Carrier draft inducer motor replacement

Options
dsiek
dsiek Member Posts: 1

I have a Carrier Weathermaker 8000TS that’s about 20 yrs old and the draft inducer motor and fan need replacing. I Hopi g just to get the rest of winter out of it before and upgrade.
I’ve searched for part# but have come across so many different numbers that I’m just uncertain which one applies. I deal with Johnstone and they were a little perplexed at finding the exact part# as well. I ended up using the part# off the motor, FB-RFB212, and using that they found a motor & fan assembly, which is great. They did find an exact motor replacement on its own but I need to replace the assembly also. So cost wise the complete unit was more cost affective.

The issue is the horsepower on the new complete assembly’s motor is 1/26hp whereas the existing motor is listed as 1/30hp. Other than that everything is identical on both motors.
my question is can I use this replacement?The staff at Johnstone thought I might but were uncertain if the pressure switch might need adjustment. I also wonder if there may be any other adjustments needed or issues

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 27,237

    Unless it's some really weird kind of motor, they will both try to spin at the same speed, so you shouldn't need any adjustments on it. The new one has slightly more rated power, but that shouldn't make any difference. If it had less, there ight be a problem, but not more.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    dsiek
  • pecmsg
    pecmsg Member Posts: 7,024

    You cannot adjust that pressure switch. Its designed to open / close at the minimum static pressure.

    Down load the manual and get the right motor.

    HVACNUT
  • mattmia2
    mattmia2 Member Posts: 16,460

    1/26 and 1/30 are essentially the same number, they are likely just the result of them buying the motor from different manufacturers.

  • Big Ed_4
    Big Ed_4 Member Posts: 3,515

    Take the model and serial number down to Johnstone , you need the complete fan assemble ..I am sure it is on the shelf .

    Stay Warm

    There was an error rendering this rich post.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,084

    He bought the complete fan assembly. The horsepower is slightly larger but the change is insignificant. Install it and it should be fine.

    mattmia2
  • Big Ed_4
    Big Ed_4 Member Posts: 3,515

    Easier too , five screws …

    There was an error rendering this rich post.

  • HVACNUT
    HVACNUT Member Posts: 7,410

    Always the whole assembly. Its a no brainer. Johnstone should be able to cross reference it.

    Have you tried to contact Carrier?