Probably don't have a 3" threader, so of course 2" is okay 🙄
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
-
Have you made final payment? If you have, probably not much leverage for anything.
If you have not, tell them you want it in writing from the manufacturer that the undersized header is approved by them, or you won’t make final payment.
They literally do not get an opinion on this one, so make it clear you aren’t accepting that. The manufacturer decides the proper header size not the installer.$100.00 says they sized the boiler wrong too.
1 -
" Any suggestions on the best options for recourse if they continue to insist that it is OK the way it is installed? "
Not in any particular order; Lawyer, BBB, pay someone else that knows what they are doing to redo it correctly. Learn what is needed to correct it, do the work yourself (Summer is coming), you can always sell the tools needed when you are done.
Personally I like the DIY option. You learn more, better satisfaction, better future maintenance. I realize it is not for everyone, but you would be surprised. Many folks here on this site have installed their own boiler and are better off for it.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
-
OK, glad it worked out without too much drama.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 966 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements