Boiler has no power after draining and refilling

Daboosa
Daboosa Member Posts: 4

Oil steam boiler MST396.

It needed maintenance. I turned off the switch. Drained the rusty water. Turned on the switch. Nothing happened. The Google nest thermostat shows "no power". Even the water auto feeder display was dark. Pressing the manual "feed" button did nothing.

First I thought it's the low water cut off stopped the electricity to the entire unit so I took off the safety valve and manually added water higher than the water level probe. Turned on the switch. Nothing happened. (Not sure if it need a reset or it even matters)

I checked the breaker box at the electricity main but nothing jumped there. (Although I didn't flip everything off and on just to make sure, maybe I should)

Does low water cut off stop power to the entire unit including thermostat and auto water feeder?

Thoughts? Thanks!

Comments

  • 109A_5
    109A_5 Member Posts: 2,219
    edited January 17

    Hello Daboosa,

    Oops, what happened ? " Does low water cut off stop power to the entire unit including thermostat and auto water feeder? " It shouldn't but if someone wired things wrong… I think you may have noticed that by now.

    If I had to guess from here I'd say the switch you used to shut off the system may have failed and did not turn back on. Or a wire was bumped and fell off. Someone with a multi-meter and knows how to troubleshoot wiring should be able to locate the defect quickly.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Daboosa
  • HVACNUT
    HVACNUT Member Posts: 6,615

    Check the molex plug and make sure the control relay is plugged in all the way.

    On more than one occasion I didn't have power after servicing and it turned out to be the switch itself.

    Daboosa
  • yellowdog
    yellowdog Member Posts: 251

    Follow the path of power from the panel with a meter or a non contact tester. You will find where it is and where it isn't.

    Daboosa
  • Daboosa
    Daboosa Member Posts: 4

    Thanks guys! I'll check the power switch next.

    Is it possible the low water cut off was wired wrong to trip the whole circuit? Could that be the case and the system could still run fine for years as long as the water level never dips to trigger it? Does low water cut off need to be manually reset if that's the case?

    Thanks!

  • Jamie Hall
    Jamie Hall Member Posts: 25,691

    Some systems are wired so that the low water cutoff will kill power to the whole system. Not the best way to do it… or is it? I think one could have a debate on that. Whatever, some are. And it iis possible that that cutoff is a manual reset, particularly if you have two low water cutoffs (the upper one should also trip the autofeeder, and be automatic).

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    DaboosaGGross
  • 109A_5
    109A_5 Member Posts: 2,219

    If the LWCO kills the power to the system and 'its self', how do you get the system to work in the first place ???

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Daboosa
    Daboosa Member Posts: 4

    Thanks! That's my system. Last night it's dark and I was tired. This morning I found the hidden manual reset button on the low water cut off. Pressed it and power kicked on.

  • Daboosa
    Daboosa Member Posts: 4

    My system is wired like that. The low water cut off still had an indicator light on though when power was out for everything else. I pressed the reset button on it and all is good now.

  • HVACNUT
    HVACNUT Member Posts: 6,615

    So there's two Low Water Cut Off controls? One auto reset, one manual?

  • ethicalpaul
    ethicalpaul Member Posts: 7,397

    Peerless boilers, at least in 2019, have a 120v LWCO that cuts off the 120v supply to the boiler and its 24v transformer. The LWCO is the power "gatekeeper". Of course, the LWCO doesn't shut off power to itself.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    GGross
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,310

    If you have a manual reset button on the LWCO on steam you need an additional LWCO that is not manual reset.

    Maybe someone installed the wrong LWCO as one is all that required on steam AFAIN unless it was commercial