way up to that radiator."
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
i'm thinking it is a pitch problem.
0 -
although thinking more, if the runout is relatively small, too small for the combined edr of the radiators, the velocity of the steam could be pulling the condensate with it and collecting it in the first radiator.
0 -
One pipe radiator? The valve is effectively closed. It's a little disc which seats on the body. Disc has come off shaft. Steam can get in — lifiting the disc a little . Water can't get out. Replace or repair.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
The runout should only be small (and 1" at a minimum) only if the radiator is small. If the radiator is small, the amount of condensate is tiny. The amount of steam flowing into a single small radiator does not provide enough velocity to pull condensate anywhere.
Of course, that's provided it was designed correctly and not modified in some insane way.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
like someone added a second radiator to the runout that was sized for one…
0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 116 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements