Wet return sizing

Ray_B25
Ray_B25 Member Posts: 1
edited February 17 in Strictly Steam

is there a chart for sizing the wet return of a steam boiler? One of our guys came across a 287,000 btu boiler with a 1” copper wet return. There was water spitting out of two gorton# 2 vents. The vapor stat was set to 16 and I had him turn it down to 11 with a 8 oz differential the spiting stoped but the 1” wet return doesn’t seem right to me. Also having him clock the meter to be sure it’s not over fired.
I would appreciate any advice

Mad Dog_2

Comments

  • mattmia2
    mattmia2 Member Posts: 11,768

    400,000 btu/hr of steam is roughly 1 gpm of condensate so I think your issues are elsewhere unless the returns are clogged.

    Ray_B25ethicalpaulDave in QCAIntplm.
  • pecmsg
    pecmsg Member Posts: 5,723

    please post pictures of the near boiler piping.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,223

    287,000 boiler output is only about .56 gallons/ min=34 gallons/hour.

    Burnham heating helper says 1" is good for 900EDR=216,000 btu

    1 1/4" =1530 EDR=367,200 btu

  • mattmia2
    mattmia2 Member Posts: 11,768

    Is that for a wet return or a 2 pipe dry return where it needs to carry condensate and air?

  • Dave in QCA
    Dave in QCA Member Posts: 1,801

    One other thing to consider that is not in this generalized for a return, it does not mention the length. If it is very long, and if there are quite a few 90s in the pathway, that will reduce the capacity. If they are straight runs with few turns, it should be OK

    By comparison, I was involved in advising on the rebuild of an 1880 2 pipe system with vertical pipe radiators aa few years ago. The total system load of 610 EDR, equally split between 2 mains and two returns that were installed with 1: soft copper, insulated and buried below the concrete basement floor. In this case the 1" wet returns have been performing just fine.

    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,223

    @mattmia2

    Wet. Thats what the op said he had.

  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,741

    I'd go with 1 1/4 copper on this one.. Mad Dog