sizing copper pipe

need to run line from propane tank to barn 160' 300000 btus -this is line from tank to regulator what size line is needed
Comments
-
Fisher Controls handbook sizing chart has 1/2" OD type L, will carry 400,000 BTUH a distance of 175'.
This is 2 psig pressure drop with 10 psig reg at tank. FWIW
0 -
Its amazing how small propane piping can be. Propane packs a high btu punch. Butane is even higher. Mad Dog
1 -
-
-
-
If you go by my generators engine natural gas provides 10-20% less power than LP.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Here' goes some high school chemistry.
One mole(or more simply the same number of molecules) of any molecule in gas form has the same volume at a given temp and pressure.
Methane is CH4. you burn it and you get 1 carbon dioxide molecule and 2 water molecules.
Propane is C3H8. you burn it and you get 3 carbon dioxide molecules and 4 water molecules.
each of those reactions releases a defined amount of energy so burning a given volume of propane releases almost 3x as much energy.
A piece of equipment running propane vs methane with no modification other than the fuel and air metering has a lower input and lower output burning propane than when it is burning methane. I don't know why this is but I suspect that it is because the propane burns at a lower temp so less work can be done with a given volume and surface area.
0 -
-
-
Pardon the possibly stupid question, but how could two different units of volume (cu ft vs gallon) have different ratios of energy like that?
2516 to 1030 = 2.44
91,452 to 85,098 = 1.07Are the gallon units in liquid vs the cu ft units being gas?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
Did we lose the op completely? I think the why does the same equipment fired with propane have a lower capacity than when fired with methane is a @Tim McElwain level question because it isn't the energy content of the gas, at least not directly.
0
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 952 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements