Lwco shuts off when boiler overfilled?

My dad has a one-pipe steam system. Bless his heart, he thought he was helping but ended up overfilling the boiler such that water came out of the radiator air vents. We let out enough water so the sight glass level is where it should be and amazingly the system (fingers crossed) seems to be working okay. But I'm confused by what happened with the low-water cut-off.

When the boiler was overfilled, the low-water cut-off went dead. The green light that's usually on was off and the red button did nothing. I assumed it was shot from the overfilling and would need to be replaced. But right before the water level became visible in the sight glass, the low-water cut-off reset itself and now the green light is back on.

Is that normal? Is it monitoring the right/low level? Why would it shut down if the level of water is too high or the boiler is full?

Thank you!

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 7,853

    The high level of water in your system could have opened the pressure control (pressuretrol) switch which, depending on how your stuff is wired, could have cut power to the LWCO

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    EBEBRATT-Ed109A_5mattmia2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,802

    Agree with @ethicalpaul

    The LWCO should not go dead on a high water level

    109A_5
  • Snowmelt
    Snowmelt Member Posts: 1,448

    or it has debris on the tip of the prob giving a false reading, drain boiler take the l.w.c.o off and clean it …..

  • Jamie Hall
    Jamie Hall Member Posts: 26,497

    Totally agree. And it is surprising how "little" overfill will do this. In many installations the pressure switch and the LWCO (and maybe other safeties) will be wired all in series (there are other way to do this, but this is very common indeed). So — I'd say everything worked the way it was supposed to work.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • 109A_5
    109A_5 Member Posts: 3,021

    If the pressuretrol (assuming your has a pressuretrol and not some other pressure cut off device) was set for 1.5 PSI Cut Out and 1 PSI Differential, once the water level went above 3.5 feet above the pressuretrol (the weight of the water) I would expect the pressuretrol should shut off the burner, it may shut off other equipment too depending on the boiler's wiring. Once the water level drops below 2.3 feet above the pressuretrol, the pressuretrol should reset. Pressuretrols are notoriously inaccurate so these numbers may vary a bit.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • CalamityQueen
    CalamityQueen Member Posts: 3

    Thank you, everyone!

    There is a pressuretrol and my guess is this is what happened. (We live in an area where steam heat is rare, so a lot about this system is a little screwy.) Do I have to worry about any damage to the pressuretrol?

  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,435

    No need to worry about to the pressuretrol. Just to verify, you could unscrew one of the wires from the ptrol and see if the LWCO goes off

  • Jamie Hall
    Jamie Hall Member Posts: 26,497

    Keeping in mind that on some installations that wiring is line voltage…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,435

    True. Turn off the power before you do this

  • CalamityQueen
    CalamityQueen Member Posts: 3

    Will do. Thank you!

  • BobC
    BobC Member Posts: 5,531

    Some boilers (Smith G8) have the Ptrol and LWO on a 120vb loop instead of the 24v transformer loop so killing your power to the boiler is important.

    Bob

    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge