Wet return sizing
Ray_B25
Ray_B25 Posts: 1
edited February 2025 in Strictly Steam
is there a chart for sizing the wet return of a steam boiler? One of our guys came across a 287,000 btu boiler with a 1” copper wet return. There was water spitting out of two gorton# 2 vents. The vapor stat was set to 16 and I had him turn it down to 11 with a 8 oz differential the spiting stoped but the 1” wet return doesn’t seem right to me. Also having him clock the meter to be sure it’s not over fired.
I would appreciate any advice
Mad Dog_2
    400,000 btu/hr of steam is roughly 1 gpm of condensate so I think your issues are elsewhere unless the returns are clogged.
    Ray_B25ethicalpaulDave in QCAIntplm.
    pecmsg Posts: 7,634
    please post pictures of the near boiler piping.
    EBEBRATT-Ed Posts: 21,328
    287,000 boiler output is only about .56 gallons/ min=34 gallons/hour.
    Burnham heating helper says 1" is good for 900EDR=216,000 btu
    1 1/4" =1530 EDR=367,200 btu
    Is that for a wet return or a 2 pipe dry return where it needs to carry condensate and air?
  • Dave in QCA
    Dave in QCA Posts: 1,811
    One other thing to consider that is not in this generalized for a return, it does not mention the length. If it is very long, and if there are quite a few 90s in the pathway, that will reduce the capacity. If they are straight runs with few turns, it should be OK
    By comparison, I was involved in advising on the rebuild of an 1880 2 pipe system with vertical pipe radiators aa few years ago. The total system load of 610 EDR, equally split between 2 mains and two returns that were installed with 1: soft copper, insulated and buried below the concrete basement floor. In this case the 1" wet returns have been performing just fine.
    Dave in Quad Cities, America
    http://grandviewdavenport.com
    @mattmia2
    Wet. Thats what the op said he had.
  • Mad Dog_2
    Mad Dog_2 Posts: 8,755
    I'd go with 1 1/4 copper on this one.. Mad Dog
    EBEBRATT-EdclammyIntplm.