Hi guys, we are in our new house. 2400 sqft two story with 4 bedrooms upstairs and one in the basement. 3.5 bath. We have a Lochinvar Epic Fire Tube Boiler – 80,000 BTU model. It supplies a 40 gallon tiger tank for dhw. And also heats infloor in the basement. About 867sqft in the basement is being heated. Our problem is that sometimes when we have showers if we have more than one shower running or my wife has a bath and a shower is running, the boiler doesn’t seem to keep up. The tiger tank drops to 40 Celsius when the set point is 60 Celsius. It then sits at that point until the hot water has been shut off and the boiler then heats up the tank to 60 Celsius. It seems like the boiler can keep up if it starts heating to 100% right away. But it almost seems like it if there is a call for space heat, that the boiler doesn’t cancel it when it calls for dhw. I’ve went through the settings as well as my plumber did and we can not find a setting for prioritizing dhw even if there is a call for space heat. All I could find was the switching times. Which were set at 30 mins from dhw>sh and 30 mins from sh>dhw. I since switched them to 4 mins for dhw>sh and 2 mins for sh>dhw. Do I need to drop the time for sh>dhw or do I need to change another setting that we can’t find.

Comments

  • mattmia2
    mattmia2 Posts: 18,399

    your indirect tank is too small for your dhw load. you could get somewhat more capacity buy keeping the tank at a higher temp and using a thermostatic mixing valve but to make for example 2.5 gpm of hot water with a 65 f rise you need 81,000 btu/hr. (i used about 35 f incoming water temp and 100 f final water temp). once you have mixed enough cold water in that indirect tank to male the water noticeably colder, you aren't replacing as fast as you are using it. your boiler is 80,000 btu/hr in and around 70,000 btu/hr out. there uis also some lag between when you start using water and the aquastat in the tank sees the tank is cooling, then some more lag for the boiler to pre-purge, light, and get hotter than the tank and start adding heat to the tank.

    the tables in the manual for the indirect are for conditions of incoming cold water that is much warmer and a boiler that is much bigger than in typical northern climate installations.

    Ironmanrick in Alaska
  • Jamie Hall
    Jamie Hall Posts: 27,975

    You're asking an awful lot of that system. 80,000 BTUh for domestic hot water works out to about 2.5 to 3.gpm recovery rate — call it 3 litres — per minute. That's one shower — and pushing it for just one shower.

    What's happening is that that one shower (or bath) takes all of that 40 gallon tank, or nearly so, and the water heater simply can't heat the water flowing through hot enough. So you need to wait for the boiler to catch up — which it will, but not that fast.

    Solution? Bigger tank. That won't solve the problem completely, but with an 80 gallon tank — which is the largest you can get for a residence but is the smallest I'd recommend — you'll have a better chance.

    Also set it to hold the water at 60 Celsius or so and use a thermostatic mixing valve to bring it down at the outlet to a save temperature.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2Ironman
  • GroundUp
    GroundUp Posts: 2,573

    DHW will always take priority over space heating if it's properly connected and piped. Are you using a sensor or aquastat in the tank? What is the tank setpoint? What is the boiler setpoint for DHW? Turn that time back to 30 minutes and raise the tank temp along with possibly the boiler temp as well so it'll store more hot water, then you shouldn't need a bigger tank or boiler.

    bjohnhy
  • Jamie Hall
    Jamie Hall Posts: 27,975

    a 40 gallon tank? with a 2 gpm recovery? for 3 and a half baths? nope.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2
  • hot_rod
    hot_rod Posts: 28,706

    if the input is 80,000, you have more like 69,000 btu/ hr to cover the dhw, so once the dump from the tank is gone filling the tub your recovery will be with 69,000, more like a 2 gpm rate depending on incoming water, possibly keeping up with a shower.

    The tub dump load may not be a good match for a 40 gallon indirect, if you want a shower at the same time or after a tub fill

    what size tub?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    i'd probably keep the 40 and add the 80, that is more the type of load they are looking at.

  • Kaos
    Kaos Posts: 1,003
    edited December 2025

    Something feels off. Triplex with a 50gal power vented tank with a 40k burner and keeps up. How many GPM is your shower and tub filler (quick test, time how long it takes to fill a 5 gallon bucket).

    Pictures of the setup first, I have feeling something is either not plumbed properly or the controls are incorrect.

    If you do need more volume, you don't need a bigger indirect. You can add a regular electric tank downstream of the indirect. If the electric tank thermostat is set bellow the indirect output, the elements will only run to make up for standby losses or after larger draws that empty out both tanks. If you have hot water recirc you don't even need to plug in the tank as the recirc can be set to re-fill it off the indirect.

    bjohnhy
  • hot_rod
    hot_rod Posts: 28,706

    The boiler needs to be sized to the biggest load. In todays energy efficient homes, the DHW ends up being the biggest load often

    So knowing what a homeowners expectations are will help with tank selection.

    If a tub is used frequently I suggest more storage capacity compared to a larger boiler able to give you 4 gpm or more

    Tank temperature could be elevated and mixed down

    Operation above 140 will shorten tank life and precipitate more minerals

    What did you have for DHW in your previous home?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    GGross
  • mattmia2
    mattmia2 Posts: 18,399

    i have a similar setup to theirs but with a 20,000 btu/hr larger boiler and i can run it out of hot water with a long, adequate shower all by myself. if they want to fill a big tub or use 2 or more showers at once their capacity is way too small. they would need a huge electric to do it with electric because of its essentially nonexistent recovery rate compared to their consumption. that boiler can recover an 80 gallon tank in less than half an hour. electric would take about 130 minutes to recover 80 gallons.

    Philthechill
  • Hi, Another option could be to add a 40 gallon (or bigger) tank in series with the existing 40 and pipe it so both are heated by the boiler. It could be a lower cost way of solving part of the problem. Still seems DHW priority isn't figured out yet.

    Yours, Larry

    Philthechill
  • I have an extra 50 gallon tank that my father in law used for about two weeks before he swapped to a bigger tank. I am very much considering putting that in. Dhw is set to 60 Celsius btw. Shower heads are about 3.5 gallons a minute and the tub would be 6gpm. I was concerned from the first time I ran out of hot water that my plumber installed a boiler that was too small. But he didn’t even spec it, he went to the lochinvar distributor and that’s what they recommended. Now whether or not he told them all of the correct info for the build is another question.

  • My last home used an electric hot water tank. I think it was 50 gallons. But the house was only 1600 sqft.

  • the tub is 66x34 free standing tub. It’s approximately 45 gallons at 3/4 full. Now writing down those numbers and knowing how large my indirect tank is, my tank doesn’t seem large enough at all.

    hot_rod
  • its using a tank sensor, tank is set at 60 Celsius. Boiler set point for dhw is 76 Celsius.

  • I was the GC of my house with my brother in law being the technical side of it since he’s built houses for about 15 years. But I left the plumbing work to my plumber and didn’t question his boiler selection, he had put a boiler in my brother in laws place and they haven’t had any issues but they have a walkout bungalow with the same amount of square footage and had gotten a larger boiler due to a lot more concrete floor to heat. So they haven’t had issues with running out of hot water. If I could I would replace the boiler with a larger one but that is money I can’t and won’t spend. Knowing I won’t be able to return the current one.

  • also i have watched the boiler when the dhw is called. It does start heating the hot water, but it doesn’t completely stop heating the infloor right away, sometimes it took quite awhile for the infloor to close the valves. That’s why I turned the times down.

  • mattmia2
    mattmia2 Posts: 18,399

    it is usually better to size the boiler to the heating load and get the needed dhw capacity with bigger indirect tank(s). if you get the capacity through boiler sizing then the boiler won't have sufficient turndown to match the heating load when it isn't at design conditions which will be most of the time.

    Philthechillrick in Alaska
  • I have read the technical manual for this boiler front to back and there are no settings to make dhw the priority, so I agree that it must be standard on it for the dhw to be priority, but from what I was reading elsewhere that the switching times basically told the boiler how long to keep the flow valves open for space heating before completely closing and switching to dhw. Unless im wrong, but that’s why I’m on this forum, to troubleshoot and find out more.

  • mattmia2
    mattmia2 Posts: 18,399

    usually it is the other way around. it immediately switches to the dhw zone on a dhw call and turns off the other zones but there is a timer that if the dhw call lasts more than x minutes it resumes the domestic heating zones in addition to the dhw zone.

  • hot_rod
    hot_rod Posts: 28,706
    edited December 2025
    IMG_1565.png

    this indicates the boiler pump turns off on dhw call

    If it is in zone mode a primary loop pump would also run

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2GGrossIronman
  • psb75
    psb75 Posts: 1,181

    Yikes, those 3.5 gpm shower heads and the 6 gpm tub spout should be plugged into your math equation (time x flow volume) when figuring your dhw needs in a given use-scenario. Your boiler (and tank) is too small. Maybe…change shower heads? Co-ordinate showering and bathing habits? Ah, "first world" problems.

    Ironmanbjohnhy
  • Kaos
    Kaos Posts: 1,003
    edited December 2025

    Filling a 40 gallon tub doesn't need 40gal of hot water since tub is usually filled with 105 or so which uses about 30 gallons. It is still a big drawdown and not much left in the tank.

    Before throwing money at the problem, I would make sure what you have works properly. Fill with 140F water, how many gallons can you get out of the tank with the boiler off?

    When the boiler is running on DHW recovery, what is the temperature delta between supply and return? How long does it take to recover the empty tank?

    If all is working well, you can look at lower flow shower heads. I run a 2 gpm rain shower and it works great, there are many out there:

    https://www.hansgrohe.ca/en/articledetail-raindance-s-showerhead-300-1-jet-2-5-gpm-27493001

    Since metric, I'm assuming Canada, which generally means basement, so access to your stack. You can also look at installing a drain water heat recovery unit which saves you money if you shower a lot and also reduces the amount of hot water you need for a shower.

    https://www.homedepot.ca/product/power-pipe-3-inch-diam-48-inch-long-price-includes-drain-connectors-/1000698161

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    While the 40 may not be enough I don't believe the controls are set properly. If you set the controls right and keep the tank at 135-140 and mix it down and be a little more selective in your water, use you might get by.

    GGrossIronman
  • GroundUp
    GroundUp Posts: 2,573

    Your tank temp and boiler temp can both be turned up, but it sounds like you either have a control and/or piping problem because the system circ should shut off immediately upon DHW call and there should be no flow through the radiant at all. Is the indirect tank piped as a zone with its own valve and a single system circulator, or is it piped direct from the boiler with its own circulator?

  • mattmia2
    mattmia2 Posts: 18,399

    Not sure from their post if that is the case. They say "It seems like the boiler can keep up if it starts heating to 100% right away." but it isn't going to start until the dhw tank cools enough to drop the aquastat/tank sensor below the cutin point so it isn't clear if it isn't doing dhw priority or if the OP just doesn't understand how it works. There are probably some icons on the Lochinvar that show which calls it has and their state if you look at the control panel pages of the manual. Usually they will do something like light the dhw icon when there is a dhw call and flash the dh icon when there is a dh call but servicing that call is paused because of dhw priority. It is also possible that the draw has gone on long enough that the dhw priority timer has expired when they look at the boiler.

    But basically they have a tank and boiler combination that is sized for one bath if they are careful and they have 3 baths connected to it.

    GroundUp
  • GGross
    GGross Posts: 2,104

    you really think a 40 gallon boiler mate with an 80k boiler is a 1 bathroom tank? I have a 50 gallon low efficient gas w/h with a 50k burner and run 3 showers simultaneously when the family comes up, one of those showers has 3 people use it one after the other and we don't run out. If all the OP was having issues with was regarding their tub I'd say its definitely too small, but they also said if they run 2 showers at the same time they run out. If these are somewhat standard showers then they have a piping or control problem in my opinion, the tub might still not be able to go at the same time as the showers though.

    GroundUpbjohnhy
  • mattmia2
    mattmia2 Posts: 18,399

    what temp is your incoming water? i can run my 40 gallon superstore with a 100,000 btu/hr in boiler out with a single shower if i'm not careful. some times of year the incoming water temp is about 35 f here.

  • GGross
    GGross Posts: 2,104

    somewhere between 35 and 40 depending. I'm on a deep well in the tip of the mitt northern michigan. we got pretty cold well water as well.

  • Jamie Hall
    Jamie Hall Posts: 27,975

    All this is partly a matter of usage and perception. If your squad comes off maneuvers and takes a Marine shower one by one on the way to mess, yes you can get by with a 40 gallon water heater.

    If you wear your hair long and want to get it really clean, probably not.

    If you like to soak in a nice hot bath, certainly not.

    I have never quite figured out why people resist putting in a big enough hot water heater. I can see it in some situations — space constraints, sometimes availability constraints. But if you can put in a big enough unit, why not do so?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hot_rod
    hot_rod Posts: 28,706

    I agree, there is no definition of adequate DHW for a home. This is pretty owner specific. You can have whatever capacity/ volume that you are willing to pay for.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • GGross
    GGross Posts: 2,104

    I'd still prefer to know how a system is controlled and piped prior to changing it out for a bigger tank I think.

    GroundUp
  • Hi, One big and one small reason not to oversize storage. The small one is more heat loss/waste from the greater surface area of the bigger tank/s. The big one is the tank can become an amplifier for bacteria if the volume of the tank is not turned over pretty consistently. The bacteria then gets inhaled in the shower or elsewhere, and nobody is happy.

    Yours, Larry

    GroundUprick in Alaska
  • Kaos
    Kaos Posts: 1,003

    @GGross Yet boiler guys keep installing indirect that cost more (bom and install), have about the same operating cost and don't really get more hot water.

    My experience with my coil based inidirect is that it worked well for a couple of years but once scale built up the heat exchanger, recover dropped. I eventually converted it to plate HX to feed the tank which did work much better in the long run.

    GroundUp
  • Ironman
    Ironman Posts: 7,975

    I have six daughters and one son. They were all teenagers at the same time, so you can imagine what the hot water demand at my house was.

    I installed an outdoor wood boiler just because of the domestic load. When we didn’t use the wood boiler during the warmer months, the entire family got by using a 50 gallon gas water heater. They learned to schedule their showers around mom and dad’s and each other.

    I install a lot of boilers and indirects and an 80k btu boiler with a 40 gallon indirect is always more than enough for an average family. It’s only when there’s an unusual demand (like a car wash shower or a large hot tub) that more capacity is needed.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    Alan (California Radiant) ForbesEBEBRATT-EdGGrossGroundUp
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    Agree with @Ironman If your running out that quick with 80k input and 40 gallons of storage your wasting water.

    I also agree with @hot_rod DHW use varies widely.

    I know people that get by with a boiler with a tankless heater. You learn to live with what you have.

    If you want to pay for the horsepower to run the dishwasher and the washing machine and 3 showers and a tub you certainly can do that.

    I think the ops system may be undersized for its present use btu I also think there are control issues.

  • hot_rod
    hot_rod Posts: 28,706

    first step is confirm the piping matches the DHW control setting.

    If the indirect is a parallel loop, then just one pump runs, boiler pump shuts off via the boiler control module.

    If it is primary secondary, 2 maybe 3 pumps need to run.

    Also the indirect loop piping should be 1” to move the boilers full output and get fast recovery

    Boiler should go to at least 180 target on DHW call, the control display in view mode tells you all this.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    GGross
  • HomerJSmith
    HomerJSmith Posts: 2,837
    edited December 2025

    A couple of questions.

    What is your altitude? Higher altitudes decrease boiler BTU rated output.

    What is the flow rate to the heat exchanger on the T Tank? A I" T Tank heat exchanger can accommodate a higher flow. Heat exchange transfer relies on two factors, water temperature and flow rate. Increasing the T Tank storage temp, as stated, increases the tank heat storage capacity and with a mixing valve keeps the delivery temp at about 120-125 degs..

    Is the input and return to and from the boiler to the tank piped correctly?

    This may or may not apply. Do you have a re-circulation circuit on the T Tank? If so not piped correctly, colder water could be mixing with the hot output at the faucet. Measure the temp of the hot water at the faucet when the boiler is only putting out hot water to the faucet. Does that match the hot water output at the T Tank?

    Some thoughts.

  • tim smith
    tim smith Posts: 2,935

    change shower heads to 1.5 or 1.75 gpm, tub is what tub is. Raise indirect tank up to 140 or even up to 160 if still running short. Add tempering valve off dhw outlet pipe to limit temp to 120. This will probably get you by. Maybe not if wife filling tub but may get close.

    bjohnhy