  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I think 290 is propane.

    But doesn't R-32 contain some 290 in the mix? I put an R-32 through the wall unit in my condo and I know it is 32 thinking I read that it is flammable??

  • ChrisJ
    ChrisJ Posts: 17,763

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    GGross
  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    What is the issue? Premature degradation? Mad Dog

  • pecmsg
    pecmsg Posts: 7,634

    I’d say at least 5 years maybe more. Not to say some old stock is not still there.

  • GGross
    GGross Posts: 2,104
    edited April 2025

    R-32 and R-454B (a blend of R-32 and R1234yf) are what you will see in the US taking the place of R-410A. These are both classified as an "A2L" refrigerant, neither contains any propane, both are considered flammable. I would suggest you seek out an A2L seminar, or take the A2L course from the EPA test site. The flammability of the refrigerant is definitely something to take seriously as an installer, however the charge of a through the wall unit is likely too low to even require sensors anywhere. If you were to look at the flame propagation of an A2L compared to R-410A it is actually very close, but propagates flame just outside of the cone at the testing facility that separates a "non-flammable" refrigerant (which are still flammable mind you) from a flammable refrigerant. The A2L classification was created because while it is flammable it is not flammable enough to warrant being in the class 2 or 3, so there was a need to more accurately classify this lower flammability refrigerant.

    If you are comfortable with natural gas or propane gas lines running through your house, which can obviously leak a lot more fuel, and fuel that is much more flammable. Then I would think R-32 or R-454B would not cause you too much distress. Manufacturers have had to spend a mountain of cash developing sensors and mitigation systems for their split systems connected to gas furnaces.

    ethicalpaulChrisJ
  • ChrisJ
    ChrisJ Posts: 17,763

    Not to mention stoves that can be turned on without a flame and left.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I guess I was wrong but just remembered that R-32 was flammable when I installed the new through the wall unit which is R-32.

    I am long past keeping up on that stuff.

    I long for the days of 12, 22 and 502.

  • pecmsg
    pecmsg Posts: 7,634

    NO, They are not flammable!

    They are mildly flammable.
    Neither one will support combustion alone. Put a flame to them it burns, take the flame away and it goes out!

  • ChrisJ
    ChrisJ Posts: 17,763

    That's strange

    You might want to contact the manufacturers about their labeling then.

    PXL_20250402_195743714.MP~2.jpg

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • pecmsg
    pecmsg Posts: 7,634

    that’s because it will burn but is not self supporting.

    Mad Dog_2
  • ChrisJ
    ChrisJ Posts: 17,763
    edited April 2025

    It literally says extremely flammable gas on it.

    The UN classification is that it's flammable.

    Here's R32

    1000015116.png

    Here's Propane

    1000015117.png

    1000015119.png

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • pecmsg
    pecmsg Posts: 7,634

    fine

    I’m not going to argue the point!

    Mad Dog_2Long Beach Ed
  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    Phosgene gas....that's what their big concern was back then. Mad Dog

  • winnie
    winnie Posts: 80
    edited April 2025

    R32 is definitely flammable. But it is much less of risk than propane by many metrics. It might have the same UN transportation classification as propane, but there is a reason that it has a different ASHRE classification.

    Of course these classifications are based on real measurements, but the classification thresholds are somewhat subjective in nature. No one would deny that both gasoline and diesel are flammable, but the risks they present are different!

    Here is a table comparing R32 to other refrigerants, including propane and butane. To get a flammable mixture you have to get about 7x the amount of R32 into the air, the minimum ignition energy is much higher, the flame speed is much lower, and the amount of energy released when it is burned is much lower:

    image.png

    (Table from https://hvacdist.com/wp-content/uploads/2024/09/Why-R32-Presentation.pdf )

    pecmsgChrisJ
  • MontufarServidone
    edited April 2025

    You're spot on that R-290 is propane—it's a pure hydrocarbon refrigerant, and yes, it's highly flammable (A3 classification).

    As for R-32 (difluoromethane), it's a different refrigerant altogether, but you're also right that it's flammable too, though not as much as R-290. R-32 is classified as A2L, which means:

    • A = Low toxicity
    • 2L = Mildly flammable

    So yes, R-32 is flammable, just not to the same extreme level as R-290. That "2L" classification means it burns, but it's harder to ignite and burns slower than full-on A3 refrigerants like propane (R-290) or isobutane (R-600a). Both refrigerants are commonly used in modern cooling systems, including ductless mini split systems, due to their efficiency and lower environmental impact compared to older refrigerants like R-410A. When choosing ductless mini split systems, it’s worth noting that R-32 is often favored for its balance of efficiency and safety, while R-290 is less common in residential units due to its higher flammability. Always ensure proper installation and maintenance to mitigate any risks with these refrigerants.

    ChrisJGGross
  • mattmia2
    mattmia2 Posts: 18,399

    kinda hard to make phosgene if you don't have chlorine

    pecmsgChrisJ