Can I install a regular thermostat on a Buderus GB142?
Hi there,My new-to-me house has a Buderus GB142 to heat hydronic radiant floors in the kitchen. There is an RC10 room controller in the kitchen. About 50% of the time, the RC10 displays the actual room temperature. The other 50% of the time, it's off by several degrees. If this were a normal thermostat on a normal system, I'd know what to do.But it isn't, and the Buderus documentation is quite incomprehensible. And as for the RC10, the only manual I could find was in Turkish! (There was an English manual behind a paywall on Scribd). What I want to know is: can I easily set it up with a regular thermostat, such as a Honeywell T4? Everything related to this machine seems discontinued.
Attached are photos showing the wiring harness, the "external control" area on the BC10, and the unit itself. Do the 24 and 25 connections correspond to a regular 24v thermostat control? In that case, would I simply disconnect the wires going into "RC," move them over to 24/25, and then connect a thermostat on the other end?
This is supplemental heat; I don't really care about any advanced features.
Thank you,
David
  • Ironman
    Ironman Member Posts: 7,942
    The “WA” terminals will turn the boiler on and off for space heating. There will be no reset, so the dail should be set the the maximum SWT that’s necessary for your heat emitters.
    Bob Boan
    david_and_heather
  • david_and_heather
    david_and_heather Member Posts: 32
    edited January 2025
    Thank you!
    EdTheHeaterMan Member Posts: 12,657
    edited January 2025
    You will just have to learn to read Turkish to get your answer.
    The T4 thermostat does not "Create" 24 volts. The T4 will operate on a 24 VAC circuit. so to answer your query… Connect the T4's R and W terminals to the WA terminals on the Buderus
    Ironman
    pecmsg Member Posts: 7,440
    Can you use in floor without measuring the floor temperature?
    YES…. That is what is in my homes in NJ. Radiant Floor Heat with wall thermostats.
    pecmsg
    The reason I asked was that control is set for 140. I would be worried about overshooting.
    If you are really worried about over-shooting, then you should aim lower. 🤣🤣🤣🤣🤣
    pecmsgIronman
  • david_and_heather
    edited January 2025
    Ironman, sorry, I have more questions! The two WA terminals are labeled "1" and "2". Obviously, there's nothing with this labeling for a thermostat. So here are my questions:
    1. Am I correct that this setup merely involves closing a circuit, so 1 and 2 are interchangeable (as long as the correct two connections are made at the thermostat)?
    2. At the thermostat end, would these be wired the same way as for a steam boiler? My steam boiler has one wire each going into W1 and R. (It has the original cloth insulation, so there is no color.) Is this right? I'm not so sure, because the Buderus manual says WA is for a "potential-free" thermostat, and I thought the R wire sends a 24V signal.
    3. Can I use any Honeywell thermostat that does not require a C-wire (such as the RTH8560D) with this?
    Thank you so much 🙏
  • david_and_heather
    Thanks, everyone!