Attached EDR vs Boiler SF of steam

Options
Fizz
Fizz Member Posts: 555

My attached radiation is 337.5 SF, and new Peerless gas steam boiler rated at 233SF. Is this sufficient? Single pipe with separate return.

Comments

  • JohnNY
    JohnNY Member Posts: 3,333

    If you're numbers are accurate, then no it is certainly not.

    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • ethicalpaul
    ethicalpaul Member Posts: 8,026
    edited December 3

    Well 233 * 1.333 = 310 so it's not TOO far off given the industry standard "pickup factor"

    If the mains are insulated and/or the house has the typical oversized radiators, and/or the house insulation/windows have been updated, and given the higher design day temps since the house was probably built I would run it. You might not quite keep up with your setpoint if you had a cold snap, but you wouldn't freeze. Space heater would help. We're only talking about the coldest days where it might struggle I think.

    As we all know, on a typical call for heat the radiators don't completely fill with steam anyway. It is the radiator vents that regulate which radiators get steam at what rate. The boiler doesn't know if you have 800 sq ft of radiation or 300 on a typical call for heat.

    Isn't it true that a perfectly sized system should run 24 hours a day on the coldest design day? My boiler is only a little oversized and I have never even come close to a 50% duty cycle I think. Has anyone ever actually installed a system of any heating technology that actually runs 24 hours straight on the coldest day?

    You'd hardly ever or never cycle on pressure, that's for sure, that's a plus. You could increase the gas regulator from the factory 3.5 inches of water column to like 4" to get more steam production.

    You could buy a new burner tray from Peerless spare parts to upgrade it from 63-03L to 63-03 which would get you 308 sq ft of steam which is really 410 sq ft. Although my current understanding is that Peerless doesn't support doing that.

    Finally, given that Peerless 63 series is now discontinued you might be able to find a buyer for it and get yourself a larger Weil-McLain or Utica.

    How did you end up with Peerless's smallest steam boiler for this house?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Steamhead
    Steamhead Member Posts: 18,168
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    JohnNY
  • Fizz
    Fizz Member Posts: 555

    My apologies! My EDR is 237.5!!! I chose the one closest to EDR

  • 109A_5
    109A_5 Member Posts: 3,302

    If the EDR is 237.5 and the boiler Sq.Ft. is 233 the system should work good.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Fizz
    Fizz Member Posts: 555

    Thanks! What a relief. Posted wrong EDR in orig post. Old age doesn't come alone

    ethicalpaul
  • dabrakeman
    dabrakeman Member Posts: 838

    Sure you just didn't want to stir the pot?😁

    EdTheHeaterMan
  • ethicalpaul
    ethicalpaul Member Posts: 8,026
    edited December 3

    OK in this case there is no "should" about it, this boiler will perform as good as any boiler you could pick.

    Congratulations for getting one of the last 63 models ever produced

    To quote one of my favorite movies, "it would be a shame to blow it up"

    And congratulations for resisting going to the next larger one "just to be safe". You have somehow, some way, actually purchased the correct sized boiler, making you very rare around here!

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    dabrakeman
  • Fizz
    Fizz Member Posts: 555

    I sometimes think I'm in the pot!

    Thanks guys.

    EdTheHeaterMan
  • 109A_5
    109A_5 Member Posts: 3,302
    edited December 3

    Paul we don't know how if it is piped or skimmed correctly, so it 'should' work good. Since it is the correct size.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • bdl
    bdl Member Posts: 63

    I have a question on matching EDR to a boiler. Should the boiler sq. ft be equal to the total radiator EDR? If not, how is the pickup factor applied? Can someone write out an equation? For some reason this isn't sticking in my head.

  • ChrisJ
    ChrisJ Member Posts: 17,036

    The EDR rating on a boiler includes the 33% pickup factor.

    I'd never exceed that rating my self. IE. if the boiler's rating is a hair under, do not go to the next size bigger, it's a mistake.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    EdTheHeaterManethicalpaul
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,279

    @bdl as @ChrisJ mentioned total up the rad EDR and compare that # to the boiler nameplate. Don't add anything

    EdTheHeaterMan
  • bdl
    bdl Member Posts: 63

    Thanks for clearing that up. Umm, the boiler states sq ft of steam, not EDR. They have the same units, correct? Hmm, my current boiler is 450 sq ft, and my EDR is 404. I think the next boiler down was 350 sq ft.

  • pecmsg
    pecmsg Member Posts: 6,706
    edited December 4

    I’d go with the 350.
    you can always tighten up the envelope if needed

    ChrisJethicalpaul
  • 109A_5
    109A_5 Member Posts: 3,302

    Or go with a different brand boiler. For example the chart posted above the Peerless 63-04L is 383 Sq. Ft. if that makes you more comfortable.

    My old 300 Sq. Ft. boiler and 347 of EDR works fine, even when it is below zero Fahrenheit outside.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    ChrisJ
  • ethicalpaul
    ethicalpaul Member Posts: 8,026

    They are the same units. Always round down. Always

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    ChrisJ
  • Fizz
    Fizz Member Posts: 555

    In second day of Peerless 63, last nite 9degrees, today 25, tonite 6. I can't believe how well it's working…so quiet, radiators all doing what their supposed to. I've been a member for yrs. My prior house had a Richardson Vapor system, I actually got it working in vacuum. Actually had one of main steam guys here who came to house in Pittston, Pa. He was from Jersey and he was only one who'd work on pipe that needed to be addressed. It was wrapped with asbestos and no heat guys locally would touch it. After it was piped correctly, I was able to put a vacuum vent on which worked wonderfully. I chose the Peerless because it was closest to EDR. The company I dealt with installed only WM, PB and Nivien.

    dabrakeman
  • bdl
    bdl Member Posts: 63

    How far should one round down? Say the next one down is 350 sq ft, your EDR is 400, next one up is 450? Which one?

  • Steamhead
    Steamhead Member Posts: 18,168

    450.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    bdl
  • ethicalpaul
    ethicalpaul Member Posts: 8,026
    edited 9:26PM

    Well those aren't actual numbers. So if my EDR is 400 I pick Peerless 63-04L

    Here's peerless:

    image.png

    Here's WM:

    image.png

    Here's Utica: (I think the first number is NG and the second number is LP)

    image.png

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • dabrakeman
    dabrakeman Member Posts: 838

    Lots of good options for a true 400sqft. I think a few % undersized could be a sweet spot for many homes. Your hypothetical example is 11% undersized if go the smaller route. There are many here that would probably say go for it. I'd say depends on how much you know about the performance history of that specific system and you perhaps as the homeowner are willing to manage the system such as insulating mains well, putting in adequate main venting and likely going through some trial and error balancing. So, depends. I think many professionals installing on someone else's house or business may not want to incur the risk.