Radiator thermostat wiring

maitoboika
maitoboika Member Posts: 3

If I have panel radiators installed with thermostatic valves attached, do I need to run any thermostat wire from the radiators to the boiler?

Comments

  • delcrossv
    delcrossv Member Posts: 2,031

    You still need some way to tell the boiler to end the call for heat. But that isn't from the radiator, that's from an average location in the house (not near an emitter)

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • Jamie Hall
    Jamie Hall Member Posts: 25,808

    Or to put it another way — the TRV on the radiator (or radiators) can neither tell the boiler to start nor to stop. They have no wires or switches in them to do that. In fact, as a bottom line, they can only tell their individual radiator to stop heating when the system is running. They can't tell the radiator to start.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • maitoboika
    maitoboika Member Posts: 3

    …that’s what I figured, thanks. Would that not make the thermostatic valves redundant, as there would be a thermostat in the room? Don’t know much about radiators…

  • Jamie Hall
    Jamie Hall Member Posts: 25,808

    If there is a thermostat in the room — not only would a TRV redundant, but — if it were turned down for some reason — would prevent the thermostat from sensing the heat, and the rest of the building would overheat.

    A TRV is only of value if there are rooms which you may want to have cooler than the thermostat will hold them — the thermostat being located in some agreeable central position. Further, it is important the remember that a TRV can only reduce the heating of a space, not increase it. They are very useful — but only in a limited way.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • delcrossv
    delcrossv Member Posts: 2,031

    Well, if isolated, they could run a room warmer than the thermostat. But you'd need specific conditions for that to happen.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • hot_rod
    hot_rod Member Posts: 24,773

    if you use an ECM circulator in the delta P mode, a relay like this is as an option

    So a TRV opens, the pump wakes up, the relay detects current and fires the boiler

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream