Air purgers with compression tanks

Options
hot_rod
hot_rod Member Posts: 26,355

Systems with plain steel compression tanks are referred to as air management systems. Meaning that the air bubble in the compression tank cannot be removed, it is the expansion space.

B&G and others devised a couple components to allow air captured in the top of the boiler sections to be placed into the tank via their Airtrol ™ components.

B&G also shows both the IAS inline air separator and the EAS enhanced air separator, a micro bubble type air separator being used instead of the Airtrol fitting into the boiler.

I believe both of these B&G products have been discontinued.

Screenshot 2025-11-26 at 8.22.45 AM.png

Screenshot 2025-11-26 at 8.22.38 AM.png

On my solar drainback tank at my last shop I piped the air vent discharge from a Discal up to the air space in the solar tank. In fig 5-10 it shows the Discal piped to the top of the tank at a cross fitting, and the siphon break air tube piped to that cross. So any air removed from the circulation, gets placed in the air bubble at the top of the tank.

I believe any microbubble type purger with a treaded vent connection could be used on a boiler system with the steel compression tank.

Any experiences with this arrangement?

Screenshot 2025-11-26 at 8.24.14 AM.png
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
Ironmanmattmia2

Comments

  • leonz
    leonz Member Posts: 1,719

    Hello Bob,

    According to Xylem/Bell and Gossett The ATFL, ATF air management valves and steel compression tanks are still offered by them.

    My Bell & Gossett 15 gallon steel compression tank was manufactured by The Wessels Tank Company.

    Happy thanksgiving.

  • Ironman
    Ironman Member Posts: 7,824
    edited November 26

    The air discharge port on a SpiroVent is 1/2”MPT, so that can be piped to a compression tank to maintain the air cushion.

    I’m not aware if any other brands of air separators (MBR) that are made that way.

    IMG_1199.jpeg
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2HydronicMikeSuperTech
  • jumper
    jumper Member Posts: 2,494

    Can an air purger produce gas at a high enough pressure to go into a compression tank? If it can then eventually compression tank will be charged with nitrogen as oxygen is consumed. My guess is that purgers should exhaust into some sort of vacuum tank. I've seen compression tanks charged with compressed nitrogen. A Cadillac system uses a vacuum tank for expansion. The tank has to be installed at high point. Very rare today but for taller buildings before circulator pumps; who is old enough? My guess is that overhead distribution was used.

    mattmia2SuperTech
  • hot_rod
    hot_rod Member Posts: 26,355

    this B&G piping shows a basic micro bubble air sep going into a non diaphragm, plain steel compression tank

    IMG_1526.jpeg

    I think the airtrol fitting into the boiler is just venting the air into the compression tank also.

    I have heard of diaphragm tanks pre-charged with nitrogen, but I haven’t had that confirmed by Amtrol or any other manufacturer

    I was told that refrigerated air, dried air, is used to pre-charge tanks.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • hot_rod
    hot_rod Member Posts: 26,355

    This thread adapter fits most of the brass air vents, Taco offers them also

    IMG_1524.jpeg

    This just converts that metric thread to NPT so you can can put a copper tube on the outlet

    While the spiro has a 1/2 npt, the hole in that stem is around 1/8”, that would be the limiting factor in how much air vents out

    IMG_1527.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • jumper
    jumper Member Posts: 2,494

    @hot_rod I've seen air separators going into compression tanks but who has measured how well that works? Tanks still get water logged so where is the air? I've also seen doohickies to vent air (to atmosphere) but not water at top of system. If pressure is controlled correctly no apparent issue. I've seen that work well for decades until somebody/something increases pressure enough to pop the doohickey.

  • mattmia2
    mattmia2 Member Posts: 15,192

    i think if you use a standard microbubble air separator you would either need to remove the float and needle or pipe a second pipe from the system to the tank so that water could flow freely both ways. ideally you would also have a tank fitting or pipe loop to prevent gravity circulation out of the tank too. The schrader cap to npt adapter would make almost any microbubble separator work.

  • hot_rod
    hot_rod Member Posts: 26,355

    good catch on the air going in and out

    The B&G has the float vent removed and just the purger part connected to the tank fitting

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • leonz
    leonz Member Posts: 1,719
    edited November 26

    If the water fill valve is left on or there is water leaking into the system a steel compression tank will waterlog. They always work as long as they are sized correctly and the water feed valve is closed and not seeping into the system as long as the proper air to water ratio is created with an airtrol valve to maintain the point of no pressure change.

  • jumper
    jumper Member Posts: 2,494

    An improvement may be to somehow locate separator at lowest pressure. That would be at top of circuit. Some buildings located boiler on roof of building.

  • leonz
    leonz Member Posts: 1,719

    The Xylem/Bell and Gossett information sheet describe how the steel compression tank or multiple tanks are plumbed in parallel with one airtrol fitting in each tank are hung between the ceiling joists in a basement above the boiler feeding the air bubbles stripped out by an Internal Air Separator that is used in a pumping away method.