I am trying to find out how to adjust the airflow on a Trane communicating furnace
Model# TUD2C100ACV52BA
The furnace is being controlled by a Trane thermostat is a model# TZON1050AC52ZB
Both the thermostat, and the furnace were installed in 2018, by others. The issue is that the air conditioner that is part of the system is four tons, 2 stage. The issue is that the interface on the furnace is indicating that the system is in second stage cooling, with an airflow of 1100cfm. This is resulting in good humidity removal, but the ductwork in a conditioned basement is sweating all over the place. The supply temperature is in the low 40's and well below dewpoint. I think if I can adjust the airflow closer to 1600 cfm the supply temperature will go up, and the issue will go away. I have found the instructions on the thermostat, but I can not find anything on the furnace. There are no dipswitches just the interface on the furnace.The other thing is that there are no thermostat wires connected to the conventional terminal block in the furnace, just one wire on the d terminal, i assume for dehumid. I assume the operation is controlled by some type of communication protocol like carrier infinity, but I did not see even a ABCD terminal block. Any assistance would be much appreciated. I am not trying to re design the whole system just adjust the airflow up to stop the duct from sweating. Thanks to all.
    I couldn't find the Trane manual although I searched for it. The answer is in the manual I am sure.
    Your down to 275 cfm/ton so that is too low. Is the unit oversized? 100,000 btu and 4 tons is pretty big.
    pecmsg Posts: 7,634
    edited July 2025
    How are you measuring the CFM‘s? If on the thermostat, it’s very inaccurate! That is the calculated CFM not actual.
    You need someone there taking static pressure readings to determine the actual CFM’s.
    HVACNUT Posts: 7,784
    Insulate the ductwork. Up in the Bay spaces won't sweat.
  • zepfan
    zepfan Posts: 494
    thanks for the responses. The cfm is what is being read on the furnace interface Yes I am fully aware that with the total ESP and the airflow table the correct cfm can be determined, however I can not find a manual that even lists that
  • ratio
    ratio Posts: 4,344
    Check the thermostat for a dehum setting, it may be commanding the fan to low speed to dehumidify.
    Do you have an installation manual for the thermostat? With no settings available in the furnace the next place I'd look for configuration options is in a communicating thermostat.
    Maybe try lifting the wire off of the D terminal, IIRC that influences fan speed.
    pecmsg Posts: 7,634
    That reading is Calculated not an actual CFM #. Real test equipment is needed to get the actual Static Pressure
  • zepfan
    zepfan Posts: 494
    Thanks for all the responses. After much digging I was able to find the directions at tranesupply.com. All airflow adjustments are made through the interface on the furnace. I was able to increase the airflow and that appears to have resolved the issue.
    Take care
    PeteA