I have a single pipe steam boiler that has two new pressuretrols . They have their own pigtails connected by a T into the boiler. Both are set at 0.5 cut in w/ a 1 differential . The burner cuts off at a gauge read pressure just shy of 2 lbs. I believe they should be wired in series , but should the cut in &/or cut out settings be different ? Thanks for setting me straight !

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    Pictures would help:

    Why two controls? Is one manual reset (with a push button) and the other auto reset?

    Does 1 control for lo-high fire control

    If they are both High limit controls it would be better to have the controls piped to the boiler in individual tapping's if possible. my not be a code requirement, however.

    Need more info to help.

    Your pressure settings are about right. The pressure setting scale on the controls is usually a little bit off from the actual pressure.

  • Jamie Hall
    Jamie Hall Posts: 27,975

    They must be wired in series, not in parallel. And if both are automatic reset then I would set one as you have it and the other at 1 psig cutout.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Big Ed_4
  • Chris_L
    Chris_L Posts: 354

    If you have a millivolt gas valve (with 100% shutoff), they should not be wired in series, and they should not be set the same.

    If it is such a millivolt system, one pressuretrol will be set as yours are to cycle the boiler on pressure. The other is set a pound or more higher to turn the gas and pilot off completely in case the other pressuretrol fails and pressure starts to build. (You'll then need to relight the pilot to operate the boiler.)

  • Jamie Hall
    Jamie Hall Posts: 27,975

    True, if sslightly misleading. They still shouldn't be wired in parallel. Rather they need to be, as iss implied, on completely different circuits. One for the millivolt gas valve. The other (it can be on the 120 volt side, perhaps) to shut the boiler down completely — all gas off, all fans, whatever — in the event of an overpressure. AND that one should be a manual reset.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Chris_L
    Chris_L Posts: 354
    edited December 2025

    I didn't mean to imply they should be wired in parallel. (And never heard of a 120 volt side to a millivolt gas valve on a residential boiler.)

    The ones I am familiar with are all millivolt. And there is no need for a manual reset on the pressuretrol that shuts down the boiler and pilot since the boiler can't be restarted without lighting the pilot.

  • mattmia2
    mattmia2 Posts: 18,399

    and no one will ever figure out that is why the pilot keeps going out. maybe about 10% will figure it out if it happens in front of them.

  • Big Ed_4
    Big Ed_4 Posts: 3,585

    I don't think you find a millivolt system with dual pressuretrols , Resistance issues ..

    There was an error rendering this rich post.

  • mattmia2
    mattmia2 Posts: 18,399

    usually don't find boilers large enough to require a redundant pressuretrol with millivolt controls either.

    Big Ed_4
  • Chris_L
    Chris_L Posts: 354

    Two pressuretrols are code in MA for residential millivolt systems, not that many people have millivolt systems anymore since you can't buy them new.

    Here is a picture of one of my 40+ year old Burnham boilers (taken some years ago) with the two pressuretrols in their original configuration. The upper one is for the total shutdown.

    image.png
  • ArtM1
    ArtM1 Posts: 14

    Both pressuretrols are automatic reset and no low-high fire regulation . They are wired in series and cannot be adjusted to a 1 psi cut-out pressure. I have read that it's possible to lower the cut-off pressure by turning the 0.05 " hex screw under the pivot arm CW ,which I have yet to attempt. Both are covered by a tamper proofing blue glue. It is a fuel oil burner ( so no millivolt gas valve ).

  • Jamie Hall
    Jamie Hall Posts: 27,975

    Don't attempt to lower the cutout. There's no point to that. 1.6 or 1.7 psig is low enough for any conventional system, and if you have a vapour system requiring lower pressure, you need a vapourstat.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I don't understand the "millivolt shut down comments" at all.

    There is normally no 120-volt power to a millivolt system. The one time I did this I had a MM #67 LWCO and added a feeder to it. The top two terminals broke the millivolt system to shut down the burner.

    The bottom two terminals ran the feeder on 120 volt.

    If you have a straight millivolt system all the power is generated by the powerpile. There is no other circuit to break to shut the boiler down. Power pile current runs up through the pressure control on off switch (if you have one), low water cutoff and thermostat.

  • Chris_L
    Chris_L Posts: 354

    @EBEBRATT-Ed , if this diagram (or the attached pdf) is legible, you'll see the second pressuretrol ("auxiliary limit") wired between the powerpile and gas valve. If that trips, it shuts off both the gas flow to the burners and the pilot. That shuts down the boiler, and it won't run again until the pilot is relit even if the pressure returns to atmospheric.

    image.png
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    @Chris_L

    Thanks never seen that done.

  • ArtM1
    ArtM1 Posts: 14
    1000001449.jpg

    This is my V35 Burnham boiler with the two pressuretrols highlighted. Because the controls are set at the same cut in and cut out pressures, I won't be able to determine if one of the controls fails. The burner was coming on at 0.5 psi and cutting out at just before 2 psi. The differential for both is set at 1. If one of the two controls is a safety shouldn't it have a different cut out pressure ?

  • Jamie Hall
    Jamie Hall Posts: 27,975

    yeah…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ArtM1
    ArtM1 Posts: 14
    edited December 2025

    So would I set up my control pressuretrol cut in @ 0.5 and cut out @ 1.5 psi (using 1 as differential even though my gauge is reading close to 2 psi in operation) ? And my safety pressuretrol cut in @ 2 psi and cut out @ 3 psi (using 1 as the differential ) ?

  • ratio
    ratio Posts: 4,344

    The safety pressuretrol needs to be a manual-reset type. It will only trip when something is wrong, like the operating control has failed closed. If it's automatic reset, you'll just switch over to using it as an operating control.