Another Honeywell Heat Generator

Nhaggard07
Nhaggard07 Member Posts: 7
edited February 26 in Radiant Heating

For your viewing pleasure- another Honeywell Heat Generator (No2) found in the wild. This one residing in an attic in South Bend, IN.

A contractor in the past converted system over to expansion tanks. The customer asked me if they need this removed or if its fine. Seeing as ive never removed one, I said its been fine sitting there so far. Thoughts? Any dangers yhr mercury could pose if it's still in the heat generator?

Mad Dog_2

Comments

  • mattmia2
    mattmia2 Member Posts: 12,139

    Is it still connected? is there a relief valve at the boiler?

  • delcrossv
    delcrossv Member Posts: 2,031
    edited February 26

    Aren't those supposed to be at the bottom of the system? 🤔

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    Alan (California Radiant) Forbes
  • mattmia2
    mattmia2 Member Posts: 12,139

    It is just a mercury pressure regulator. It will work just under the open expansion tank too but it is usually far more convenient to put it by the boiler.

    delcrossv
  • bburd
    bburd Member Posts: 1,148

    I have seen those installed in other attics.


    Bburd
    delcrossv
  • techforlife
    techforlife Member Posts: 120

    In the words of his eminence Dan Holohan, pick up your tools and back away………….

    bburdMad Dog_2EdTheHeaterMan
  • mattmia2
    mattmia2 Member Posts: 12,139

    or just keep it upright until you get some plugs in it

    delcrossv
  • delcrossv
    delcrossv Member Posts: 2,031

    Someone with a gravity system may pay some cake for an intact one. Ebay.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • mattmia2
    mattmia2 Member Posts: 12,139

    easier and better to retrofit it to a prv and expansion tank

    delcrossvtechforlife
  • bburd
    bburd Member Posts: 1,148
    edited February 26

    That thing is full of mercury. If any of it spills, your house turns into a hazardous waste cleanup site at great expense. This has happened occasionally.


    Bburd
    Mad Dog_2
  • TheUpNorthState88
    TheUpNorthState88 Member Posts: 56

    Mine is still active but since this one has already been decommissioned, and in an attic space, I would leave well enough alone. It will not cause any harm. However, if the homeowner does ask you to remove it, make sure not to tip it over or all the mercury inside will spill out and you will have a serious situation on hand. Let the customer know this as well.

    If you haven't already, please watch Dan's video on the subject. Send it to the customer to watch as well. Knowledge is power.

    Lifelong Michigander

    -Willie

    GGrosstechforlifedelcrossv
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,887

    Only if you tell.......In this day & age, I'd make the building owner fully aware verbally & in writing of the mercury content & possible hazmat condition. Let THEM get it removed, Professionally by an abatement company. Mad Dog

    pecmsgtechforlife
  • mattmia2
    mattmia2 Member Posts: 12,139
    edited February 26

    that is sort of like calling an abatement company to remove a toaster that has asbestos in it instead of just carrying it outside.

    or in this case plugging the tapings and carrying it outside.

    Alan (California Radiant) Forbesdelcrossv
  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,355
    edited February 26

    So, if you're the installer back at the turn of the last century and you want the system to run as hot as possible, do you install the HHM next to the boiler in the basement or up in the attic? I have my answer.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • mattmia2
    mattmia2 Member Posts: 12,139
    edited February 26

    i thought the answer was attic when i saw this a couple days ago but now i think it is it doesn't matter because addition is commutative

    assuming the tank is in the attic in both cases.