House not getting heated
I have boiler running. Thermostat is set at 74 F. However, th ehouse is ot getting heated and inside temprature remains 59 F. I couln't find the reaon. The steam radiators get heated sometimes - but normally are cold. This issue has started just last week since temprature dropped considerably.
Comments
-
I hate to ask this — but let's be sure this is really steam and not hot water? The radiators can look similar.
Assuming that it really is steam, next question is also kind of embarassing: the boiler is really running? It's not just a fan on the boiler burner that you are hearing?
There will be an inspection port where you can look in and see — if it's oil, is there a good bright fire in most of the firebox? If it's gas, is there a good bright blue flame on the burners or a good flame in the firebox?
I apologixe in advance if those questions seem obvious, but… it helps to be sure.
Now. If the boiler is really running, how much water is in it (where is the water level on the sight gauge) and what pressure, if any, is showing on the pressure gauge? when you go outside, do you see any steam — billows of white "smoke" coming out of the chimney?
Honestly, there isn't much that can go wrong with a steam system — if the boiler is producing steam, it has to go somewhere. You can feel along the pipes leading away from the boiler (careful — they may be very hot) to see how far the steam is getting.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Some pictures would help us to help you: of the boiler and the piping around it, from floor to ceiling and from the sides.
—
Bburd0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 116 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements