I have an old Pennsylvania Furnace Company boiler from the early 1960's still running fine. But due to age and condition, I know at some point I have to get something new. It is a millivolt system. I want to replace it with another millivolt system so I will still have heat in a blackout. Do they make modern millivolt system steam boilers today that dont have a need for any transformers?

IMG_0188.jpeg IMG_0186.jpeg IMG_0185.jpeg

Comments

  • Steamhead
    Steamhead Posts: 19,007

    No. Millivolt systems no longer meet energy-efficiency requirements.

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,948

    Agree

    But that does not mean that you can't get those old style parts brand new in the box and put them on the boiler after the job has been inspected.  A steam boiler is the easiest piece of equipment to do that to.  There are no circulators or zone valves involved.  Just a high limit pressure control and a mechanical LWCO will make the minimum safety requirements  You wont have the auto vent damper and electronic ignition but you will also not have frozen pipes during a power failure.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    109A_5Long Beach Ed
  • ratio
    ratio Posts: 4,344

    There are 24 VAC inverters available that will keep a gas valve open for a goodly while now too. More complicated, and there's the whole battery maintenance thing too, but it'll definitely keep the heat on until you can get the generator started and plugged in.

    Captain Who
  • hot_rod
    hot_rod Posts: 28,705

    These power stations come in many sized. You could run a 24V system for days, maybe weeks with a large enough pack. Very handy for camping, tailgating and other remote uses.

    I power lights and chargers and a small fridge in my camper for 4 days with a mid sized unit.

    Screenshot 2026-01-26 at 8.56.09 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    ethicalpaul
  • mattmia2
    mattmia2 Posts: 18,399

    What are the idle losses of that inverter, if the inverter is on but has no load? When I have run salvaged ~1kw UPSs to power something like a cable modem with a pots bridge it seemed like the power to the load was negligible compared to the quiescent current of the inverter. Is that still a problem with these, if you want to power a small load for a long period of time you have to frankenstein a big battery in to a tiny ups.

    bjohnhy
  • hot_rod
    hot_rod Posts: 28,705

    Idle consumption varies based on the model ad size of the inverter. A few online sites test and publish that data for various brands and models.

    Screenshot 2026-01-26 at 11.02.08 AM.png

    I keep mine plugged into a 200W PV array on my camper, or at home into a wall charger. So it is always up to speed for power needs.

    Or convert you boiler to DC volt, and switch off the inverter

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    wouldn't converting it to dc be the same effort as converting it to millivolt?:)

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I think a power station as @hot_rod mentioned is the best bet to keep a boiler on. No sense hacking in some millivolt controls.

    The pressure control, LWCO and thermostat would have to be millivolt rated

    ethicalpaul
  • kcopp
    kcopp Posts: 4,735

    This is what I have my System hooked into if I lose power.

    I just have a pigtail that I can plug into this.

    M18 CARRY-ON 3600W/1800W Power Supply | Milwaukee Tool

  • hot_rod
    hot_rod Posts: 28,705

    I guess it comes down to how often the OP has blackouts, how long they last, how much power the boiler needs, and how much $$ they want to spend on a back up system.

    I imagine hacking a new boiler, converting the control would void warranty and put any failure liability on the hacker

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    EBEBRATT-Ed
  • Long Beach Ed
    Long Beach Ed Posts: 1,851
    edited January 29

    In the buildings we own, we've wired backup jacks and isolation switches to the boilers, so we can plug in small battery inverters during the many regular power disruptions.

    The atmospheric gas/steam systems run for seven hours continuous (14 hours of heat on a 30 degree day) using a $200 inverter/battery. Hot water with a pump gets about four hours (eight hours heat at 30 degrees). Really just concerned with freeze-ups.

    We have millivolt controls and gas valves packed away if New York ever degrades so badly that we need them and we still install new float low water cutoffs.

    hot_rod