Can you double check the wiring for my Hydrostat & ZVC?
Backstory:
  • I noticed I am using ALOT of oil. Already at half a tank only 3 weeks in. I looked at the Hydrostat and noticed ECO was off. I have since adjusted it to 2. I also noticed the wiring does not match the drawings in the instructions of the Hydrostat or the ZVC
System:
  • Buderus G115 with Reillo burner.
  • Hydrostat 350-Plus.
  • ZVC404.
  • 3 total zones (2 heating baseboard hydronic, 1 indirect water heater).
  • 3 zone valves Z100P2-2.
  • 1 Circulator pump.
  • LL set to 140
  • HL set to 191
Notable Connections:
  • T T of the Hydrostat is connected to X X Insulated End Switch of the ZVC.
  • C2 C1 of the Hydrostat connected to the circulator pump.
  • Indirect water heater zone valve connected to Zone 4 with Priority OFF.
  • ZC ZR of Hydrostat has no connection. But Z/I switch set to I.
Are these correct or wrong? Thanks
    Jamie Hall Posts: 27,989
    To point out the obvious: the amount of oil you use — unless you have an oil leak somewhere (I hope not) — is related to the amount of heat required by the structure. If the structure is not overheating, you needed that oil to keep it at the set temperature.
  • cckriss
    cckriss Posts: 47
    So, the oil usage has nothing to do with the ECO mode or incorrect wiring or settings at the Hydrostat or ZVC?
  • yellowdog
    yellowdog Posts: 295
    First thing, get rid of the low limit. Absolutely no reason to have a low limit set on a Buderus.
    Grallert
    109A_5 Posts: 4,773
    Is this system new ? You did not say how long you have lived with this system, if it has been multiple seasons the wiring probably has not changed. The burner may need a tune up and the boiler cleaned.
  • cckriss
    cckriss Posts: 47
    edited January 2025
    The entire system is few years old but it has not been used much because I have been renovating and not living in the house until now so I do not have a baseline of what is "correct". This is the first winter season living in it.
    The wiring has not changed but I just happened to notice that it does not match the instructions for the Hydrostat or the ZVC
    very little, anyway — a few percent at the most related to the ECO mode.
