I realize this has been covered a million times. I thought for sure someone once said 1.33 was on the conservative side; if the mains were fully insulated, it was once said you could easily drop. I don't recall how much though, down to 1.2 recall.

Gotta guy with a dead boiler, and if I downsize a smidge I can get it up and running in a week. Or it's a 2-3 week wait for the Carlin 201GAS

Thanks for your opinion

Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com

Comments

  • GW
    GW Member Posts: 5,211

    Context- rads are 772 EDR. Thinking of a W/M SGO-7 with an EZ Gas running full bore- 275k. Just don't wanna get pinched😁

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Steamhead
    Steamhead Member Posts: 18,735

    Are the mains well vented and insulated?

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

    GW
  • Jamie Hall
    Jamie Hall Member Posts: 27,600

    Make sure the mains are well insulated and that is in range of should work well.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    GW
  • Jamie Hall
    Jamie Hall Member Posts: 27,600

    Oh. And near boiler piping! Meticulous!

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    GabGW
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,325

    What they said above for 1 pipe steam! For 2 pipe steam, you usually can orifice down the radiator capacity to about 60% of the existing EDR and then add about a 15% factor. You'll need to check heat loss if you go to orifices to make sure you have enough radiator capacity once downsized.

    To learn more about this professional, click here to visit their ad in Find A Contractor.
    GW
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,552

    7 section is good for 758 sq feet rads are 772. Your within 3280 over on btus. It will be fine.

    I wouldn't give it a second thought.

    GWmattmia2ethicalpaul
  • GW
    GW Member Posts: 5,211
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • GW
    GW Member Posts: 5,211

    Cool - it’s a one pipe

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • GW
    GW Member Posts: 5,211

    Ed Does the 275k input make you squirm at all?

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,552

    @GW

    I don't understand the question.

    If you rads are 772 sq feet and the boiler will do 758 those ratings are without the PU factor. The actual load is 772 x 240=185280 + piping and PU.

    The boiler can fire 280,000 input gross output is 240,000 after chimney and jacket loss. the difference between 240,000 and the radiation load of 185280 is 54720 which is what is left for piping and pick up.

    240,000/185280 so your left with a PU factor of 1.295 instead of the normal 1.33

  • GW
    GW Member Posts: 5,211

    @EBEBRATT-Ed sorry Ed I am throwing different factors.

    The bigger carlins are not available off the shelf.

    The Carlin EZ will run at 275k max, am I slicing hairs and running thin?

    Can I still expect the .85 with a gas gun? Will the EZ gas truly pump out 275?

    275 x .85 is 233

    233,000/ 185,280 = 1.25

    let it rip?

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • GW
    GW Member Posts: 5,211

    Jamie the current boiler seems to be a big ole 1970s Weil McClain, no header, no equalizer, no H Loop. I gonna try hard to make it better😊

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,552

    @GW, Got it.

    I think you will still be ok. I always question why the pick up needs to be so much. 33% is a lot. I can see needing more PU in the spring and fall when the boiler cycles a lot and sits off for a long time.

    When its really cold the boiler sits idle for a shorter time and the piping stays warmer and would need less PU in my opinion.

    The difference between 1.33 and 1.25 isn't much.

    Rather than taking the suppliers word for it it might be worth a call to Carlin to see if they can scare up a 201. Sometimes the distributors don't try hard enough

    GW
  • GW
    GW Member Posts: 5,211

    Thanks Ed

    I have a few EZ burners in my bone yard too, I could mount one if the 201 takes a couple weeks

    Or I can run an oil gun too, there are good tanks in the basement.

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,552

    @GW that would work I am sure they can get you the larger burner before it gets really cold.

    GW
  • mattmia2
    mattmia2 Member Posts: 17,569

    If you really want to know, you can estimate the amount of different sizes of pipe and figure the edr of that, i suspect you will find it is more like 10%, not 30%

    GW
  • mattmia2
    mattmia2 Member Posts: 17,569

    The smaller boiler will be happier than the one with the 30% pickup factor. It will better match the amount of steam the system can consume and will shut off less on pressure if at all.