2 pipe vapor system with orifices /regulating-valves . NO traps on rads.

I'm assuming nearer rads would see steam first.

Am I correct that reducing the orifice size on faster heating rads would encourage steam to find rads further down the line?

Sort of "balancing back pressure " between emitters? Seems the only way without traps to provide positive close for filled rads.

Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
DanHolohan

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 25,811

    Main and dry return venting!!! Then main insulating. Changing the inlet orifice or metering vavle size will indeed reduce the heat ouput of the radiator — but will not have much effect on how soon it sees steam. If the mains and dry returns are adequately vented, and the steam mains are insulated, even fairly long mains — say 100 feet or so — should see steam full length within 5 minutes of the boiler making steam, and in the context of a full burn cycle that's not that important.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    delcrossv
  • delcrossv
    delcrossv Member Posts: 2,035

    @Jamie Hall , I imagine some thought was put into pipe sizing when these systems went in?

    Seems none of this would have been an issue with coal, but is one with intermittent firing.

    So in these modern times, you'd still be looking for longer cycle times?

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • Steamhead
    Steamhead Member Posts: 17,669

    @delcrossv , there were several systems that used this setup- ADSCO, Kriebel, Hutchison, Tudor- have you found any markings on the original rad valves?

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    delcrossv
  • Jamie Hall
    Jamie Hall Member Posts: 25,811

    Was thought put into pipe sizing? Much as we love the dead men… probably not always! But since the pressure drops, even with somewhat wonky sizing, are very low and the actual free steam velocity is remarkably high, I doubt that pipe sizing and pressure loss is as much of a factor as simply heating the pipes up — that insulation bit — combined with adequate venting. It's worth noting that the old boys didn't use crossover traps because it was easier (it's not) but because they recognized that they are essentially free flowing, in contrast with vents.

    Cycle timing is one of the minor curses of on/off modern boilers. Ideally, even with modern boilers however, the optimum seems to be that the overall average firing rate matches the heat loss of the structure (obviously!) and that the "off" part of the cycle should be short enough that the system never really cools down. Doesn't work in the shoulder seasons. If one had a vacuum tight system (good luck with that) one could operate at sub-atmospheric pressures with some means of modulating the boiler output. Otherwise, one is really depending on the thermal inertia — heat capacity — of the radiation itself and the space to a lesser extent. I'm not sure there is a good way to minimize the problem of the more distant radiation not getting as much heat in warmer weather, though.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    delcrossv
  • delcrossv
    delcrossv Member Posts: 2,035
    edited March 22

    No, unfortunately. Do you think they just throttled the hot rads down?

    For my purposes, I'd better be careful with where the thermostat goes.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    Mad Dog_2
  • Steamhead
    Steamhead Member Posts: 17,669

    Vent the mains quickly, as @Jamie Hall said. This will level the playing field and you won't have to fiddle with the rad valves to balance it.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    delcrossvMad Dog_2
  • delcrossv
    delcrossv Member Posts: 2,035

    Vent dry returns fast too? Or does that not make as much difference?

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    Mad Dog_2
  • Jamie Hall
    Jamie Hall Member Posts: 25,811

    It makes even more difference… and if the system uses crossover traps, as many vapour systems do, the dry returns are your ONLY vents.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Mad Dog_2
  • mattmia2
    mattmia2 Member Posts: 12,142

    Because it is 2 pipe and the seam and condensate don't have to share the same pipe, the mains can be much smaller so they heat faster than 1 pipe mains.

  • delcrossv
    delcrossv Member Posts: 2,035
    edited March 23
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • Jamie Hall
    Jamie Hall Member Posts: 25,811

    Even so — the dry returns have to be vented. Copiously. And with no crossovers, so do the mains.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    delcrossv
  • delcrossv
    delcrossv Member Posts: 2,035

    Gotcha.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • mattmia2
    mattmia2 Member Posts: 12,142

    A lot of vapor systems have some sort of device at the boiler that is a crossover trap but doesn't look like one.

  • Jamie Hall
    Jamie Hall Member Posts: 25,811

    All kinds of strange stuff, indeed. But I was specifically referring the crossovers from the ends of the steam mains to the corresponding ends of the dry returns.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • mattmia2
    mattmia2 Member Posts: 12,142

    Others i think vent the mains through the emitters and the dry returns which probably works ok because the mains are much smaller than in 1 pipe systems.

    delcrossv
  • Jamie Hall
    Jamie Hall Member Posts: 25,811

    I suspect it does work OK — but there's something to be said for a nice big crossover or vent…

    On the other hand, maybe not. Consider that Cedric's entire system is vented through one Gorton #2…1300 square feet EDR… and works just fine at 2 ounces gauge or thereabouts.

    Hmmm…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • delcrossv
    delcrossv Member Posts: 2,035

    Maybe because it doesn't matter if the dry returns are full of air, the volume you need to vent is just the mains, risers and rads. Dry returns shouldn't have steam in them anyway. (?)

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • jumper
    jumper Member Posts: 2,440

    If dry return is mechanically evacuated before firing; AND there are no traps….. then steam fills all radiators quickly. IF boiler size is sufficient. At least I think that was the theory or hope behind the design of some steam systems I remember. Situation became interesting when boiler was replaced with multiple small ones. Operator would cook occupants early AM then shut down all but one or two. Procedure repeated late afternoons. Can't do that with HHW.