Welcome! Here are the website rules, as well as some tips for using this forum.

Need to contact us? Visit https://heatinghelp.com/contact-us/.

Click here to Find a Contractor in your area.

If our community has helped you, please consider making a contribution to support this website. Thanks!

Liner with oil heat?

Options

I have a very old boiler with oil heating and I live in NY. I recently had a chimney company come out and they are saying I need a new liner and repointing. I am not convinced about the liner, and am wondering if it matters whether I do repointing or lining first, as I may need to break up the work into 2-3 years. Pictures attached. What looks the most urgent/concerning?

2b898817-4b01-4288-aa0a-02bde3734e7e_cdv_photo_000.jpg 97567fd2-2bc3-45bf-b277-e1b5ba798569_cdv_photo_018.jpg 99193279-5d2a-42e9-af51-5466b3ee56aa_cdv_photo_001.jpg 87ed4949-7f1c-4bd8-8071-90978dd4a65e_cdv_photo_014.jpg

Comments

  • mattmia2
    mattmia2 Posts: 18,445

    If it really is only another 2-3 years, repointing it then vs now won't be a lot different. if it were 5-10 years that would be a different story.

    rmlewi
  • mattmia2
    mattmia2 Posts: 18,445

    I don't know if any of the chimney experts here are in your area but their opinion will cost more but it will be correct and possibly their solution will cost less.

    rmlewisdodder
  • HVACNUT
    HVACNUT Posts: 7,814

    How about some pics of the "very old boiler"? If you plan on upgrading in the near future, you would most likely NEED a liner. The reason being, a new high efficiency oil fired boiler will have a much lower flue gas temperature than the "very old boiler". That coupled with a terra cotta lined exterior chimney is a recipe for condensation. I've seen countless plugged chimney bases less than a year after a new high efficiency oil fired boiler was installed because no liner. The terra cotta deteriorates and gravity does the rest. @Bob Harper can give a much better explanation.

  • rmlewi
    rmlewi Posts: 7

    @HVACNUT here is the boiler. We bought the house in 2020 and I was told the boiler is at least 30 years old. Yes, part of my concern is if we have to replace the boiler, would we possibly have to replace the liner again if it is the wrong type or something?

    IMG_0003.jpg IMG_0002.jpg
  • rmlewi
    rmlewi Posts: 7

    Ok, thanks! I do have annual boiler maintenance scheduled for the end of the week.

    Intplm.GGross
  • jesmed1
    jesmed1 Posts: 1,630
    edited March 2025

    I'm a homeowner and we have the same boiler as you do, of probably the same age, around 30 years old. Ours is still in good shape and could easily last another 10 years, as could yours. So I agree with @mattmia2 that there's no need to give up on it prematurely.

    We also have a brick chimney with terra cotta liner as do you. Ours is a little cleaner than yours, but yours may still be usable without a new liner. As has been said, get a good chimney sweep.

    rmlewisdodder
  • kcopp
    kcopp Posts: 4,741

    Besides the boiler what else is going into the chimney? I see another smoke pipe going into the chimney…

    mattmia2
  • rmlewi
    rmlewi Posts: 7

    On the roof? That's the plumbing vent.

  • rmlewi
    rmlewi Posts: 7
    edited March 2025

    @mattmia2 I'm not exactly sure but it's no longer in use:

    IMG_0006.jpg
  • Could someone clarify what is the main reason for installing a liner? Is it because the chimney is bad or flue temps not expected to be hot enough to prevent condensation?

  • Mad Dog_2
    Mad Dog_2 Posts: 8,758

    Both reasons mad Dog

    Waher
  • Grallert
    Grallert Posts: 1,251

    I would start with pointing. Once that mortar starts to go it goes fast.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

    rmlewi
  • leonz
    leonz Posts: 1,996
    edited March 2025

    Your coal stoker is an anthraheat mini stoker. You could sell it easily by placing an advert in the coal pail forum.

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,027

    When you disconnect that vent pipe from the Mini Stoker, think about adding a 7" RC Barometric draft control. 

    Screenshot 2025-03-28 at 2.25.19 PM.png

    It is recommended by the boiler Manufacturer on page 12 and 13 of the Installation Manual. 

    Screenshot 2025-03-28 at 2.29.47 PM.png

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    MaxMercyrmlewi
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,370

    I don't think the chimney guy is scamming you. It looks like you need repointing however the chimney is not going to fall down soon its not that bad but needs to be done.

    As far as relining we can't see the whole thing with pictures and what I can see looks ok. I would repoint first and save up for a liner unless the chimney guy is saying the liner is unsafe now.

    rmlewisdodder
  • Bob Harper
    Bob Harper Posts: 1,192

    You have a Weil McLain Gold boiler, which is relatively efficient venting into an unlined, cold, exterior masonry chimney in NY. You might be able to get a properly sized smoothwall 316ss liner down this offset terra cotta but they likely would need to break out the old clay liner to make room for a sufficiently sized ss liner. The chimney must be suitable for the class of service- it is not. Refer to NFPA 211. Aside from the liner, the exterior chimney above the roof appears to have de-bonded between the mortar and brick. The Ordinary Portland Cement-based mortar is too hard for that reclaimed soft brick as noted by the spalling, crumbling and de-bonding at the boundaries. Old used bricks still have original mortar impregnated into the pores of the bed joints thus rendering them less likely to bond with new mortar. The freeze-thaw cyclic damage to the upper chimney repeatedly erodes this boundary causing the brick to actually separate from the mortar.


    Meanwhile, the weather has been eroding the mortar externally. Since there is no rain cap, significant frank water has penetrated down the clay tile putting the acidic condensation and soot into solution form where it easily destroys the mortar joint between flue tiles. From there, the water easily pours into the interstitial spaces of the chimney infusing it with soluble salts created by the acids combining with the alkaline mortar. This salt attracts water and is drawn to both the surface where it is visible. We call this chalky powder 'efflorescence'. It's a water magnet. However, there is also similar salt migration to the interior of the chimney interstitium where it condenses at the capillary break formed by the gap between the clay tile and the chimney wythe walls. Where there is bridging caused by mortar backfilled between the wythe walls and the tiles, water and salts will migrate to the interior of the clay flue tiles. As it wicks up the unglazed ends of the clay tiles, it is easily drawn up the 2 foot length of each tile by capillarity. As the water right behind the glazed or vitreous inner face of the flue tiles gets heated during a firing cycle, this trapped water converts to steam expanding 1,600 times. The result is the spalled face you see of the tiles. Now the tiles have lost mass and no longer meet the code for thickness, nor their joint integrity not the chimney proper. The cracked cast crown allows further water penetrating hastening the demise of this chimney. The counter flashing appears to be slightly let into mortar joints but not sealed in. This allows more water in.

    If you pushed hard against the upper chimney, it would probably fall over. From the comfort of my home, it appears to justify rebuilding from viable material-up.

    The chimney connector off the WM boiler does not appear to slope upwards 1/4" per LP. It must have a barometric damper per code unless that boiler mfr expressly forbids it (WM does not). The connector must be the proper gauge thickness (appears to be 26ga. galv. x 7" diameter, which is too thin. Must be 24 ga. You must have a minimum of 3 screws per joint equidistantly spaced. The connector must be supported, which it is not. No pic of the chimney breaching- can you supply? The flue was grossly undersized for both boilers firing simultaneously so glad it is shut down but needs to be disconnected, which can be done when the connector pipe is replaced.

    I think you need to consider demolishing that chimney down to where it is viable and rebuilding with a properly sized smoothwall 316ss liner to new 24 ga. galv. connector or better yet 26ga. ss rigid liner as connector with a tee and barometric damper as shown above.

    This is a very sick chimney probably well beyond simple pointing and lining. Repointing and relining do not remove those soluble salts, and pointing is not a structural repair.

    HTH

    Waherrmlewisdodder
  • rmlewi
    rmlewi Posts: 7

    @Bob Harper I appreciate the very thorough analysis, but since I can't afford to rebuild it now, and the proposed liner and repointing work won't solve the problem, I'm inclined to just do nothing for at least another year or two. We do also have another chimney connected to a wood burning stove in the basement, which we have not yet used. We will eventually get that one cleaned, inspected, and at least repointed at the top (it goes up through the center of the house), but we have only owned this house for five years and there have been more pressing issues to address before we could tackle that.

  • rmlewi
    rmlewi Posts: 7

    @Bob Harper does this help at all? Tough to get a better shot with that other wall in the way.

    IMG_0019.jpg
  • Bob Harper
    Bob Harper Posts: 1,192

    Punch a hole in the back of the chimney 18" above grade. Connect a few feet of smoothwall 316ss liner from a sidewall power venter, such as a Field Controls SWG interlocked to the burner, connect new stovepipe, put a rain cap on top of the flue, and call it a day until you can do something more permanent.

    HTH