Options
Mad Dog_2
Mad Dog_2 Posts: 8,755
edited June 2025 in THE MAIN WALL

Installed approximately 17 years ago...glue joint pulled apart easily. Mad Dog

20250627_102957.jpg

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    Obviously from what we have learned PVC for flues is not a good idea unless approved and the only one I know that is is Ipex,

    It looks like the glue and primer is good but who knows.

    Dis they sand the fittings and pipe?

    was the glue old?

    did they let the primer dry tooo long b4 gluing?

    It doesn't look like the PVC was overheated, it usually turns brownish.

    GGrossmattmia2LRCCBJ
  • mattmia2
    mattmia2 Posts: 18,399

    yeah, that looks like the glue was allowed to dry too long before assembling or they went over it a couple times because it dried

  • ChrisJ
    ChrisJ Posts: 17,763

    I just want to mention that when PVC is solvent welded, you're using a solvent like acetone or MEK to literally melt the plastic. Once the solvent evaporates it leaves the PVC solid again and in literally one piece rather than two.

    I'm not sure that even counts as glue, technically.

    If memory serves PVC cement is solvent with some pvc mixed into it to act as filler material.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    mattmia2GGross
  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    I installed dozens of GB- 142s with PVC exhaust before they banned it in NY. Never seen it be an issue, but apparently "they" decided it was. Mad Dog

    9326yssh
  • pecmsg
    pecmsg Posts: 7,634

    I still see a lot of installations using PVC on the east end!

    Mad Dog_2
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    MA has basically banned it I think.

    If the existing PVC flue is in a wall (difficult to replace) you can reattach a new boiler to it if the new boiler is listed for a PVC flue and the pVC shows no damage or overheating but then they want you to go to the new boiler with "approved pvc" like the Ipex so now you have a mix of PVC so its an issue.

  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    This Installer, whomever it was, was neat, conscientious and thorough...using plenty of primer and glue. I'm not supporting installer error. Mad Dog

  • HVACNUT
    HVACNUT Posts: 7,784

    It doesn't have that toasted marshmallow look. Any other joints come apart that easy?

    Mad Dog_2
  • pedmec
    pedmec Posts: 1,488

    That PVC pipe and coupling was not pushed in all the way. There is no way that pipe bottomed out in the coupling. My guess is the installer didn't notice it was pushing apart before it dried. The PVC is still white like its relatively brand new.

  • LRCCBJ
    LRCCBJ Posts: 1,043

    I am a bit curious on how you came to that conclusion. How can you know if it bottomed out or not by looking at the two photos? You certainly cannot judge this by the length of the primer.

    Mad Dog_2
  • very first picture looks like it could have gone in a little bit further, maybe 1/4 to 1/2 inch but kind of hard to tell. my unprofessional view is operator error but again, what do i know. thanks matt for the topic. i learn something new all the time.

    Mad Dog_2
  • JUGHNE
    JUGHNE Posts: 11,653

    That looks like 2" PVC. 2" couplings are a poor excuse of connection IMO.

    I Have always used pressure couplings for 1 1/2 and 2" venting and DWV…..over twice the bury and better stability.

    The ratio of bury to circumference gets better at 3", 2" is the worst.

  • Don_4
    Don_4 Posts: 41

    I have used PVC venting on scorched air systems for over forty years. That is clearly a poor installation job. A proper connection is actually a solvent WELD, impossible to disassemble after curing.

  • PC7060
    PC7060 Posts: 1,980
    edited June 2025

    The listed IPex system 1738 includes primer and adhesive with additives to allow for inspection via UV light.

    the primer and adhesive solvents seem to be more aggressive than standard PVC products with much stronger odor.

  • Bob Harper
    Bob Harper Posts: 1,189
    edited June 2025

    You can armchair quarterback your opinions and guesses as to the failure but without lab analysis you are still just grasping at straws. Was it installed per the mfrs. listed instructions as well as those of the PVC pipe mfr, the primer and the solvent cement? Was the pipe used within the approved applications by the pipe mfr? Was the pipe properly supported? Was it leak tested prior to use? Was the appliance inspected and tested including gas pressures, orifices, firing rate, MUA, intake air obstructions/ sizing/ pressures? Flue gas outlet temperatures? Any signs of overfiring in the unit or historical evidence such as tripped safeties? Was the heat exchanger ever replaced? Lot's of questions in a forensic investigation.

    I don't like PVC for a number of reasons: The pipes out there were never listed for this use but specifically forbidden per most pipe mfrs. While the pipe itself might withstand short term temps upwards 170F, the solvent cement routinely fails at 140F or lower. I've never seen an HVAC tech properly cut, chamfer, deburr or join PVC for venting. Never. I see pipe cut with a Sawzall held with one hand and the pipe with the other. The end of the pipe resembles a hole saw with all its jagged edges. The end is never chamfered nor deburred and there is no way to tell externally once the joint is made. Meanwhile, inside, the rough joint plows the cement pushing a dam of it ahead while scraping cement from the outer walls. The result is a very weak, often leaky joint.

    The pipe mfrs. expressly FORBID pressure testing with gas, such as done with gas piping. You can do a low pressure water test but how are you going to test the seal on a flush wall termination like a Bayvent? You would have to test with the pipe extended, tested, cut to length and attach AFTER the test. You might be able to rig a test ball in some cases. Also, on long runs through crawlspaces, you may get a few drips that harbinger a future failure yet not manifest during the test duration. You have to rely on one end of the pipe or another just as with gas pipe testing. That brings in the gauge resolution, test duration and allowable leakage. It has to be reasonable yet reflective of the conditions.

    The UL 1738 test seems fairly reasonable and reliable. It is also repeatable.

    Everything made by man can and will eventually fail. It's just a matter of when and at what cost.

    PC7060Mad Dog_2
  • hot_rod
    hot_rod Posts: 28,708

    when glue gets old and starts to gel it doesn’t work so well

    PVC that turns beige is an indication of over heating. If the boiler runs 140f continuously it is exceeding the temperature rating of pvc.
    boilers running 180 tend to stress the pvc quickly, color turns dark

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2
  • PeteA
    PeteA Posts: 328

    when I got rid of the old combi unit in my PA property I installed the polypro pipe for the intake and exhaust. The old unit had PVC which seemed to be holding up well since the installers installed it back in the day but man when I was comparing the weight of the newer material and the gasket instead of glues sealing methods I was really debating using the pvc in my install but the polypro was on the approved list so I bit the bullet and went with it. I just hope the polypro thinner walled pipe and the gasket seals hold up as long as the pvc did. Time will tell.

  • hot_rod
    hot_rod Posts: 28,708

    high temperature systems with PP and long horizontal run can be a problem if not supported properly.

    I have seen the piping sag and leak condensate at the joints.

    HTTP failed , standard PVC and CPVC isn’t the best solution, some stainless suffered gaskets or silicone adhesive failures,

    Hopefully PP holds up better. It is a harsh environment for the tube and seals

    Dirty or plugged HXers can run the flue temperatures up pretty hot. Hot enough to trip temperature safeties.
    Mod cons in DHW mode are generally exceeding the PVC, maybe even CPVC temperature limits

    Not to mention the lack of listing for flue gas conveyance on typical PVC pipe

    Yet manufactures are still sending equipment out with PVC or CPVC “starter pieces” PVC fittings and rubber sewer pipe connectors😲 Some brands sent ABS start pieces, which would often get connected to PVC. Crazy!

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    9326ysshMad Dog_2
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I can remember installing a boiler back in the 80s. MOD CON where they required ABS vents. Can't remember the boiler.

  • hot_rod
    hot_rod Posts: 28,708

    Some of the early HTP products included a short piece of ABS, the Voyager maybe?

    What I find is

    PVC 140°F max

    Screenshot 2025-06-29 at 10.45.34 AM.png

    IPEX 636 CPVC (flue gas certified) 194°F, with their solvent and glue

    Screenshot 2025-06-29 at 10.55.58 AM.png

    CPVC 200°F max

    Centrotherm PP 230°F continuous

    Screenshot 2025-06-29 at 10.42.37 AM.png

    DuraSeal single wall stainless 480° operating, 550°F max

    Screenshot 2025-06-29 at 11.03.03 AM.png

    Flue gas sensor on my Lochinvar Knight is 225°F to shut down burner. So essentially only the Centrotherm and SS vent pass the potential flue gas temperature question

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    This was 3"pvc... .I agree with Bob Harper...we're all just taking a stab at why...only a lab analysis can possibly determine why it pulled apart. Let's just keep an open mind....could the manufacturers have very sound reasons for disallowing pvc in flue exhausts?

    Could acidic flue gases cause this is as well? Mad Dog

    PC7060
  • hot_rod
    hot_rod Posts: 28,708
    edited June 2025

    acids are one of the things PVC does seem to handle well

    https://ipexna.com/wp-content/uploads/2022/08/chemical-guide-caen-ipex-pvc.pdf

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I think it was a Teledyne Laars

    PC7060