I recently had my old boiler replaced with a new one and I’m having more issues than with the old one that had a corroded heat exchanger. I am currently waiting for a new condensation tank.
Tonight the rad in my kitchen (the last one on the line) started to mist and spray water, so I went to replace the steam vent.
When I did about 3 gallons of hot water came out of the vent.
I must have a corroded pipe. Is there any way to clean it out without replacing it?

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 7,305

    I'm not sure I agree with your diagnosis.

    You are having a condensate tank brought in? Did your system have one before?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Long Beach Ed
    Long Beach Ed Member Posts: 1,637
    edited February 7

    No "corroded pipe". Just a new boiler that wasn't properly cleaned or wasn't properly piped.

    And what's the "new condensation tank" about?

    delcrossvethicalpaul
  • delcrossv
    delcrossv Member Posts: 1,916

    Picture of the new boiler and the connection to the system would be helpful.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    Long Beach Ed
  • Jamie Hall
    Jamie Hall Member Posts: 25,624

    Sounds to me, I regret to say, like an unusually poor install of the new boiler. We need pictures of the new boiler and all the new near boiler piping, from several angles.

    Unless this place is huge or there is something very odd, you don't need a condensate tank. That's another clue that the install is… dubious.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Long Beach Eddelcrossvethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 7,305

    Yeah I assume it is surging, which is resulting in a low water condition in the boiler, and someone erroneously thinks the tank is the cure for that.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el