Need new boiler
Good day.
I had a service tech. do our yearly check up. Our 25 year old Buderus boiler is burning poorly and I can see rust on the inside top.
The tech. quoted me a price for a Navien tankless boiler. Can I replace with a comparable boiler if there is such a thing?
Thanks for the help! Jeff
Comments
-
There's a lot more to it than that.
First, "burning poorly" is a service and adjustment problem. Something a competent tech should be able to remedy. A brand new boiler can burn poorly. A 50 year old boiler can burn very well.
Second, rust — without a leak — is not necessarily a problem. Is it leaking? If not, it ain't broke.
Now let's suppose that it is in fact leaking.
To replace it you first need to know what the actual heat loss or power demand of the system is. With hot water heat, there's no point in putting in a boiler which can make more heat than the building can use. Also with hot water, it helps to know what temperature the system needs to run it — which is determined partly by the heat loss and partly by the radiators or baseboards or whatever that are in there..
Then you need to choose a fuel.
Then you can begin to wonder what boilers to look at.
Oh and just one more thing. We don't quote prices on The Wall.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
-
-
A few pictures would help.
0 -
Hi @jeff3176, I've edited out the pricing in your post as it goes against the site rules. I also agree with @EBEBRATT-Ed that posting a few pictures of your system would help us help you.
Forum Moderator
0 -
-
You asked for salami, you got baloney.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
guys doing yearly check ups, most of the time, dont understand steam.
they know enough to do basic wrenching but their knowledge ends there. and they can actually make your system work worse (as was the case with one of my "techs").
the usual qute for boiler replacement is price of the boiler (look it up) x3. it's expendive! especially since one of those Xs is due to fact that lack of skilled trades people allow the plumbers to quote what they want.
bring in a skilled plumber, not a "tech" that comes with one of those yearly contracts and they should solve your "poor burning ".
0 -
My boiler is a Buderus G 124 X. When I was told it was burning dirty, the inside wasn’t bad with the exception of the rust. Where the problem is is in the exhaust. The CO reading out the back is around 300 ppm. In the pipe the reading was over that. I’m not getting any CO alarms anywhere in the house.
0 -
As we have said — there's probably nothing at all wrong with that boiler that a competent technician with the proper test equipment can't fix.
You don't need a new boiler. You need a competent tech.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England4 -
-
Every so often I get called for a second opinion on wether a boiler needs replacement or not. Seems more often than not I tell the customer that while a new setup would save fuel, their boiler is in fine shape. What I find amusing is that sometimes the customer does eventually decide to upgrade and he gets us to do it instead of the company that said it needs replacing.
1 -
You got a salesmen ,the g124 is most likely one of the best cast iron boiler made in recent decades . In the past i have installed many and never had one issue ,I had a large company tell my parents that there g124 was in bad shape and parts where unavailable total bull being there off the shelf common parts . Get a new tech not a salesmen.
clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1 -
Is that the shadow of a steel compression tank on the wall? If so, the air eliminator shouldn't be there. And the boiler is fine.
0 -
what type of heat emitters, radiators or fin tube?
Rust around the flue connection could indicate it has been running to low of a temperature. Or short cycling due to over sizing. This can also lead to dirty combustion chambers
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements