water coming out of a steam radiator vent?
bbillcee
bbillcee Member Posts: 67
edited January 2025 in Strictly Steam
hey guys
i've had 2x now ive gotten up in the morning and the mat in the bathroom was wet on the corner closest to the radiator. i dont see any evidence of water leaking from the vent. there is no other indication of water coming from anywhere else. i even considered that i was sleep walking and pee'd on the floor 🤣. the only logical explanation is the radiator. i checked all other radiator and see no signs of any spitting etc. The bathroom radiator is the closest radiator to the boiler. boiler water level is 2/3 of the sight glass. does this make any sense to someone?
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,843
    Can you post a photo of the piping on top of your boiler, and a picture of the vent on the radiator? And check that the radiator valve is open all the way - turned counter-clockwise.
    Jamie Hall Member Posts: 27,571
    Well… it would be tempting to say the vent was bad — they do fail — but there are so many other possible causes.
    How's the near boiler piping? Any water getting up into the mains would be a problem, particularly since this is the nearest radiator to the boiler.
    Is the boiler surging?
    What pressure is this operating at?
    Can condensate accumulate in the runout to the radiator?
    Is the radiator inlet valve fully open?
    For starters…
  • bbillcee
    the valve completely opened and radiator pitched to the valve
  • Long Beach Ed
    edited January 2025
    For starters, check the pressuretrol on the boiler and that the pigtail isn't clogged. The pressure must be set below 2 lbs.
    Then check the radiator vent. What is the size of that vent? It should be 4,5,6,C or D. If all else looks okay, replace it with a #4 Gorton or a #40 Hoffman vent.
    And look over all the pipes running to that radiator ascertaining that all have a significant pitch toward the boiler, and none have sags or missing hangers that can cause them to collect water.
    There are a few inadequacies in that boiler piping which may also contribute to this problem. Is the water level stable?
    That is also a fairly new radiator. I assume that it has never done this before?
    Do you "set back" the room temperature at night?
  • bbillcee
    the boiler could be surging, im think its when the boiler is bringing the heat up from night to daytime heat 68 degrees to 71. valve is fully opened not sure about the pressure…i thinking the pressuretrol is set at about a pound
  • bbillcee
    ok i have 2 pressuretrols ….1 i think is for high pressure only and the other is the regular one. should check both pigtails? its never done this before
  • dabrakeman
    dabrakeman Member Posts: 1,020
    I'd suggest getting up a bit early tomorrow morning and witnessing what the radiator is doing during the recovery. Everything except what got absorbed into the mat likely has evaporated before you get down there to see it. If that MoM is spitting water it will still have water in it. Unscrew it and shake it out. If there is water there then you can be assured wet steam is your problem. While the vent is off test it for function blowing through it upright and upside down.
    Set your pressuretrol as low as it will go. 0.5psi with 1psi diff.
    Looks like you have two risers off the header. ARe both of the mains off those risers parallele flow or is the one on the left counterflow? Can't tell from the photo. Which main is the suspect radiator off?
  • Long Beach Ed
    edited January 2025
    Both pigtails should be checked. It's part of regular maintenance. If you have steel ones and they do commonly clog; brass, less so. When they are clogged, the boiler does not shut off on pressure, so on an extended run, the radiators can accumulate condensate with higher-than-ideal pressure holding it up in the radiator.
    ethicalpaul Member Posts: 8,927
    Radiators don't accumulate condensate on extended runs, but yes check the pigtails!
  • bbillcee
    one main goes to a tee and one goes to the from the other to the back…the skinny pipe off the header goes to a basement bath rad…presssuretril is set to 2 psi…bring down to .5?
  • bbillcee
    edited January 2025
    @long beach ed ill pull them off tonight and clean
  • yellowdog
    yellowdog Member Posts: 294
    Step 1 is to remove the bath mat so it does not absorb the water when it leaks. With that done, you might be able to trace the leak back to its origin better.
  • bbillcee
    just like to add my tenant called me about some abnormal banging she heard around 3 am
  • Long Beach Ed
    edited January 2025
    Paul, two similar radiators: One is supplied with steam for five minutes, the other is supplied with steam for three hours. Which radiator produces more condensate?
    If, for whatever reason, condensate cannot leave either radiator, which radiator will accumulate more condensate?
    Are we playing semantics or is there a misunderstanding?
    If either radiator accumulates condensate, something is wrong with the piping or the trap, if it has one.
    edited January 2025
    Thanks for the clarifying question, Ed!
    There is a thought out there that radiators hold onto their condensate until after the call for heat ends, or they hold onto it if there is a vacuum in the system. That idea is what I was countering. I admit I wasn't completely sure if you were saying that, but you seemed to indicate that condensate builds up over a long call for heat, hence my response there.
    More condensate is definitely produced over a long call for heat vs a 5 minute call, but in either case all the condensate runs out as it is produced unless, as Jamie said, there is something broken.
    Long Beach Ed
  • Long Beach Ed
    Paul and Jamie, I completely agree. Unfortunately problems often only present themselves when a certain threshold is crossed. Sometimes that threshold is an unusually long boiler run, or an exceptionally cold radiator or system.
    On a mild or more typical day, an inferior system may putter along merrily. Thank you guys, for your notes.
  • bbillcee
    i pulled of both pigtails they were both clear, i set the pressuretrol a slight bit above .5psi with a diff of 1 (it was 2psi 2 diff) the vent is a no 5 gorton …i pulled it off, a few drops of water when i shook it
  • bbillcee
    update on this:
    so things have been working well till today. Its really cold in the North east so this morning i had steam coming out of that bathroom radiator vent ( i put a new gorton 4 on there a few days ago)i went down and checked the boiler the gauge said around 3 psi. I have the pressuretrol set at .5 with diff of 1. shouldnt the boiler have cut off? i just check the pigtail a couple days ago and it was clear. the past few days i always saw the gauge showing 1 psi when the boiler was running. 🤷🏻‍♂️
    Pressuretrols are very inaccurate, to the heavy side. Yes it should have cut off. You can try a long call for heat to see if it does get to a point where it cuts off the boiler.
  • dabrakeman
    Copied post from @Fred to me 10 years ago:
    Inside the Pressuretrol, right below the micro switch, there is a pivot arm. At the end of that arm you will see a screw pin that is activated by the diaphragm at the bottom of the Pressuretrol. If you look very carefully at that screw pin, you will see it actually has a tiny (I mean tiny) hex head on it. It takes a .050 hex wrench and you can turn it clockwise (Towards the bottom of the Pressuretrol to decrease the Cut-out pressure or counter clockwise to increase the cut-out pressure (which none of us want to do but who knows, your Pressuretrol may be really screwed up!). Turn the power to the unit off first. You may find the first attempt to turn that screw a little bit stubborn (relatively speaking) because it has some Locktite on it but it does turn. Don't turn too much, a fraction of a turn goes a long way towards getting it adjusted where you want it (maybe 1/32 inch turn to start with). You may need to play with it to get it exactly where you want cut out to be.
    Pressuretrols are not very accurate. This is a method of fine tuning. MAy still not be possible to get all the way to a 1.5psi cut-out and 0.5 cut-in. Will depend upon your unit. AFter each incremental change you make watch a couple cycles because the cut-in may get too low and prevent the boiler from turning back on in which case you will have to back off your adjustment slightly. This is also pointless if you don't have a 0-3psi or 0-5psi gage. Suggest you get one if you don't have one already.
    Or, you can get a vaporstat.
    bbillcee
  • bbillcee
    i have a high limit pressuretrol on there as well set at 10….is that too much?
    edited January 2025
    No. It won't come into play at all unless the lower-set one fails. You can put it lower if you like but I assume it has a manual reset button so you don't want it to cut out casually.
    bbillcee
  • bbillcee
    so is the new Gorton vent that I put in bad already that it was letting steam out?
  • bbillcee
    would this be the right vaporstat? honeywell L408J1009(0-16 oz)
    It's hard to tell from here. If it was steam hot (too hot to hold onto) then it should have closed.
  • dabrakeman
    I will defer to one of the pros to advise you on the vaporstat 009 vs 017 vs 033.
  • delcrossv
    delcrossv Member Posts: 2,204
    edited January 2025
    009 is the one you want.
    https://www.supplyhouse.com/Honeywell-L408J1009-Vaporstat-Controller-Steam-0-to-16-oz-in2?utm_source=google_ad&utm_medium=Shopping_Heating&utm_campaign=Shopping_X_Heating_X_SSC_ClassA&utm_campaignid=21633352233&utm_adgroupid=170415967350&utm_targetid=pla-2350258627814&utm_product_id=L408J1009&utm_matchtype=&utm_keyword=&utm_adtype=pla&utm_category=Heating&gad_source=1&gclid=Cj0KCQiAy8K8BhCZARIsAKJ8sfQjF_uW6Bx5BnMweO3U4jGvWxOQD0MJNqqYVaYjy9qjCLyGLU7brs8aAll6EALw_wcB