Help! Storm and no heat

Desdemona
Desdemona Member Posts: 5

Our wood furnace is indicating that it is overheating, yet there is hardly any wood left in the box. Our heating system relies on a combination of wood and oil through a boiler located in the basement, but we currently have no oil available. We are solely using wood for heating, and all the radiators are cold. We observed last night that the radiators were not warming up, so today we flushed each one. Additionally, we heard a high-pitched buzzing noise coming from the pump connected to both the boiler and the wood stove, which is a Grundfos model. We attempted to reset the power, but there was no change. We hear it turn on but then it switches off after a few minutes. This grundfos pump lacks a valve or bleed feature. We reset the temperature to the maximum of 160 degrees, yet it continues to overheat. What steps should we take next?

Comments

  • delcrossv
    delcrossv Member Posts: 2,064
    edited February 18

    Any water in the boiler? Valves all open?

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • hot_rod
    hot_rod Member Posts: 24,800

    what was the indication that it overheated?

    Did it steam or cause a relief valve to discharge?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Desdemona
    Desdemona Member Posts: 5

    Yes water is in the boiler.
    Yes valves are open. (nothing has been turned since we moved in a year ago)

    The thermostat on the woodstove shows 210f. There is barely any wood in it. A few months back, I did put too much wood in and steam was released and the temp showed 190f. This time, no steam, barely had any wood in it.

  • jesmed1
    jesmed1 Member Posts: 1,228
    edited February 18

    "Additionally, we heard a high-pitched buzzing noise coming from the pump connected to both the boiler and the wood stove, which is a Grundfos model. We attempted to reset the power, but there was no change. We hear it turn on but then it switches off after a few minutes."

    Buzzing noise = pump locked up?

  • delcrossv
    delcrossv Member Posts: 2,064
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • Desdemona
    Desdemona Member Posts: 5

    Yes, a very high-pitch buzzing noise.

    Earlier today there was a loud buzzing noise that was coming from the Grundfos unit. We bled each radiator throughout the house, opened the wood stove box, ceased adding wood, and reset the power to the Grundfos. Everything resumed functioning after about ten minutes, but then a very high-pitched noise came from the Grundfos, and all operations halted once more.

  • pecmsg
    pecmsg Member Posts: 5,868

    better picture of the pressure gauge?

  • Jamie Hall
    Jamie Hall Member Posts: 25,845

    If the pressure is OK — air bound, or the pump has died.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,782

    Hi, The blue pump has a plug on the back of the motor that can be unscrewed, and then you can feel whether the rotor is turning by gently poking a phillips screwdriver or some-such into the opening that's uncovered. I've used this approach to move and free up stuck rotors too. I don't know if the red pump has similar access. 🤔

    Yours, Larry

  • Desdemona
    Desdemona Member Posts: 5

    The fire is completely out. Temp has gone down finally. Temp shows 90.

  • pecmsg
    pecmsg Member Posts: 5,868

    90*C is near 200*
    with the fire out how is that possible?

  • Jamie Hall
    Jamie Hall Member Posts: 25,845

    Your boiler pressure is too low. Or much too low, depending on which gauge I believe. I'd want to see it around 15 psig — 33 feet. The pump may be airbound, or the system may need to be purged.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    delcrossv
  • delcrossv
    delcrossv Member Posts: 2,064
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • Desdemona
    Desdemona Member Posts: 5

    Yes - only 2 or 3 embers. The fire went out 8 hours ago. The temp has dropped considerconsiderably from the first picture we took of the gauge. (Look at first picture)




    Jamie Hall

    is there a way to release the air via a valve? The pump does not seem to have a valve/screw release. The pump is emitting a high pitch buzz.

  • mattmia2
    mattmia2 Member Posts: 12,222

    if you slowly add water does the pressure go up? gravity should allow water to flow in to the circulators, the air will be at the high points.