New boiler - pipe noise / surging

2»

Comments

  • delcrossv
    delcrossv Member Posts: 2,124

    Probably don't have a 3" threader, so of course 2" is okay 🙄

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • pecmsg
    pecmsg Member Posts: 5,966

    if permits were pulled that IS NOT installed as per the manuals.
    beyond that find a steam contractor and just pay to get it right!

    CLamb
  • KC_Jones
    KC_Jones Member Posts: 5,883

    Have you made final payment? If you have, probably not much leverage for anything.

    If you have not, tell them you want it in writing from the manufacturer that the undersized header is approved by them, or you won’t make final payment.

    They literally do not get an opinion on this one, so make it clear you aren’t accepting that. The manufacturer decides the proper header size not the installer.

    $100.00 says they sized the boiler wrong too.

    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    CLamb
  • 109A_5
    109A_5 Member Posts: 2,372

    " Any suggestions on the best options for recourse if they continue to insist that it is OK the way it is installed? "

    Not in any particular order; Lawyer, BBB, pay someone else that knows what they are doing to redo it correctly. Learn what is needed to correct it, do the work yourself (Summer is coming), you can always sell the tools needed when you are done.

    Personally I like the DIY option. You learn more, better satisfaction, better future maintenance. I realize it is not for everyone, but you would be surprised. Many folks here on this site have installed their own boiler and are better off for it.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • football_plus
    football_plus Member Posts: 10

    Ever since they fixed the pitch of that return pipe 2 weeks ago the noise has been completely gone. 👍️

    delcrossv
  • 109A_5
    109A_5 Member Posts: 2,372

    OK, glad it worked out without too much drama.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System

Welcome