Help Sizing A Multi-Zone Mini Split System - Minimum Capacity?
Comments
-
Yes.
Now, when it comes to sizing I'd be looking at your average annual low, which is -1F, and has a 27% higher heating load as 12F, which is the design temp I used, so you can go as much as 27% higher without really oversizing. You said earlier your designer was using a design temp of 6F, which accounts for some of the difference.
You try to get the heat loads as close as you can, and then you look at equipment. Typically it comes in half ton increments anyway.
1 -
Awesome… you've given me a lot to think about here, in particular the idea that I should be focus on the heat capacity at the low end rather than the nameplate capacity.
Although, I think that to some extent I do want to be mindful of the capacity at 47F? Avoiding short cycles and such, right?
We just got a 2nd proposal back (this one has Mitsubishi HyperHeat, the other was Bosch ducted downstairs, Fujitsu ductless upstairs) and its load numbers are 58K heating / 32K cooling. This new one uses a 3.5 ton for most of the house while using a 2.5 ton for the loft (C-03) and the ground floor room below C-02.
0 -
@JustinS : "Awesome… you've given me a lot to think about here, in particular the idea that I should be focus on the heat capacity at the low end rather than the nameplate capacity."
If you take away only one thing, that would be it.
"Although, I think that to some extent I do want to be mindful of the capacity at 47F? Avoiding short cycles and such, right?"
In the spreadsheet I put in a column for short-cycling loss, it's just a guess but if you don't put in something the numbers lead you toward dramatic oversizing. There's a tradeoff, as you go smaller you start coming up short on the cold end and have to supplement with resistance heat, as you go bigger the oversizing losses start to add up.
As a practical matter units come in fixed sizes, usually in half ton increments. So it boils down to picking between two sizes.
1 -
@DCContrarian Looking more closely at your spreadsheet - I was wondering how I might estimate the total kWh consumption for the entire house? Would I set up similar spreadsheets for each heat pump that's being considered?
If it were as simple as the whole house being 2x the 2nd floor and we were using 2 heat pumps of the same specification, I imagine that I could just double it and that'd be pretty good, right?
But since we won't have two identically sized units, I'd want to do a spreadsheet for each unit and use the heat load for the serviced rooms in cell B4, right? Naturally, I'd get the specific Heat Pump Performance Curve for each model.
Sound about right?
0 -
-
If you want "more better", have the contractor install a bunch of singles.
—more efficient
—quieter, no odd noises in the 'off zones'
—Better de humidification (smaller compressors means good long run times)
—easier to work on, less labor (especially if you pop a leak down the road)
—redundancy, if your big 8 zone goes down in 10 years for whatever reason, you're jammed until parts are located.
With hat said, we do large Multi Zone jobs all the time. It works. Is it perfect? No. Bit it does the job (heats and cools)
Pros and Cons galore when it comes to singles vs Multis
My last parting words- hire someone that will be around down the road to work on this thing, there's a certain 'reciprocation' factor. Finding a new contractor to work on a major repair down the road may be scary
1 -
@DCContrarian So I understand how to do sheets for each individual heat pump but how do I do it for multi-head splits units?
I have an AHRI number for each outdoor unit and its associated indoor units. What's confusing me is how to analyze each individual indoor unit. Or do you not do that instead treating them as a single combined system whose IDU always run together?
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 134 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements