Does metal radiator cover affect performance? Absorbs heat or passes it along?

Options

Metal case. Hinged top is open.

Does case absorb heat and just relay it to the room? Net zero impact?

Or does the metal case eat some of the heat?

image.png

Comments

  • hot_rod
    hot_rod Member Posts: 28,078

    well it certainly blocks a portion of the radiant heat transfer. For convection, you need a slot at the bottom and top for the warmed air to pass out.

    Probably not as restrictive as draping a blanket over the radiator but un encumbered would give it the best opportunity to move its output, out😗

    I’m not sure it is being eaten? It just doesn’t make it into the room space.

    Good news, the next radiator down the line has more heat energy available.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2ethicalpaul
  • CoachBoilermaker
    CoachBoilermaker Member Posts: 462

    But the cover in the photo has a slot at the bottom and the top is hinged open.

  • mattmia2
    mattmia2 Member Posts: 17,905

    if the top is left open it probably doesn't affect the convective heat output but some of the radiant heat being reflected back to it by the enclosure will reduce the radiant heat output.

    PC7060ethicalpaul
  • HeatingHelp.com
    HeatingHelp.com Member, Moderator, Administrator Posts: 267
  • CoachBoilermaker
    CoachBoilermaker Member Posts: 462

    I guess the cover is just like the radiator metal itself. Just another skin. Obviously, the heat gets thru the thick radiator metal

  • Steamhead
    Steamhead Member Posts: 18,805

    @CoachBoilermaker , the metal of the radiator stays the same, but if you add a cover you can lose up to a third of the rad's capacity. Read the article linked in the above post for more detail.

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

    Grallert
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,834

    Expanded metal like that is too restrictive. You need opening at the bottom and the top (not the front) to get full capacity.

    It acts like a chimney.

  • hot_rod
    hot_rod Member Posts: 28,078

    If you have air space between the skin and radiator you no longer have conduction heat transfer and the skin will not get to the temperature of the cast iron. The air space is an insulator.

    Push the sheetmetal skin against the cast and you have a different dynamic.

    3 modes of heat transfer

    Conduction, a pan sitting on a electric stove top

    Convection natural or forced, fin tube or an air handler

    Radiation, thermal radiation is what we experience from the sun shining. If a heat emitter transfers 50% or more of it's output by radiation, it is considered a radiant panel

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Marc_18
    Marc_18 Member Posts: 22

    The primary mode of heat transfer here is via convection. With the open lid and slotted bottom, the radiator cover is fine.

  • pugman2
    pugman2 Member Posts: 16

    We just had our dinning room completely repainted and decorated with block wall accents. The radiator in that room is 7' long ! It's hard to cover that under the bay window. I celebrated the size by painting it silver/aluminum. Looks great.

  • Mark Eatherton
    Mark Eatherton Member Posts: 5,875

    This is a VERY interesting subject, and it encompasses most everything about heat transfer known to mankind, and a few we don't know, "see" or acknowledge. Kudos to Dan and Frank for their contribution, as well as the Dead Men.

    First off, remember that thermal energy can't be created or destroyed, only converted, used and dissipated. The actual net output of a radiator, as shown by Dans old charts can be "enhanced" and increased by forcing one of the means of heat transfer to be increased or suppressed , that being the chimney effect of convection.

    You can also increase the radiant output, but that requires significantly more manipulation of the variables, i.e. the MRT within the room. If you have a cold room, whereby all the surfaces surrounding the radiator (MRT) are cold, and immediately dump steam into the emitter, once it has its own mass heated up (conduction) and it's emitting surfaces are up to its maximum, its' radiant output is significantly higher than would be under "normal" considerations. Of course, its convective outputs should also be higher at that point due to the same variable, that being differential temperature of the "fluid" (air) being in contact with the emitters (radiator) exposed surfaces.

    Covering the emitter changes all of those dynamics. It' can't "destroy" them, it can only change them, and in my minds eye, those changes are numerous and can only SLOW the flow of heat (radiant and convective) but all the heat the radiator is capable of producing should still end up in the room. For example, radiant heat from the radiator will be absorbed by the metal cover. Through conduction (minus the convectionocurring inside the cover) the outer surface of the cover will get hot, and will then re-radiate heat to the surrounding surfaces (minus the convection of being in contact with a cooler air, which then rises up, thereby creating additional convective extraction). The difference between radiant and convective on these outer surfaces are a function of many additional things that most people don't think about, like color.

    Not only the color of the emitting surface, but also the color of the absorbing surfaces surrounding the radiator. It is a known fact that the dead men painted the radiators a metallic color to suppress their output. I've tested copper fin tube in joist bays, and by painting the fin tube a flat elm leaf green, and painting the joist bay flat black, increased the radiant output of the fin tube significantly, like by 25% if memory serves. So flat black radiator in a dark painted room will output more radiant than convective energy. This is one of those factors that is tough to "see" in ones minds eye. Copper and shiny aluminum have a different "emmisivity" than do flat colors. I also once tested a ceiling radiator the I had built out of copper and aluminum. Just by painting the metal a flat white color, the delta T on the fluid side went from 5 degrees F to 10 degrees F, and you could "feel" the difference in radiant heat being output.

    The convective capacity is a function of surface temperature, surface orientation, chimney affect and fluid (air) flow resistance. Within some radiator enclosures I've seen, there are curved surfaces at the back bottom and back top to enhance air flow and lessen resistance to air flow. Sharp surfaces create eddy currents that cause the flow to slow, and hence reduce output. Surface area and orientation should be fairly obvious. So as with any question regarding Hydronics, the only correct answer is "It depends…"

    As Dan always says, keep an open mind and a bright flashlight on hand at all times. It's necessary to "see" all of the players in the game to determine the net results, and even those will change as the room and emitter dynamics change. As the differential in air temperature and surrounding surface temperatures change, so do the active dynamics.

    Hope this helped to open your eyes. :-)

    ME

  • CoachBoilermaker
    CoachBoilermaker Member Posts: 462

    So the metal casing will absorb but then pass along the heat to the room?

    Mark Eatherton
  • hot_rod
    hot_rod Member Posts: 28,078

    Assume any changes made to the radiator will change output.

    However adding a fan behind or below will "force" some convection and add output.

    The air space between the radiator and the sheetmetal cover will prevent the cover from reaching the temperature of the cast iron, so radiation transfer is reduced.

    Any change to the air flow design through the radiator will change the output.

    Now you have a constipated radiator.

    Any heat that cannot be "emitted" to the room by any changes, goes back to the boiler.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    bburd
  • patrykrebisz
    patrykrebisz Member Posts: 142
    edited November 2025

    if you take two exact rooms, one with just radiator and the other with covered radiator, the one with covered radiator will heat up the room 15-25% slower. mostly, due to restricted air movement.

    »»» See my steam heat YouTube videos:
    https://www.youtube.com/@HeatingBlog

  • Steamhead
    Steamhead Member Posts: 18,805

    Why not have the rad refinished, and lose the cover?

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

    BobC
  • dabrakeman
    dabrakeman Member Posts: 1,021

    I sense the cat would complain.

  • dabrakeman
    dabrakeman Member Posts: 1,021

    I have always thought nicely finished radiators were more attractive than the enclosures, but, if indeed you wanted to move toward the configuration you mentioned I guess you could just drill a couple hundred holes in the top or saw off all but the last two hinges worth of the cover at the vent end (for the sake of the cat). If we believe it according to the publication you are referencing adding a mid shield inside the front of the enclosure to enhance the convective flow path would get you another 5%.

    There is a competing enclosure document out there that unlike the one being referenced shows no configuration with "enhanced" output vs naked radiator.

    Day_Tripper
  • hot_rod
    hot_rod Member Posts: 28,078
  • neilc
    neilc Member Posts: 3,201
    edited November 2025

    these cats in direct contact, how are they not burnt? or do they leave as the rad gets steam hot?

    known to beat dead horses
  • guzzinerd
    guzzinerd Member Posts: 463

    I bought this old cast iron rad cover over 20 years ago in Miami for a few bucks, the top is poured concrete. I'm still waiting to cover an actual radiator with it.

    1000027110.jpg

    Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf

    Day_Tripper
  • dabrakeman
    dabrakeman Member Posts: 1,021

    Cutting the lid where you marked it seems an easy immediate remedy for cat and masters. Cats are finicky though. He may like to walk the plank to find his optimal temperature zone😁. Obviously which end you leave him will impact the propensity for a warm seat.

    Shield you could probably hook on from the inside. I would lean toward sheet metal or aluminum over an insulating material. Trying to enhance convection, not seriously reduce conduction and radiation.

    Day_TripperTonKa
  • CoachBoilermaker
    CoachBoilermaker Member Posts: 462

    Is there a big difference if @Day_Tripper

    keeps the top open one inch (photo)

    vs. keeping the lid all the way open?

    Untitled Image
    Day_Tripper
  • dabrakeman
    dabrakeman Member Posts: 1,021

    Cant find any examples of an enclosure that blocks some part of the front but with a wide open top. Guess that is because it is not about aesthetics, rather it's all about the cat.

  • hot_rod
    hot_rod Member Posts: 28,078

    radiators like that are about 80% convection, 20% convection

    Conduction transfer when the cat is touching the cast iron

    The amount of heat output depends on the square footage of the radiator

    But don’t discount the heat effect of the radiant as you stand in front of a warm surface radiator that is the selling feature if radiant systems

    You may need to play around with grill size on top to make sure you cover the heat load in coldest conditions if you go that way

    In older homes, windy days can be high load days also

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • guzzinerd
    guzzinerd Member Posts: 463

    Would make a great window guard if it didn't have the concrete table top.

    Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf

  • gfrbrookline
    gfrbrookline Member Posts: 788

    For what it is worth I have a steam radiator in my bedroom that I put a piece of granite on top of that was leftover from my kitchen remodel. It did cut down on the amount of heat the radiator gave to the room, not huge but noticeable but my cats love the heated bed.