Steam pressure control

neals
neals Member Posts: 61

So I was home today for a change, and noticed more hissing from the upstairs vents than usual. It's been pretty cold, so the system was at full steam, and when I went down to check the pressure was up to 3 PSI. I figured that would kill the vents so cycled the boiler off manually. Apparently the pressure cut off that came with the boiler isn't sensitive enough to stop at 2 PSI. Can an ordinary homeowner change this gizmo out for a more sensitive one? Do I even have the right one identified?

Comments

  • neals
    neals Member Posts: 61

    Here's the controller model.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,478
    edited February 19

    The scale on those controls is inaccurate….they all are. Take the cover off the control and set the white wheel inside to 1 psi. Set the scale on the outside with a screwdriver as low as you can go.

    Caution you have to try this. If you go to low you may back the screw out of the control or if the pressure setting is too low the boiler may not fire.

    make small adjustments at a time.

    tcassano87Intplm.
  • neals
    neals Member Posts: 61

    I should have searched better first. In a different thread was the advice to open it up, set the inner wheel to 1, and then use the screw to drop the cut-in all the way to the bottom. So I did that and will report back later.

  • Jamie Hall
    Jamie Hall Member Posts: 25,831

    Two other comments: that 0 to 30 psig gauge is required by code — but is almost useless for figuring out what a boiler is really doing. I would add a 0 to 3 psig gauge somewhere — the easiest thing to do is to mount it above the existing gauge in much the same way, and then the pressuretrol on top of that.

    And while you are doing that make sure that the pigtail — the pipe going from your gauge and control into the boiler — is clear.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Long Beach Edtcassano87
  • tcassano87
    tcassano87 Member Posts: 84

    question, I was always taught to have a gauge at least double what your testing for best accuracy. This was a general rule of thumb for plumbing applications not steam boiler obviously. Wouldn’t you want a gauge a little higher then 3 in case the pressure spikes so you know it’s over 3 & maybe have an issue with the pressure troll

  • Long Beach Ed
    Long Beach Ed Member Posts: 1,722
    edited February 19

    Good practice would say yes. Many people put a valve on the gauge, to protect it. And "accurate" gauges are out of the price range of many of the folks who make a hobby out of this. A cheap gauge reading in their expected range with Chinese accuracy is sufficient for their use.

    Remember that most all small systems are operated at a pressure of 1-1/2 pounds or less.

    tcassano87Intplm.
  • ethicalpaul
    ethicalpaul Member Posts: 7,455

    Can an ordinary homeowner change this gizmo out for a more sensitive one?

    A handy homeowner could change it out for a vaporstat, a device by the same company that costs a lot of money and operates at a lower range of pressure.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    Intplm.
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,722

    A new control may not give you any better accuracy. A Vaporstat will, but the improved accuracy will only be cost effective if your boiler is grossly oversized and/or regularly cycles on pressure.

    Follow Jamie's advice if you want to improve the accuracy and lower the operating limit of your boiler. Then if you can't get the control to ycle at a lower pressure, and still want to do that, look at Paul's suggestion to install a Vaporstat.

  • Intplm.
    Intplm. Member Posts: 2,573
    edited February 19

    Good advice. A valve on the gage is great for service and as you say, for protection. Turning the valve off to protect the gage?

    However this might not be protection. Go one step further and install a brass pig tail below the gage and fill the pig tail with water during the install. This will protect the gage from steam damage and allow you to get a reading at any time. This is what a pig tail is for. To protect controls from steam flashing into the control. Does steam always cause damage? No. The steam will turn to condensate in the pig tail during use. That water will also protect the gage. That one step further, by adding water, is the most thorough way.

    Long Beach Ed
  • 109A_5
    109A_5 Member Posts: 2,289

    That gauge should work. While adding it with a Tee under the pressuretrol with a valve and a elbow to the new gauge, also make sure to not forget to verify the pigtail all the way back to the boiler is not blocked or plugged up as advised previously.

    If the pressuretrol can't monitor the boiler's pressure it can't shut off the burner to limit the pressure.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • neals
    neals Member Posts: 61

    What's the valve for?

  • neals
    neals Member Posts: 61

    If for protection as said a couple of time in the thread, would I only open it when I want to read the gauge? If so, won't that be when the boiler is at max pressure and temp? So what is is protecting against?

  • 109A_5
    109A_5 Member Posts: 2,289

    You could open it slowly. With a system that should not go over 1.5 PSI a 3 PSI gauge should have some margin for error. And if the 0-30 PSI gauge is reading greater than 3 PSI just don't open the valve, no valve, no protection at all.

    Personally I use a Dwyer Magnehelic Gage which is more expensive, even used or NOS, than the 0-3 PSI gauge mentioned above. The Dwyer Magnehelic Gage which displays in inches of water column yet it is rated to tolerate up to 15 PSI so I don't worry about it. My system never goes over 0.072 PSI (2 inches of water column) anyways. 1 PSI = 27.68 inches of water column.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System