I have a GSA 125 steam boiler with single pipe radiators and have owned my house for ~13 years. The system is heating appropriately, but is making a churning noise at the boiler when firing. I'm not sure if this is a new issue or a newly noticed issue.

Any ideas?

Comments

  • patrykrebisz
    patrykrebisz Member Posts: 142

    on oil burner, it stops soon after, right?

    if so, it s the igniter sending high current to start the flame. after a short moment it stops because ignited fuel starts more combistion of the incoming oil.

    »»» See my steam heat YouTube videos:
    https://www.youtube.com/@HeatingBlog

  • toccmatt
    toccmatt Member Posts: 5

    It’s a natural gas boiler. Doesn’t start right away after it ignites and sounds like it’s coming from the pipes above the boiler itself.

  • mattmia2
    mattmia2 Member Posts: 17,905

    What does the level in the sight glass look like, does it bounce around or drop significantly?

  • Waher
    Waher Member Posts: 373

    Is the sight glass surging? The water may have oil in it or have gotten dirty enough with rust over time that the boiling action is puking water into the main.

  • toccmatt
    toccmatt Member Posts: 5

    Yes, sight glass is bouncing around a bit. It was overfilled as well. I drained some water out so the water line was at a normal level but the sight glass is still bouncing around.

  • neilc
    neilc Member Posts: 3,201

    show the boiler, from a couple angles, floor to ceiling, and we'll tell you how to clean it

    known to beat dead horses
  • mattmia2
    mattmia2 Member Posts: 17,905

    Might need to skim it, flooding it might have released some oils that normally didn't get water or steam contact

  • toccmatt
    toccmatt Member Posts: 5

    Here’s the full look at the boiler

    IMG_4303.jpeg IMG_4302.jpeg IMG_4304.jpeg
  • mattmia2
    mattmia2 Member Posts: 17,905

    Is there even a skim port installed on the boiler?

  • ethicalpaul
    ethicalpaul Member Posts: 8,978

    It goes here I think:

    image.png

    It's surging/carrying over is my guess. You can really hear it on those copper headers. You can try draining out that nasty green boiler treatment (there are a couple that are that color and I don't like them) and refilling with fresh water (not something you want to make a habit of due to increased corrosion from the fresh water).

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • neilc
    neilc Member Posts: 3,201

    anyone notice the gage at 25 psi?

    has the pigtail been serviced? it needs to be free breathing back into the boiler so that the Ptrol sees what the boiler is doing,

    Dial (gently, stop as the indicator hits the bottom of the scale, and you realize some slight resistance, ) the Ptrol down as low as it will go without not refiring, if it won't light up again then add a turn back in, inside there's a wheel, it should be set to 1,

    yeah, spill the chem water and go with fresh clear water,

    you need a skim nipple where that insulation is showing on the jacket,

    known to beat dead horses
  • pecmsg
    pecmsg Member Posts: 7,442

    that control looks fine. Could be a bad gauge

    mattmia2ethicalpaul
  • neilc
    neilc Member Posts: 3,201

    that cut in is showing above 2, that's fine?

    dial it down,

    known to beat dead horses
  • toccmatt
    toccmatt Member Posts: 5

    The pigtail was serviced about a year ago, but guessing whatever happened to get this thing overfilled probably clogged it back up.

    Here's what I'm gathering I should do from this thread, let me know if I'm missing something:

    1. Adjust the pressuretrol way down.
    2. Drain boiler. Fwiw, the water is more brown than green, I don't think there has been any boiler cleaner added to it, that I know of.
    3. Remove pigtail/pressuretrol, clean pigtail.
    4. Refill
    5. Install a skim port

    Does that make sense? Anything I'm missing?

  • mattmia2
    mattmia2 Member Posts: 17,905

    i'd put a low pressure gauge on the pigtail with the pressuretrol, that gauge likely got tweaked and is wildly inaccurate. does it go to 0 when the boiler is off?

    might as well skim it before you flush the boiler.

    ethicalpaul
  • clammy
    clammy Member Posts: 3,259

    Look like a genus installed ,piped wrong and god forbid you have to remove any burners .Who installed the boiler w the front facing a wall ? It looks as though the hartford loop is remotely installed instead of off the equalizer drop again a public school grad not reading instructions but the copper pipe gives it right away . Typical a good install in reality you need some one to re install that boiler correctly the performance and your fuel consumptions will tell the tale . Most likely its has a good deal of mud and rust in the boiler hence the churning noise but some will stay unnecessary but usually a good wanding and flushing of the bottom of the boiler and flushing of the return piping will help . Your performance will only as good as the near boiler piping but as most know steam is quite forgiving and will usually work even if installed improperly unless by some one who has a clue then there issues but when a hack installs it works perfect 'one of god miracles for sure and in complete opposite of murphy's law .

    peace and good luck clammy

    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating

    Dave in QCApecmsg
  • gfrbrookline
    gfrbrookline Member Posts: 788

    what @clammy said. No copper pipes on steam heating systems.