Radiator vent issue

Options
alanm
alanm Member Posts: 149

Looking for potential remedies for "sounds" from some of my radiator vents. I have a one pipe steam system…when i turn the heat up, especially in the morning…some radiators sound like an airplane taking off…hissing noises..Not all the radiators…just a few. side note..it seems to be from the radiators that look like "hot water radiators" and not the steam radiators…house over 100 years old. suggestions? different type of vents (sizes?). Thanks Alan

«1

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    are all the noisy ones the same model of vent? Post a pic?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • alanm
    alanm Member Posts: 149

    no…i will send pictures

  • alanm
    alanm Member Posts: 149

    here is the one radiator….a bathroom ….i have a cover over it….so you can see the vent and the tough spot it is in…any suggestions

    thanks

  • geemalar
    geemalar Member Posts: 98

    I believe the experts here might bring up 2 points for starters, I'll let them verify that first………

    1. The vent should not be at the top of the radiator, should be mid position of the radiator
    2. The vent is not vertical, it's turned to a certain degree
  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    The location on the radiator isn't optimal, but is not affecting the sound.

    But the rotation of them could be causing them to make noise. Rotate them to vertical like @geemalar said

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • alanm
    alanm Member Posts: 149

    with that "bolt" there, i cannot screw in the vent to get it vertical……do i have to drill a hole lower and then plug that top hole?

  • alanm
    alanm Member Posts: 149

    i am not an expert in Radiators…but the two that are doing that "noise" have a different design than the others in my house….are they hot water radiators? are they ok to use with one pipe steam system?

    thanks

  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    Please show us a picture of the vent side of one of those radiators

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    If it's the pictured radiators you are talking about, they are fine for steam.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    If your upcoming photo of the vent side of one of those radiators shows no other port, then you can put a short 1/8" nipple with a 1/8" coupler and extend the vent away from the radiator a bit.

    But why can't you rotate them clockwise away from the bolt to get them vertical? I'm not understanding

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • dabrakeman
    dabrakeman Member Posts: 1,001

    Vent should be below the halfway point on the radiator but to sort out whether the orientation is an issue with the vent you could for a few bucks get a 1/8" npt nipple and coupling to extend the vent away from the radiator a bit.

  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    Also if it's just hissing (I confused your post with the "air horn noise" thread), then perhaps your main venting isn't working or is insufficient. You can try a different model of vent. If your boiler is oversized, some hissing may be unavoidable. Is this a single family home, or an apartment building?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • alanm
    alanm Member Posts: 149

    thanks…so a few follow up to questions:

    1. so take a look at photo 2…that "nut" pertrudes out so i cannot turn the vent anymore
    2. i have a cover over that radiator so if i put on an extension then a vent,the cover will not fit …the cover is already pretty close to the side
      1. i didnt think it would be the main…since i really dont have that issue in any of the other ones except really two.
        1. but if the main vent…how do i know if it is bad…or do just replace…i think i have a Hoffman 75 on it now
        2. this is a 3 story single home
  • ethicalpaul
    ethicalpaul Member Posts: 8,741
    edited January 27
    1. Rotate it clockwise to vertical (or are my eyes deceiving me in some way??)
    2. You can try other models of vents. Try a Maid O' Mist, they are pretty good and not pricey
      a. Well that doesn't really prove the main is working—the air has to escape somewhere
      i. watch it when the boiler starts boiling. You should be able to feel or hear it letting air escape.
      ii. thank you
    image.png

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • alanm
    alanm Member Posts: 149

    also…what is better….

    1. Try the extension first ….cover will not fit…..but if it stops the hissing…drill down lower and put vent in?
    2. do these work…Varivalve 925005-00 Adjustable Angle Vent Valve
      1. these look smaller and may be able to turn with that "nut" there
    3. also…if it is hissing….like i have in another…do i need to slow down or increase the size of the vent?…

    thanks!

  • alanm
    alanm Member Posts: 149

    thanks….sorry…it is not turned all the way vetical because i have a cover that it is just over the top of the radiator…so if i turn the vent…it would hit the radiator….i think these wood covers were done way before my time!

  • ethicalpaul
    ethicalpaul Member Posts: 8,741
    1. I'm still waiting on that photo of the vent side of one of these radiators
    2. They probably work but I don't use them
    3. I wouldn't change the vent size to try to eliminate hissing. Hissing is one or more of the following:
      1. Your boiler is oversized
      2. your main venting is not functioning or is not sufficient or both
      3. your pressure control isn't functioning and is allowing too much pressure in your system

    The air must escape your system every time there's a call for heat. You want the air from the main to exit via the main vent in the basement, then after that you want the radiators to slowly vent the remaining air.

    Does this happen all heating season, or is it exacerbated during cold snaps?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Captain Who
    Captain Who Member Posts: 877
    edited January 27

    When you hear the vent noise where are you in the cycle? Also, do you have a low pressure gauge on your boiler?

    By where are you in the cycle I mean, for example, is it near the end of the burner on/steam generation cycle or is it after the burners have shut off………etc.?

    Are your vents ever closing, ie. they go silent during the burner on/steam generation cycle?

    Maybe babysit one of those vents during entire cycle and let us know what happens. If you have a helper to correlate with boiler pressure (if you have a gauge) that would be helpful.

    Heat Timer Varivalves are also available in the straight (as opposed to angled) configuration and would clear your covers until you can relocate them down lower.

    Edit to add - If you don't have a bush in the casting down lower below the midpoint, which is where you would drill and tap 1/8 NPT for a vent, then I would say that these radiators were not manufactured for steam.

  • ethicalpaul
    ethicalpaul Member Posts: 8,741
    edited January 27

    OK but you can at least rotate one of them vertically with the cover off to see if it affects the sound. If not, we can drop that item from our list of things to do

    There is a lot of negative opinion about these Varivalve vents, but they are very small and might suit your situation. A lot of people I visit have them on their radiators that are under covers:

    https://www.supplyhouse.com/Varivalve-VAAV-Varivalve-Adjustable-Angle-Air-Valve-3840000-p

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • alanm
    alanm Member Posts: 149

    here are some other photos

    so i was going to try the following:

    1. Take off cover, and put in anotehr vent…
    2. if that works…and i need to keep cover, try that varivalve vent; or
    3. looks like there is a spot midway…..can i block the top and put a regular vent in the middle?
  • alanm
    alanm Member Posts: 149
  • Captain Who
    Captain Who Member Posts: 877

    Good for you. Photo 8 clearly shows the plug you need to remove to relocate the vent, which you probably know. I'd move the plug to the upper location, assuming it is same thread size as that Ventrite? vent.

  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    This is where the vent is supposed to go. But remember, this is unrelated to the hissing you are hearing. It will just make your radiator fill with steam better to have the vent down here

    image.png

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • alanm
    alanm Member Posts: 149

    how do you take the plug out…anything special? if this will not reduce the hissing/noise….what will this do ?

  • ethicalpaul
    ethicalpaul Member Posts: 8,741
    edited January 27

    It might make it easier for you to correctly orient the vent with the cover installed.

    As I said, it will make your radiators behave more as they are supposed to in terms of filling with steam.

    Otherwise, it won't affect your hissing issue. The guys just mentioned the vent was in the wrong place because it's in all of our nature to point out problems when we see them in photos.

    You unscrew that plug with a flat head screwdriver, looks like from here. But it might prove difficult. Be prepared to drill it out and clean the threads if you go down this road.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • alanm
    alanm Member Posts: 149

    thanks….will try….i was going to put in a gorton #4…since in a bathroom…does that make sense?

  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    it’s hard to tell until it’s in there, since it’s such a small rad and since people like warm bathrooms you might start with a 5 or 6

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Grallert
    Grallert Member Posts: 1,111

    I'd be very surprised if that plug comes of with out a battle. Sorry to say. It might but be prepared. That's why folks are suggesting simple turning the vent counter clockwise to vertical. The cover will have to wait until the plug comes out. It is the same threading as above though.

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

  • alanm
    alanm Member Posts: 149

    thanks

  • dabrakeman
    dabrakeman Member Posts: 1,001

    Generally the smaller the vent the less hissing you will get but it could get louder at other locations that have bigger vents. More important to have the right amount of heat that you want in the bathroom. If too warm then go with smaller vent.

  • alanm
    alanm Member Posts: 149

    here is the other radiator…it is in the kitchen….probably one of the further radiator from boiler on the first floor…..other radiators are the "other types" and really no hissing from them…see photo……..any suggestions what i need for this radiator?

  • dabrakeman
    dabrakeman Member Posts: 1,001

    I think @ethicalpaul and I have repeatedly asked you about your main venting. What do you have and how long and what pipe size are your mains? The single Hoffman 75 may be insufficient if it is working at all. Balancing as well as minimizing early cycle hissing starts there. You ahve also not clarified when in the cycle your hissing issue exists (i.e. from the point the boiler starts making steam onward, or only after the main vent closes, or only just before the radiator fills and the radiator vent closes, or after steam has reached the vent and it is not closing, or after the boiler shuts off… You also do not apparently have a handle on your overall balancing so I and others have suggested using economical but as reliable as any MoM vents for which you can easily adjust the venting rate with different orifice caps.

    ethicalpaul
  • alanm
    alanm Member Posts: 149

    thanks….here is photo of the boiler…some info

    there are 2 mains off the boiler….one (going to the "right" in the photo feeds a radiator on the 2nd and 3rd floor

    One little run feeds a radiator on the first floor

    the big main, going to the left in the photo takes care of all other radiators in the house (about 12). House heats up well and all radiators working….no hissing..When the few do hiss…seems to be when at night i turn down to about 69 degrees…and then in the morning…move to 71 and more if still cold.

    the "big" main runs probably about 100'…kind of like a sqaure in my unfinished basement (house is 30 x 40 — 3 stories).

    that Hoffman 75 main vent probably there about 10 years……

    There was an error displaying this embed.
  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    thanks, but picture didn't seem to make it

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • alanm
    alanm Member Posts: 149
  • ethicalpaul
    ethicalpaul Member Posts: 8,741

    your mains are long, even I would recommend starting with a Gorton #2 instead of that Hoffman

    The near boiler piping will work. Obviously the smaller copper pipe isn’t ideal but it probably isn’t hurting you

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Captain Who
    Captain Who Member Posts: 877
    edited January 30

    What boiler mfg. and model and size? Need more pictures and angles. That equalizer looks undersized. I think those 1-1/2 in. supplies should be 2 in. Top of Hartford Loop close nipple needs to be min. 2 in. below the normal water level.

  • alanm
    alanm Member Posts: 149

    ok….i am a novice…so what could changing the Hoffman main to Gorton 2 do?

    thanks for your help!

  • alanm
    alanm Member Posts: 149

    crown….model Ksz 200BOP

  • ethicalpaul
    ethicalpaul Member Posts: 8,741
    edited January 30

    It would increase the rate at which air was purged from your main piping as the steam pushes in from the boiler. This would let your radiators start to get steam at closer to the same time and let heat get to your living space faster on a call for heat. It would also reduce the amount of air that had to be pushed through each of your radiators' vents, reducing "hissing" sounds.

    This removal of air from your main pipes and your radiators has to occur each time the thermostat calls for heat so it's good if the time that takes can be minimized (within reason)

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    dabrakeman