Hi everyone-
Newbie to the forum.
I have a GSA 125 steam boiler with single pipe radiators and have owned my house for ~13 years. The system is heating appropriately, but is making a churning noise at the boiler when firing. I'm not sure if this is a new issue or a newly noticed issue.
Any ideas?
Comments
-
on oil burner, it stops soon after, right?
if so, it s the igniter sending high current to start the flame. after a short moment it stops because ignited fuel starts more combistion of the incoming oil.
0 -
It’s a natural gas boiler. Doesn’t start right away after it ignites and sounds like it’s coming from the pipes above the boiler itself.
0 -
What does the level in the sight glass look like, does it bounce around or drop significantly?
0 -
Is the sight glass surging? The water may have oil in it or have gotten dirty enough with rust over time that the boiling action is puking water into the main.
0 -
Yes, sight glass is bouncing around a bit. It was overfilled as well. I drained some water out so the water line was at a normal level but the sight glass is still bouncing around.
0 -
show the boiler, from a couple angles, floor to ceiling, and we'll tell you how to clean it
known to beat dead horses0 -
Might need to skim it, flooding it might have released some oils that normally didn't get water or steam contact
0 -
Here’s the full look at the boiler
0 -
Is there even a skim port installed on the boiler?
0 -
It goes here I think:
It's surging/carrying over is my guess. You can really hear it on those copper headers. You can try draining out that nasty green boiler treatment (there are a couple that are that color and I don't like them) and refilling with fresh water (not something you want to make a habit of due to increased corrosion from the fresh water).
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
anyone notice the gage at 25 psi?
has the pigtail been serviced? it needs to be free breathing back into the boiler so that the Ptrol sees what the boiler is doing,
Dial (gently, stop as the indicator hits the bottom of the scale, and you realize some slight resistance, ) the Ptrol down as low as it will go without not refiring, if it won't light up again then add a turn back in, inside there's a wheel, it should be set to 1,
yeah, spill the chem water and go with fresh clear water,
you need a skim nipple where that insulation is showing on the jacket,
known to beat dead horses0 -
-
that cut in is showing above 2, that's fine?
dial it down,
known to beat dead horses0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 75 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements